Topic: Using Building Steel to "Ground" "Stuff"

User: jes25, Location: Midwest

Asked on: Friday, August 8, 2025 at 8:30 am EDT
Answered on: Friday, August 8, 2025 at 8:30 am EDT

Question: I'm kinda the code guy around here and lately I've been asked by the account managers how to ground random objects their customers are wanting grounded. In one case it was fancy vending machine and the other a flammables storage cabinet. I know the vending machine is grounded through the EGC and the storage cabinet I don't believe needs any special external ground either. No matter, that's what the customer wants. Driving an aux rod is not practical due to the layout of the building..............So they want to just bond this building steel. I know this isn't required, but do you think it permitted? Do you think the bond wire would be required to meet the NEC rules for GEC's?

Okay, you're in a tricky spot. You're right, what the customer wants isn't always what's necessary or correct according to code and best practices. Let's break this down

1. Understanding the Customer's Motivation (and Addressing It):
Find out WHY they want it grounded. This is crucial. Is it a perception of safety? Are they concerned about static electricity buildup? Understanding their concerns will help you address them appropriately. They might be misinformed or have a specific risk in mind. Explain the Existing Grounding System

Clearly explain how the building's electrical system is already grounded, and how the vending machine's equipment grounding conductor (EGC) connects to that system. This is usually enough for most people.

2. Grounding the Vending Machine (Already Grounded)

As you stated, the vending machine should already be grounded through the EGC in its power cord/conduit. Verify this by:

Checking the power cord

Ensure it's a 3-wire cord with a grounding pin, and that the receptacle is properly wired and grounded.

Using a multimeter

Test the resistance between the vending machine's metal frame and a known good ground (like the grounded receptacle's ground slot). You should see very low resistance (ideally close to 0 ohms).

3. Grounding the Flammable Storage Cabinet (Probably Not Necessary)



Flammable storage cabinets generally don't require additional grounding, unless the manufacturer specifies it.
This is important. Read the manufacturer's instructions for the cabinet. If the instructions don't say to ground it, don't do it. Static Electricity

If the concern is static buildup in the cabinet, address that directly. Grounding
might help, but there are other (possibly better) solutions:

Anti-static mats

Place an anti-static mat inside the cabinet.

Humidity control

Increasing humidity can reduce static buildup.


Proper ventilation

To prevent the buildup of flammable vapors.

Bonding within the cabinet

Make sure the shelves and any metal containers within the cabinet are bonded to each other and to the cabinet frame.

4. Can you ground them to building steel?
NEC Perspective

The NEC is primarily concerned with electrical safety as it relates to the power distribution system. Grounding objects that aren't part of the electrical system isn't directly addressed by the NEC, as long as it doesn't compromise the existing grounding system.

The concern becomes how you connect to the steel.
If you do it improperly, you could create a hazard. You can bond (connect) non-electrical metallic objects to the building steel. However, consider the possibility of unintended consequences: Path of Least Impedance

If a ground fault occurs in the building's electrical system, you don't want the fault current traveling through the building steel (and then your bond wire). This can create a shock hazard.

Permitted, but with Caveats



It is likely permitted, but not required, and only if done safely.
You need to be very careful to not create a situation that could introduce fault current onto the building steel or compromise the existing grounding system. Bond wire rules NEC 250.64(E) states, "Where a service raceway, cable tray, auxiliary gutter, or busway is used as the grounding electrode conductor, it shall comply with 250.64(A), (B), and (C). It should be a conductor of sufficient size for your installation In general, you'd want to select a conductor size suitable for it's function as an equipment grounding conductor. Table 250.122 can be used. Keep in mind, a smaller conductor can be used when the overcurrent protective device is reduced.5. Recommendations


EDUCATE THE CUSTOMER.
Start by explaining the existing grounding system and why additional grounding is likely unnecessary.2. ADDRESS THEIR CONCERNS. Find out why they think additional grounding is needed.3. READ MANUFACTURER'S INSTRUCTIONS. This is critical for the flammable storage cabinet.4. IF YOU MUST BOND TO BUILDING STEEL (against my better judgment)



Use a qualified electrician.
This is not a DIY project. Ensure the connection to the steel is solid and corrosion-resistant. Use appropriate bonding hardware (e.g., exothermic welds, listed grounding clamps). Use an appropriately sized equipment grounding conductor (EGC). Reference NEC Table 250.122. This will be sized based on the overcurrent protection device feeding the circuit that could fault to the item being grounded. Make the bonding connection as short and direct as possible. Document everything. Note the customer's request, the work performed, and the reasons why it was (or was not) code-required.5. Consider Alternatives

Explore alternatives like anti-static mats, humidity control, and proper ventilation, especially for the flammable storage cabinet.6.

GET IT IN WRITING.
If the customer insists on something that you don't believe is necessary or that might be marginally compliant, get their request in writing, acknowledging that you've advised them otherwise.

Important Considerations



Local Codes

Always check your local electrical codes and regulations. They may have specific requirements.


Professional Liability:
Be aware of your professional liability. If you do something that's not code-compliant or that creates a hazard, you could be held responsible.In summary, while bonding to building steel might be permissible in this situation, it's likely not necessary, and it needs to be done carefully by a qualified electrician to avoid creating a safety hazard. Educating the customer, addressing their concerns, and exploring alternative solutions are the best first steps. Flag for review