Topic: VD Calc

User: Alwayslearningelec, Location: NJ

Asked on: Friday, August 8, 2025 at 7:32 am EDT
Answered on: Friday, August 8, 2025 at 7:32 am EDT

Question: How would you do a VD calc for wiring running to (15) lights in a row. Thinking about what would be entered for "current at the end of the run"?

Okay, let's break down how to calculate voltage drop (VD) for a string of 15 lights in a row. The crucial point is figuring out how the current is distributed along the run, which directly affects the calculation.

Understanding the Scenario

We assume the lights are connected in parallel along a single cable run. This means the cable supplies power to each light in sequence. Each light draws current from the cable at its connection point.

The Challenge: Variable Current

Unlike a simple circuit where the entire current flows through the entire wire length, in this scenario, the current decreases as you move down the line of lights. This is because each light "taps off" some of the current.

The Solutions (and Their Complexity)

There are a few ways to approach this, ranging from approximations to more precise methods.1. Approximate Method (Acceptable for Many Situations) Assumption

Assume that the current is evenly distributed. This is a simplification, but often close enough,
especially if the voltage drop is not a major concern.

Steps


Calculate Total Current (I_total)

Determine the total current drawn by all 15 lights. `I_total = (Current per light) 15`2.

Calculate Average Current (I_avg)

Divide the total current by 2. `I_avg = I_total / 2` This is because, on average, you can assume the wire length has this value.
3.


Use the VD Formula

Use the standard voltage drop formula, substituting the average current (`I_avg`) as your current value:


Formula (for single-phase circuits)

`VD = (2 K L I_avg) / CM` (USA / Imperial)

Formula (for single-phase circuits)

`VD = (√3 ρ L I_avg) / A` (Metric) `VD` = Voltage Drop (Volts) `K` = (Imperial) `ρ` (rho) = Resistivity of the conductor material (ohm-meters). Copper: ~1.724 x 10^-8 ohm-meters. Aluminum: ~2.82 x 10^-8 ohm-meters. `L` = One-way length of the conductor (feet or meters) `I_avg` = Average current (Amps) `CM` = Circular Mils of the conductor (look up in a table) `A` = Cross-sectional area of the conductor (mm²)4.

Check for Acceptable VD

Compare the calculated voltage drop to the allowable voltage drop (typically 3% to 5% of the supply voltage for lighting circuits).

Current at the end of the run

In this approximation, the current at the "end of the run" is considered to be ZERO because all of the current is consumed by the lights before getting to the end. The assumption that the current is evenly distributed assumes that, on average, there is no current at the end of the run.


Pros

Simple to calculate. Often good enough for initial estimates.

Cons

Less accurate than the iterative method. May underestimate voltage drop, especially if the voltage drop is near the limit.

2. Iterative (Segment-by-Segment) Method (More Accurate)


This is the most accurate way to determine voltage drop, but it requires more calculations.
Steps


Divide the Run

Divide the cable run into 15 segments, each running to one light.2.

Calculate Current in Each Segment

Segment 1 (closest to the power source): Carries the current of all 15 lights (I_total). Segment 2: Carries the current of 14 lights. Segment 3: Carries the current of 13 lights. ...and so on, until... Segment 15: Carries the current of 1 light.3.

Calculate Voltage Drop in Each Segment

Use the VD formula for each segment, using the
actual current in that segment and the length of that segment.4.

Sum the Voltage Drops

Add up the voltage drops calculated for each segment. The sum is the total voltage drop for the entire run.


Formula (for each segment 'n')

`VD_n = (2 K L_segment I_n) / CM` (Imperial) `VD_n = (√3 ρ L_segment I_n) / A` (Metric) Where `I_n` is the current flowing through segment 'n'.

Pros

Highly accurate.

Cons

More time-consuming. Best done with a spreadsheet or simple program.

Choosing the Right Method
When to Use the Approximate Method

Preliminary design. When the run is short and voltage drop is likely to be low. When you need a quick estimate.

When to Use the Iterative Method

Long runs. Circuits sensitive to voltage drop. Final design calculations. When code requires a more precise calculation.

Example (Approximate Method)


Let's say: Each light draws 1 Amp (I_light = 1A). The run is 100 feet long (L = 100 ft). We're using 12 AWG copper wire (CM = 6530 circular mils, K = 12.9).
1. Total Current

I_total = 15 lights
1 A/light = 15 A2.

Average Current

I_avg = 15 A / 2 = 7.5 A3.

Voltage Drop

VD = (2 12.9 100 ft 7.5 A) / 6530 CM = 2.97 VoltsIf your supply voltage is 120V, a 2.97V drop is approximately 2.5% (2.97/120 100), which is likely acceptable.

Important Considerations



Code Compliance

Always check local electrical codes for maximum allowable voltage drop. The NEC (National Electrical Code in the USA) recommends a maximum of 3% voltage drop for branch circuits and 5% overall (from the service entrance to the furthest outlet).


Light Sensitivity

Some lights (especially electronic ballasts or LED drivers) are more sensitive to voltage drop than others. Check the manufacturer's specifications.

Conductor Temperature

The resistance of a conductor increases with temperature. For very long runs with high current, it might be necessary to account for conductor temperature when calculating voltage drop.


Power Factor

If the lights have a significant inductive load (e.g., older fluorescent ballasts), the power factor will affect the voltage drop calculation. You'll need to use a more complex formula that includes the power factor. Most modern LED lights have a Power Factor close to 1, so this is not usually an issue.

Three-Phase Circuits

The voltage drop calculation is different for three-phase circuits.

Tools



Voltage Drop Calculators

There are many online voltage drop calculators (search for "voltage drop calculator"). Some allow you to specify the number of loads and their locations.*

Spreadsheet Software:
You can easily set up a spreadsheet to perform the iterative voltage drop calculation.By understanding these methods, you can accurately calculate voltage drop for a string of lights and ensure that your installation meets code requirements and provides adequate performance. Remember to prioritize the iterative method when precision is crucial. Good luck! Flag for review