User: Jpflex, Location: Victorville
Asked on: Monday, August 18, 2025 at 10:41 am EDT
Answered on: Monday, August 18, 2025 at 10:41 am EDT
Question: I was wandering if what i believe to be rigid metal conduit and an LB body going to pv inverter boxes are a code violation?I see that there are no support or securing straps withinn 3 feet of box termination or 10 feet for the conduit for every inverteron site.I do recall that somewhere else in NEC code allows certain sized conduit bodies to be considered supported and secured if RMC is the conduit used but this exemption should no not allow full lengths of RMC to be free standing?The entire photovaltaic field has all invwrters this way. Do inspectors just overlook these things?
You're right to question the installation. Here's a breakdown of the relevant NEC rules and why your concerns are valid
Key Issues:
Support and Securing of RMC
Rigid Metal Conduit (RMC) must be properly supported and secured. You correctly point out the general rule: NEC 344.30(A): RMC shall be supported at intervals not exceeding 10 feet (3 m). NEC 344.30(B)(1): RMC shall be supported within 3 feet (900 mm) of each box, cabinet, conduit body, or other termination.
Conduit Body Support (LB Exemption)
There is an exception that applies to conduit bodies, but it's often misunderstood: NEC 314.40(E)(5): Conduit bodies with one or more conduit hubs not larger than the trade size of the conduit to which they are attached are permitted to be supported by the conduit. They shall be permitted to be supported as if they are conduit, provided the conduit is supported within 3 feet of the box on each side.
This means if the LB is supporting the RMC AND the RMC is properly supported within 3 feet of the LB (on both sides), then the LB itself doesn't necessarily need additional support.
Why Your Situation is Likely a Violation
No Support Within 3 Feet
You state there are NO supports within 3 feet of the inverter boxes and NO supports at all for 10-foot RMC runs. This violates NEC 344.30(A) and (B)(1).
LB as Sole Support
The LB body is not intended to be the sole support for long runs of RMC. It's designed to provide access for wiring, not to bear significant weight and prevent sagging. The exception in 314.40(E)(5) only applies if the RMC itself is supported appropriately within 3 feet of the LB on BOTH sides.
Sagging/Mechanical Stress
Unsupported RMC can sag over time. This puts stress on the connections at the inverter box and the LB body, potentially leading to loose connections, water ingress (if outdoors), and even damage to the inverter itself.
Why This Matters
Safety
Proper support prevents the conduit from coming loose, which could create a shock hazard or damage equipment.
Reliability
Stress on the conduit system can lead to premature failure of connections and wiring.
Code Compliance
An installation that doesn't meet the NEC can be rejected by inspectors and may void warranties.
Why Inspectors Might Miss It (And Why They Shouldn't)
Workload
Inspectors are often very busy and may not catch every detail.
Difficulty Accessing
Sometimes, the back of an inverter or the layout of the PV array makes it difficult to visually inspect the conduit supports.
Assuming Compliance
An inspector might assume the installer knew the rules and followed them, without carefully checking.
Lack of Specific PV Expertise
Some inspectors may be more familiar with general electrical installations and less familiar with the nuances of PV systems.
What You Should Do
Document
Take photos of the unsupported RMC runs, focusing on the lack of support within 3 feet of the inverter boxes and the long unsupported spans.2.
Communicate
If you are involved in the project contact the installation contractor directly. Explain your concerns, show them the photos, and cite the NEC sections (344.30(A), 344.30(B)(1), 314.40(E)(5)). Give them the opportunity to correct the issue.
3.
Report (If Necessary)
If the contractor doesn't address the issue, you may need to contact the local electrical inspection authority. Provide them with the documentation you've gathered.
In summary, it is highly likely that the installation you describe violates the NEC due to inadequate support of the RMC conduit. It's important to address this issue to ensure the safety, reliability, and code compliance of the PV system. Flag for review