Topic: Wire size for control panel

User: FlatStanley, Location: Portland Oregon

Asked on: Friday, August 15, 2025 at 10:01 am EDT
Answered on: Friday, August 15, 2025 at 10:16 am EDT

Question: We are about to run wire for some preassembled control panels for a motor and pump we are confused. The motor is a 10 hp, 480 volt. Which would only be 14 amps. However the control panel has a sticker on the front saying the motor is 2 amps. It also calls for 60 amps even though the control circuit is only 5 amps. Where are they getting these numbers from? How do I determine my wire size?https://imgur.com/a/5npedSC

Let's break down the likely scenarios and how to approach this

Understanding the Discrepancies
Motor Current Discrepancy (14A vs. 2A)

This is the biggest red flag. A 10 HP motor at 480V
will draw around 14 amps (refer to the NEC table 430.250 for exact full-load current). The 2A sticker on the control panel is almost certainly not the motor's full-load current. It could be the current drawn by the control panel's internal components.

60A Requirement

This is likely related to a combination of factors:

Motor Starter Overload Protection

The motor starter in the control panel needs to provide overload protection for the motor. The breaker ahead of the control panel must be sized appropriately for the motor's FLA and the overload protection rating. This breaker needs to be sized large enough to handle the
inrush current (also called locked-rotor current) of the motor. Motor inrush can be 6-8 times the full-load current.

Control Panel Components

The control panel itself may have other components (relays, contactors, small transformers, etc.) that contribute to the overall amperage draw.

Future Expansion

The panel could be designed to accommodate other equipment in the future.

Steps to Determine Wire Size (Important - Follow all applicable Electrical Codes!)
1. Identify the Motor's True Full-Load Amps (FLA)


Crucially, verify the nameplate rating of the motor itself.
This is the definitive answer. If you can't access the nameplate, use NEC Table 430.250 (Three-Phase AC Motors) to find the FLA for a 10 HP, 480V motor. It will be around 14 amps.
2. Determine the Overload Protection Size

The overload relay should have an adjustable range that will protect the motor at 125% of the FLA. For the motor, use table 430.52 to determine the breaker for the motor protection3.

Understand the Control Panel's Sticker



DO NOT ASSUME the 2A on the sticker is the motor current.
It is almost definitely not the motor's current. The sticker is telling you that the entire control panel, including the motor, requires a 60A overcurrent protection device (breaker or fuses) feeding into the control panel.4. Calculate Wire Size for the Motor Branch Circuit



General Rule

NEC Article 430 dictates motor circuit conductor sizing. The conductors supplying a single motor must have an ampacity of at least 125% of the motor's FLA.

Example

If the motor FLA is 14A, the minimum conductor ampacity is 14A
1.25 = 17.5A.

NEC Table 310.16

Use this table to select the appropriate wire size based on the ampacity you calculated (17.5A in the example above). Consider the insulation type (THHN is common) and the ambient temperature. For this example with THHN wire, you'd likely use #14 AWG copper (rated for 20A) or #12 AWG aluminum.
However, read on, because other factors may require larger wire.5.

Calculate Wire Size for the Control Panel Input

The 60A requirement means the conductors feeding into the control panel must be rated for at least 60 amps. Again, use NEC Table 310.16 to determine the wire size. With THHN, you'd need at least #4 AWG copper (rated for 70A) or #2 AWG aluminum.
6.


Consider Voltage Drop

For longer runs, calculate voltage drop to ensure it's within acceptable limits (typically 3% for power circuits, 5% total). Voltage drop can require larger wire sizes than the ampacity calculation alone. Use a voltage drop calculator or consult with an electrician.7.

Account for Conduit Fill

If running conductors in conduit, ensure the conduit isn't overfilled. NEC Chapter 9 provides conduit fill tables.8.

Grounding

You must have a properly sized equipment grounding conductor (EGC) running with the circuit conductors. Consult NEC Table 250.122.

Summary and Recommendations
1. VERIFY MOTOR NAMEPLATE

This is non-negotiable. Get the exact FLA from the motor nameplate.2.

Consult an Electrician

If you're unsure about any of these calculations or interpretations, hire a qualified electrician. Motor circuits are safety-critical, and incorrect wiring can lead to equipment damage, fire, or personal injury.3.

Document Everything

Keep a record of all calculations, wire sizes, breaker sizes, and code references for future reference.

In summary, you likely need two different sets of wiring



Wiring feeding the control panel

Sized for 60A (as indicated on the panel). This is likely #4 AWG copper or #2 AWG aluminum with THHN insulation, but verify based on conduit type, ambient temperature, and voltage drop calculations.


Wiring from the control panel to the motor:
Sized based on 125% of the motor's FLA (which should be about 14A). This might be #14 or #12 AWG, but always check based on calculations, NEC tables, and voltage drop. Flag for review