User: Isaiah, Location: Baton Rouge
Asked on: Friday, August 15, 2025 at 6:37 am EDT
Answered on: Friday, August 15, 2025 at 6:40 am EDT
Question: We have a 3phase, 3wire bus duct coming from the secondary side of an ungrounded delta-delta transformer, 13.8kV to 480V. Shouldn’t this be a 4 wire secondary to account for the SSJB connection NEC 250.30?Enviado desde mi iPhone utilizando Tapatalk
You're correct to be questioning this. The situation you describe is problematic and doesn't easily comply with the NEC. Let's break down why and what needs to happen
Understanding the Problem
Ungrounded Delta-Delta Secondary
With an ungrounded delta secondary, there's no intentional connection to ground at the transformer itself. This means there's no reference point for voltage relative to earth. This is inherently a problem for safety because a single ground fault on the system can elevate the voltage of the unfaulted phases relative to ground.
SSBJ (System Bonding Jumper) and NEC 250.30
NEC 250.30 requires a separately derived system (SDS), like your transformer secondary, to have a grounding electrode conductor (GEC) connected to the grounding electrode system. The link between the secondary neutral (even though you don't have a neutral in a straight delta) and the grounding system is the System Bonding Jumper (SBJ). The SBJ essentially creates the reference to ground.
3-Wire vs. 4-Wire
A 3-wire delta system by definition does not have a neutral conductor to connect the SBJ. A 4-wire system (e.g., Wye) would provide a neutral.
Why a 3-Wire Ungrounded Delta is a Problem for Safety and Code Compliance1. Lack of Ground Fault Path
Without a grounding electrode system properly bonded through a SSJB the system will float voltage, making it nearly impossible for overcurrent protection devices to operate reliably when a ground fault occurs. This increases the risk of electrical shock and fire.2.
Voltage Stress
Without a grounding reference, a single line-to-ground fault can cause the unfaulted phases to rise to line-to-line voltage with respect to ground. This can stress insulation and damage equipment.3.
Code Violation
It's very difficult to make a 3-wire ungrounded delta system comply with NEC 250.30 and related sections regarding grounding and bonding of separately derived systems.
Solutions and Recommendations
Here's what you should do:1. Change to a Grounded System
This is the strongly recommended approach. The best solution is almost always to modify the transformer secondary configuration to create a grounded system. Here are the options:
Delta-Wye
This is often the best solution. Change the transformer to a delta-wye configuration (13.8kV delta primary, 480V wye secondary). This inherently creates a neutral point that must be grounded, giving you a 4-wire system. You can then run a 4-wire bus duct (A, B, C, Neutral) from the transformer to your load centers. The neutral is then bonded to ground through the SSBJ and the GEC to earth at the transformer's secondary.
Corner-Grounded Delta
While less common, you could ground one corner (one of the phase conductors) of the delta secondary. This turns one of your phase conductors into a "grounded" conductor. However, this has significant drawbacks: It complicates the design and implementation of overcurrent protection. It requires careful labeling of the grounded phase conductor. It can create confusion and increase the risk of accidental shorts to ground. It's generally not recommended unless there's a very specific reason and a good understanding of the implications.In this configuration one of the three phase conductors is bonded through a SSJB to the GEC to the grounding electrode system. The phase conductor is now the grounded conductor for the separately derived system.2.
High-Resistance Grounded Delta (HRG)
A High-Resistance Grounded Delta (HRG) system is another option. In this setup, a resistor is connected between the delta corner (or a neutral point derived from zig-zag grounding transformer) and ground. This limits the ground fault current to a relatively low value (typically 5-10 amps). HRG systems provide some level of ground fault protection but still allow the system to operate for a short period with a single ground fault. This allows for scheduled shutdown rather than immediate tripping. They require a ground fault monitoring system to detect and alarm on ground faults. They are more complex and costly than a simple grounded system.
HRG still requires compliance with NEC 250.30 and related sections.Important Considerations
Consult an Electrical Engineer
Crucially, consult with a qualified electrical engineer familiar with power system grounding. Choosing the right solution depends on your specific load requirements, existing equipment, and safety priorities. They can perform a power system study to determine the best grounding method for your application.
NEC Compliance
Ensure that any changes you make are fully compliant with the NEC (National Electrical Code) and any other applicable local codes.
Ground Fault Protection
Regardless of the grounding method, you must have appropriate ground fault protection in place. This typically involves ground fault relays and breakers to quickly isolate ground faults and prevent damage.*
Bonding
Proper bonding of all metallic enclosures, conduit, and equipment grounding conductors is essential to provide a low-impedance path for fault currents.
In summary, running a 3-wire bus duct from an ungrounded delta secondary without a system grounding connection is a code violation and creates a significant safety hazard. You need to change the system configuration to a grounded system and ensure proper grounding and bonding throughout the electrical system. Flag for review