Topic: Bonding between two electrical services.

User: M_Verrando, Location: Ocala, Fl

Asked on: Monday, August 18, 2025 at 11:19 am EDT
Answered on: Monday, August 18, 2025 at 11:32 am EDT

Question: I have two buildings, each with separate electrical services. The Main Electrical Services are separated by roughly 560 feet. The Owner would like to install a single standby power generator to power loads in both buildings. Can the Main Grounding Electrodes for both electrical services be bonded, to permit the use of a solid, non-switched neutral, and if so how is the bonding conductor sized?

This is a common scenario, and it's definitely possible to use a single generator for two buildings with separate services. Here's a breakdown of the requirements and considerations based on the NEC (National Electrical Code)

Yes, you can bond the Grounding Electrode Systems (GES) to permit a solid neutral in the transfer switch, however there are some potential hazards

The Goal: Ensuring Safety and Proper Operation

The main goal is to create a safe and properly functioning system that minimizes voltage differences between the two buildings during both normal and generator operation. Bonding the GES systems together plays a crucial role in this. Here's why you'd want to do that (or why you might not want to... discussed below): Equalizing Potential

Bonding minimizes voltage differences between the two buildings' grounding systems, reducing the risk of touch potential hazards if a fault occurs in either building.


Proper Generator Operation

A solid neutral (non-switched) with a properly bonded GES is essential for the generator to detect ground faults and operate its overcurrent protective devices correctly. A floating neutral could lead to dangerous fault currents that don't trip breakers.

NEC Requirements and Considerations


Here's a breakdown of the relevant NEC sections and how they apply to your situation: NEC 250.32 Buildings or Structures Supplied by a Feeder or Branch Circuit. This is the key section for your situation. It dictates how separately derived systems (like your generator acting as a standby power source) are to be grounded at each building. NEC 250.32(A): Grounding Electrode System. You essentially have two options:1. (1) Grounded Conductor. You can connect the generator neutral to a grounding electrode system at each building. This is what you want. That means each building needs a grounding electrode (ground rod, water pipe, etc.) that meets the requirements of NEC 250.52. These are already in place at your service and you will be bonding them to the generator.
2. (2) Equipment Grounding Conductor. If you cannot use a ground electrode system in each building, then you must run an equipment ground from the generator to each building and bond to the first means of disconnect. NEC 250.32(B) Grounding Electrode Conductor for Alternating-Current Systems. The grounding electrode conductor is what bonds the generator's neutral to the grounding electrode at each building. NEC 250.64(E) Installation of the bonding jumper. Allows the GEC to be run exposed along the exterior of the building. NEC 250.102 Bonding Jumpers and System Bonding Jumpers. This section covers the sizing of bonding jumpers.

Sizing the Bonding Conductor (GEC)

The bonding conductor between the generator neutral and each building's grounding electrode system is sized according to NEC 250.66. Here's the process:1. Determine the size of the generator's ungrounded conductors (the phase conductors). This is the primary factor in determining the GEC size.2. Consult Table 250.66 in the NEC. This table provides the minimum size of the grounding electrode conductor based on the size of the largest ungrounded conductor. You read across from the ungrounded conductor size to find the required GEC size for copper or aluminum.3. Example

If the generator's phase conductors are 3/0 AWG copper, Table 250.66 will likely require a #2 AWG copper grounding electrode conductor.
Always consult the table for the specific conductor sizes.4.

Enclosure for GEC
The GEC and bonding jumper should be run in conduit or otherwise protected from physical damage.5. Termination Be sure to use listed lugs and connectors approved for grounding and bonding purposes at all termination points.

Critical Considerations and Potential Problems
Existing Grounding Electrode Systems

You must ensure that each building's grounding electrode system is properly installed and meets the requirements of NEC 250.52. This typically means a ground rod driven at each building, or connection to a metallic water pipe. If the existing electrodes are inadequate, you will need to supplement them.

Voltage Drop

At 560 feet, you need to carefully calculate the voltage drop for the generator feeders. This will influence the conductor size you choose. Undersized conductors will lead to poor performance and potential equipment damage. Use a voltage drop calculator (available online) and consider using larger conductors to minimize voltage drop. Aim for a voltage drop of no more than 3% from the generator to the farthest load.


Overcurrent Protection

The generator's overcurrent protection (circuit breakers) must be properly sized to protect the generator and the feeder conductors. Coordinate the breakers at the generator and at each building's main disconnect to ensure selective coordination (the breaker closest to the fault should trip first).

Transfer Switches

Ensure that the transfer switches are suitable for use with a solid neutral system. Most automatic transfer switches are designed for this, but manual transfer switches can vary.


Conductor Type

Typically, THHN/THWN conductors are used for this type of installation.

Permitting and Inspection

This work
requires a permit and inspection by your local electrical authority. They will verify that the installation meets all applicable codes and regulations.

DANGERS of Interconnecting Grounding Systems (IMPORTANT)


While bonding the grounding systems is
often required, it's crucial to understand the potential hazards and why it might not be the best approach in some circumstances: Stray Currents

In some areas, there may be significant stray currents flowing through the earth and the interconnected grounding system. These currents can cause:

Corrosion

Accelerated corrosion of buried metal objects (pipes, tanks, etc.)


Objectionable Current Flow

Nuisance tripping of GFCI (Ground Fault Circuit Interrupter) breakers.

Increased Risk of Shock

If someone comes into contact with two grounded objects at different potentials.


Neutral Currents on Ground

Bonding the grounding systems can create a path for neutral currents to flow through the ground conductor instead of the intended neutral conductor. This is undesirable and can cause problems.

Alternatives to Consider


Before automatically bonding the GES, consider these alternatives and discuss them with a qualified electrical engineer: Separate Grounding Electrodes

While bonding is usually preferred, there are certain situations where it is not recommended. If the two buildings are separated by a long distance, or if there is a high risk of ground faults due to soil conditions, it may be better to isolate the grounding systems. In these cases, the grounding system for each building should be kept separate.


Isolation Transformer

If stray currents are a concern, an isolation transformer at one or both buildings can electrically isolate the grounding systems while still allowing power to be transferred.

Recommendation
Engage a Qualified Electrical Engineer

This is not a DIY project. The complexities of generator grounding, voltage drop calculations, overcurrent protection coordination, and potential stray current issues require the expertise of a licensed electrical engineer. They can assess your specific site conditions, perform the necessary calculations, and design a safe and code-compliant system.


Thoroughly Inspect Existing Systems

Before making any modifications, carefully inspect the existing electrical systems at both buildings, including the grounding electrode systems, main disconnects, and wiring. Document any issues or deficiencies.

Local Codes and AHJ

Always consult with your local Authority Having Jurisdiction (AHJ) – the electrical inspector –
before* starting any work. They may have specific requirements or interpretations of the NEC that you need to follow.

In summary, while bonding the Grounding Electrode Systems is generally required to use a solid neutral with your generator, you need to carefully consider the potential for stray currents and other issues. A qualified electrical engineer is essential to ensure a safe and reliable installation.