Question: must i use grounding jumper from the rec, to the metal box, all conduit 2020 nec. ??????????????????????????????????????????????????????????????

Okay, let's break this down according to the 2020 NEC. Your question is about the requirement for a grounding jumper (equipment bonding jumper) from a receptacle to a metal box when using metal conduit.

The Short Answer (Generally)



Yes
, in most cases, you DO need an equipment bonding jumper (grounding jumper) from the receptacle grounding terminal to the metal box unless the box is considered to be reliably grounded through the conduit connection itself. How the box is grounded thru the conduit depends on the conduit and fittings used.

Here's the longer, more detailed explanation based on the 2020 NEC


The Principle: Effective Ground-Fault Current Path
The primary goal of grounding/bonding is to create a low-impedance path for fault current to flow back to the source (transformer or panel) during a ground fault. This allows the overcurrent protective device (circuit breaker or fuse) to quickly trip and clear the fault, minimizing the risk of shock or fire.2. Metal Conduit as an Equipment Grounding Conductor (EGC) Metal conduit (RMC, IMC, EMT) can serve as the equipment grounding conductor if it is properly installed with listed fittings. NEC 250.118 lists the acceptable types of equipment grounding conductors. Metal conduit (RMC, IMC, EMT) is on that list.3. Bonding the Receptacle to the Box: The Critical Question Even if the metal conduit is serving as the EGC, you still need to ensure the receptacle is reliably bonded to the box. NEC 250.146 addresses connecting receptacle grounding terminals to boxes. It essentially says: 250.146(A) Surface-Mounted Box

For surface-mounted boxes, the receptacle must be bonded to the box, and the box must be grounded (usually through the conduit). This is often achieved with a bonding jumper from the receptacle grounding screw to a screw on the box.


250.146(B) Flush-Mounted Box

For flush-mounted boxes (recessed in the wall), there are a few options:

Yoke Contact

Receptacles listed as self-grounding. These receptacles make reliable ground contact with the box when properly installed. The yoke of the receptacle must make direct metal-to-metal contact with the box. Paint, coatings, or corrosion prevent metal-to-metal contact. If the box is not grounded (for example, using a nonmetallic cable feeding a metal box with conduit running onward), a jumper wire must be installed from the box to the receptacle's grounding screw.


Jumper Wire

Use a bonding jumper from the receptacle grounding terminal to a grounding screw on the box. This is the most common and reliable method.

Other Listed Means

There might be other listed methods approved by the authority having jurisdiction (AHJ), but these are less common.4.

Why the Jumper is Often Needed (Even with Metal Conduit)
Corrosion/Looseness

Over time, the connection between the conduit and the box can corrode or loosen, reducing the effectiveness of the ground path. The bonding jumper provides a redundant, more direct path.

Paint/Coatings

Paint or other non-conductive coatings on the box can prevent good electrical contact between the receptacle yoke and the box.


Flush-Mounted Boxes

Flush-mounted devices often need a jumper wire because the contact area between the device yoke and the box is not always considered reliable enough without it.5.

Exception (Potentially)

If using self-grounding receptacles in a flush-mounted box and you are absolutely sure that the box is reliably grounded through the conduit and fittings, and there is perfect metal-to-metal contact between the receptacle yoke and the box (no paint, corrosion, etc.), you might be able to argue that a jumper is not strictly required.

However, this is generally NOT recommended and is often rejected by inspectors.
It is always better to install the bonding jumper.

In Summary



Always install a bonding jumper from the receptacle grounding terminal to the metal box, unless the receptacle and box combination are specifically listed for grounding without a jumper.
This is the safest and most reliable way to ensure proper grounding and bonding. It avoids any potential issues with corrosion, loose connections, or coatings that could compromise the ground path. It's a small extra step that provides a significant safety benefit.

Important Considerations



Local Codes and AHJ

Always check with your local electrical codes and the authority having jurisdiction (AHJ) for their specific requirements. They may have more stringent rules than the NEC.*

Inspection

The electrical inspector has the final say on whether your installation meets code. It's always best to err on the side of caution and install the bonding jumper.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Always consult with a qualified and licensed electrician for any electrical work. They can assess your specific situation and ensure that your installation complies with all applicable codes and regulations. Flag for review