Topic: EGC working in parallel with Grounding grid

User: jsim, Location: Venezuela

Asked on: Thursday, August 14, 2025 at 3:26 pm EDT
Answered on: Thursday, August 14, 2025 at 3:35 pm EDT

Question: Greetings,From what I read in previous forum threads, I understand a grounding grid can't be used to replace the equipment grounding conductor in a installation. (Primarily due to the non cancellation of magnetic fields due to the separation of the source and return conductors)But, can the EGC work in parallel with a grounding grid? For example: imagine a main AC Panel, electrically joining the neutral with the ground bus bar and the ground bus bar connected to a grounding grid. Then that AC Panel feeds another sub-panel elsewhere, giving it phase, neutral and EGC, connecting that EGC to this subpanel's ground bar, then connnecting that ground bar to the grounding grid.In the event of a ground fault after the sub-panel, current would flow from the phase conductor through a normally non-current carrying metallic case, then through the EGC into the subpanel then at the sub-panel it will encounter two paths:- The EGC to the main panel then to the main panel's neutral and,- Another path through the grounding grid into the main panel's ground bus bar to the main panel's neutralhttps://imgur.com/a/XQvsFLw

Yes, your understanding is correct. Let's break down why.1. EGC is Mandatory, Grounding Grid is Supplementary

The Equipment Grounding Conductor (EGC) is always required for creating a low-impedance fault current path back to the source, which is essential for the overcurrent protective device (circuit breaker or fuse) to trip quickly and clear the fault. A grounding grid (also called a grounding electrode grid or ground mesh) is supplementary to the EGC. It's designed to provide safety by: Equipotential bonding of the ground. Stabilizing the ground potential relative to remote earth. Dissipating fault current into the earth. Providing a path for static electricity. Helping to mitigate touch and step potential hazards.

2. EGC in Parallel with Grounding Grid – the Reality

Yes, the scenario you describe is absolutely how systems are often designed and how they function in practice. Here's why it works and is beneficial:


Parallel Paths Reduce Impedance

When a ground fault occurs, current will split between the EGC and the grounding grid, following the path of least impedance. While the EGC provides the primary low-impedance path for fault clearing, the grounding grid provides an additional path. This reduces the overall impedance of the fault current path, potentially helping the overcurrent device operate even faster.

Equipotential Bonding and Safety

The grounding grid connects multiple points to a common ground potential. This minimizes voltage differences between equipment and structures during a fault, reducing the risk of electric shock.


Mitigating Step and Touch Potentials

The grounding grid helps distribute fault current over a larger area, lowering the ground potential rise (GPR) and reducing step and touch potentials.

3. Key Considerations and Caveats



Proper Design and Installation

The grounding grid must be designed and installed correctly according to applicable standards (e.g., IEEE 80, IEC 61936-1) to be effective. This includes proper grid spacing, conductor size, and connections to the earth.


EGC Size and Integrity

The EGC must still be sized according to the code (NEC in the US) for the fault current it is expected to carry. The grounding grid does not allow you to reduce the size of the EGC. The EGC must also be continuous and electrically sound.

Ground Resistance

While a low ground resistance (resistance between the grounding grid and remote earth) is desirable, it's
not the primary factor in clearing ground faults. The EGC's low impedance is what's critical for tripping the breaker. The grid primarily affects the touch and step potential safety and the GPR.

Bonding

All metallic equipment and structures within the grid area must be properly bonded to the grid to create a true equipotential zone.

Single Point Grounding

In sensitive electronic installations, single-point grounding may be preferable to a grid in order to minimize circulating currents. This depends on the application.

4. Why Your Thinking is Correct

You correctly identify the two paths for fault current in your scenario:1.

EGC Path

Fault -> Equipment Case -> Subpanel EGC -> Main Panel EGC -> Main Panel Ground Bus -> Neutral-Ground Bond -> Neutral2.

Grounding Grid Path

Fault -> Equipment Case -> Subpanel EGC -> Subpanel Ground Bar -> Grounding Grid -> Main Panel Ground Bar -> Neutral-Ground Bond -> NeutralBecause electricity takes all paths available, the total current will divide between those paths based on the impedance of each path.

In summary:


A grounding grid
cannot replace the EGC. The EGC provides the primary low-impedance fault current path. However, a grounding grid significantly enhances* the safety and performance of the grounding system by providing additional fault current paths, reducing impedance, and creating an equipotential zone. The two work together. Flag for review