Question: Hi all,We're getting ready to do and install on a new home, however this one has metal (steel) siding instead of vinyl or wood which is what we're use to.Mounting the Meter (320a) and two Disconnects (200a ea) is not the issue as it's metal board and batten and all fit fine directly onto the metal panels.However, looking up to see if the meter can and disconnects need to be isolated from the walls, I'm getting conflicting information.We have a bonded ground going from one disconnect box to 2 ground rods and back up to the second disconnect. But putting both disconnects and the meter can all onto the metal siding is effectively bonding them all together?Most people are saying this is the norm, a select few are saying they need to be isolated from the siding.Thoughts?Thanks all!
You're right to question this and seek clarification. Here's a breakdown of the situation and what to consider, along with code references to look into
The Core Issue: Bonding vs. Isolation
Bonding
Ensures all metallic parts that could become energized are electrically connected, providing a low-impedance path back to the source. This is crucial for safety, allowing overcurrent devices (breakers) to trip in the event of a fault.
Isolation (in this context)
This would mean preventing any unintended electrical connection between the electrical equipment enclosures and the metal siding.
The General Consensus: Bonding is Usually Required, Not Isolation
Generally, you want to bond metal enclosures to the metal siding in a residential application. The rationale is that the metal siding itself could become energized due to a fault, and bonding it to the electrical system's grounding electrode system ensures that the fault current has a path to trip the breaker.
Why the conflicting information?
The confusion likely arises from a few factors: Different Interpretations
Electrical codes can be open to interpretation by different inspectors.
Specific Local Requirements
Some municipalities or regions have specific requirements that go beyond the NEC.
Misunderstanding of Isolation
The idea of "isolation" might be confused with concerns about dissimilar metals causing corrosion (addressed below).
Key Considerations and Code References (Consult the latest NEC and local codes)
NEC 250.130(C) Equipment Grounding Conductor Connections
This section deals with methods for grounding equipment, specifically non-current-carrying metal parts of equipment. You should be connecting the metal enclosures (meter can, disconnects) to the grounding system.2.
NEC 250.134(B) Metal Enclosures
Metal enclosures containing service conductors must be grounded.3.
NEC 250.92(A)(1-4) Service Equipment
This section outlines the requirements for bonding service equipment. In your case, the meter can and disconnects are service equipment and must be bonded to the grounding electrode conductor.4.
NEC 250.24(A)(5) Grounded Conductor Brought to Service Equipment
The grounded conductor (neutral) must be bonded to the service equipment enclosure and the grounding electrode conductor at the service.5.
Verify Local Codes
This is the MOST IMPORTANT step. Contact your local electrical inspector and ask about their specific requirements for grounding electrical equipment to metal siding. They will have the final say.
Practical Implementation and Best Practices
Ensure Good Grounding
Your ground rod system sounds correct (two ground rods at least 6 feet apart). Ensure the connections to the ground rods and the grounding electrode conductor are properly made (exothermic welds or listed clamps).
Bonding Jumper
You may need to run a bonding jumper from the grounding electrode conductor to the metal siding itself to ensure it's properly bonded. Consult with your inspector on the appropriate size and connection method.
Consider Corrosion
Where dissimilar metals (e.g., steel siding and aluminum meter can) are in contact, consider using an anti-corrosion compound (like Penetrox or Noalox) to prevent galvanic corrosion. This isn't about electrical isolation, but about protecting the connections and the integrity of the materials.
UL Listing
Ensure all equipment you use (connectors, clamps, etc.) is UL listed for its intended purpose and for use with the specific metals involved.
Steps to Take
Contact Local Electrical Inspector
This is the most important step. Explain your situation and ask for their specific requirements.2.
Review NEC 250
Familiarize yourself with Article 250 of the National Electrical Code (NEC) regarding grounding and bonding.3.
Document Everything
Keep detailed records of your conversation with the inspector and any specific instructions they provide.4.
Proper Installation
Follow the NEC, local codes, and manufacturer's instructions for all equipment installations.5.
Inspection
Be present during the electrical inspection to answer any questions the inspector may have.
In summary: In most cases, bonding the meter can and disconnects to the metal siding is* the correct approach, ensuring a low-impedance fault current path. However, you MUST verify this with your local electrical inspector. Also, address any potential corrosion issues with the use of appropriate compounds and listed connectors. Flag for review