Question: Looking at a house with a 100 amp feed to a main lug panel in a detached garage.4-wire feed to the panel from the house6 Spaces, 6 breakers in useUnbondedNo EGC in place (easy fix)Panel was installed maybe 15-20 years ago based on what I think is a date code.Aside from local inspectors who might have said ok based on a misinterpretation with there being 6-throws, was this ever allowed (or not explicitly prohibited)?Seems like one of those 'probably ok but not compliant' situations if I assume it was actually inspected at installation.Opinions appreciated.Dave
Okay, Dave, let's break down this detached garage electrical situation. You've highlighted some key observations, and I'll give you my opinion based on the NEC (National Electrical Code), keeping in mind that local interpretations always prevail.
Here's a summary of what you've described
100 Amp Feed
4-wire feed (L1, L2, Neutral, Ground) from the house.
Main Lug Panel
In the detached garage.
6 Spaces/Breakers
Seems fully utilized
Unbonded
The neutral bar and panel enclosure are not bonded together.
No EGC
No equipment grounding conductor running to the panel.
Age
Approximately 15-20 years old.
The Core Question
Was this ever allowed, or at least not explicitly prohibited?
Analysis & My Opinion
The EGC (Equipment Grounding Conductor) issue is critical and the biggest problem. This is the primary safety concern. Having an EGC is mandatory for a detached garage's subpanel fed from another building. It provides a low-impedance path for fault current to return to the source, tripping the breaker and preventing dangerous voltage on metal parts of equipment. NEC 250.32(A) requires an equipment grounding conductor run with the feeder to a detached building. Unbonded Panel
A detached garage subpanel must have the neutral isolated from the enclosure and ground. The neutral should be bonded to the enclosure ONLY at the service entrance panel in the main building. This is to prevent parallel neutral paths.
6 Spaces/Breakers
The number of spaces is irrelevant to the legality of the initial installation (assuming the load calculations were correct for the 100A feed). However, if you're already maxed out, future expansion will likely require upgrading the panel.
The "6 Disconnects" Myth
The "6 disconnect rule" (allowing up to six circuit breakers to serve as the main disconnect) applies to service entrance equipment in a single-family dwelling. It does not apply to a subpanel in a detached garage. This is a common misunderstanding. This panel should have a main breaker to act as a disconnect.
Was it ever allowed? Here's where it gets nuanced. Back 15-20 years ago, NEC requirements for detached garages were generally the same as today. The EGC was required. The separated neutral was required. The main breaker in the panel (disconnect) was required. Therefore, it's unlikely this would have been explicitly allowed if inspected and done to code. It's more likely a misinterpretation or oversight. "Probably OK but not Compliant"
Your assessment is accurate. It may have "worked" without problems, but it was never fully compliant and is unsafe.
Possible Explanations for Passing Inspection (If it did)
Oversight
Inspector missed the lack of EGC and/or the bonding issue.
Misunderstanding
Someone claimed it was a simple circuit extension and not a "feeder" to a detached building.
Older Code Interpretation
Very unlikely that anything in the NEC 15-20 years ago would have allowed this configuration. Code language may have been slightly different, but the intent for safety was the same.
No Inspection
The work was done without permits or inspections, and nobody ever checked it.
Ground Rods
The panel needs to be grounded at the detached garage.
NEC 250.32 (A)
For a detached building, "an equipment grounding conductor shall be run with the supply to the detached building or structure, and shall be connected to a grounding electrode system."
NEC 250.52
The grounding electrode system includes things like ground rods, ground rings, metal underground water pipes, or concrete-encased electrodes.
What to do
Correct the Grounding
Immediately install an EGC (equipment grounding conductor) from the main panel in the house to the subpanel in the garage. This is essential. Ensure it's sized according to NEC Table 250.122 based on the overcurrent device (100A).
2.
Separate Neutrals and Grounds
Make sure the neutral and ground are isolated from each other at the detached garage subpanel.3.
Ground Rods
Install ground rods at the detached garage and connect them to the ground bar in the subpanel.4.
Consider a Main Breaker
While not strictly required if you want to replace some breakers so that the main panel has open spaces, I would recommend installing a main breaker in the panel to act as the disconnect, especially if you're going to be using the garage for something like a workshop where you might have power tools and equipment.5.
Load Calculation
Double-check that the 100A feed is adequate for the loads in the garage. If you plan to add circuits, you may need to upgrade the feed.6.
Consult a Qualified Electrician
This is highly recommended. Let a licensed electrician assess the whole setup and make sure everything is compliant with current NEC requirements and local codes.7.
Local Inspection
Once the work is done, have it inspected by your local electrical inspector.
In conclusion: While you may have gotten away with this setup for a while, it's not safe or code-compliant. Correct the grounding issues immediately. Consult with a qualified electrician to ensure everything is done correctly and safely. Flag for review