Question: Like the title saysI’m remodeling a hotel tower and have a 480 feed running up tower with no EGC. On floors 2, r, and 6 there are xfmrs stepping down to 120/208. I ran a seperate 3/0 GEC up the tower and set external ground bus bars on every floor there’s a xfmr.Inspector wants me to bond in the first panelboard coming off of the xfmr. So do I just run a GEC off of the bus bars into the panelboard based on the main in that panelboard? Do I have to pull a ground with my secondary off of the xfmr to bond the xfmr shell?I’ve never done it this way always bonded at XO on the XFMR. Appreciate any insight. Thanks
Okay, let's break this down. What you've described is a multi-story, separately derived system (SDS) setup with an external ground bus. The inspector's request to bond the first panelboard isn't wrong, but it needs to be done correctly in conjunction with proper transformer bonding.Here's how to approach this, in order of priority
1. Addressing the Inspector's Concern (Panelboard Bonding):
Understanding the Inspector's Reasoning
The inspector is likely concerned with ensuring a low-impedance path back to the source (the transformer) in case of a fault on the 120/208V system. By bonding the first panelboard, they want to ensure that a fault clears quickly and safely.
How to Bond the First Panelboard
Yes, you would run a
bonding jumper (not a GEC, but a system bonding jumper) from the ground bus bar on each floor (where the xfmrs are) to the grounding terminal bar (or neutral bus if that's where grounding is terminated) in the first panelboard fed by that floor's transformer. This jumper sizes per 250.28 based on the size of the largest phase conductor feeding the panelboard. Think of it this way
The ground bus bar on each floor acts as the main "grounding electrode conductor (GEC)" termination point for that floor's separately derived system (the xfmr). From there, you're running a SYSTEM BONDING JUMPER to the first panelboard to ensure proper fault clearing.
Important Clarification
This jumper is in addition to the equipment grounding conductors (EGCs) that run with the branch circuits from the panelboard to the loads. This bonding jumper is for the system, not the individual branch circuits.
2. Transformer Bonding (The Most Important Part)
This is where things get very specific, and often misunderstood. You must ensure proper bonding at the transformer before worrying about downstream panelboards.
The XO Bond
You are absolutely correct. Code requires to connect an unspliced conductor from XO to a GEC. You need a connection from the XO point (neutral point) of the transformer secondary winding to the grounding electrode system. This connection establishes the system ground for the 120/208V system.
Size per 250.30(A)(1). This conductor is a GEC. You use 250.66 (Table) to size the GEC based on the size of the largest secondary phase conductor. It connects to the grounding electrode (the GEC you ran up the tower and terminated at your ground bus). Important
This connection must be continuous and unspliced.
Transformer Enclosure Bonding
You absolutely need to bond the transformer enclosure (the "shell") to ground.
Method 1 (Preferred)
Run an Equipment Grounding Conductor (EGC) from the ground bus bar (the one you installed on that floor) to a grounding lug or screw on the transformer enclosure. Size this EGC per Table 250.122 based on the size of the overcurrent protective device protecting the transformer secondary conductors.
Method 2 (Less Desirable, but potentially acceptable)
Use a bonding bushing on the conduit nipple or raceway connecting the transformer to the first panelboard and a bonding jumper from that bushing to the ground bus bar. This relies on the metallic raceway as the EGC.
Why the Enclosure Bond is Critical
This ensures that the transformer enclosure is at the same potential as ground. If a fault occurs within the transformer, this bonding provides a low-impedance path for fault current to flow back to the source (the transformer's secondary winding, and ultimately to the XO point). This is essential for the overcurrent protective device to trip and clear the fault quickly.
3. Your Existing GEC (the 3/0 Up the Tower)
You've already run a 3/0 GEC up the tower and connected it to the ground bus bars on each floor. This is generally a good practice and a safe way to tie the grounding electrode system together.
Important
Verify that this GEC is properly connected to an effective grounding electrode system at the service entrance (the bottom of the tower). This could be a building steel, a ground ring, or other approved grounding electrode.
Check the Size
Ensure the 3/0 is large enough for the largest transformer secondary conductors.
4. Addressing the Original 480V Feed Without an EGC
This is a Significant Issue. You cannot have a 480V feed without an EGC. The Code is very clear on this. Solutions (in order of preference)
Pull an EGC
This is the ideal solution. Run an EGC (sized per Table 250.122, based on the overcurrent protection of the 480V feeder) along with the existing 480V conductors. Connect this EGC to the service equipment grounding bus and to the ground bus on each floor where the transformers are located.
Replace the Feeders
This may be the most practical solution if pulling an EGC is difficult. Replace the existing 480V conductors with conductors that include a properly sized EGC.
Use the Metal Conduit (if applicable and meets all requirements)
If the 480V feed is in rigid metal conduit (RMC) or intermediate metal conduit (IMC) and the conduit run is electrically continuous and properly installed with listed fittings, the conduit itself can serve as the EGC. However, this is often not the most reliable solution, and it's crucial to verify that the conduit system is properly bonded and electrically continuous throughout its entire length.
Summary and Recommendations
Prioritize the 480V EGC Deficiency
Fix the lack of an EGC on the primary feeder immediately. This is a serious safety hazard.2.
Bond Each Transformer Properly
Ensure each transformer has a properly sized GEC from the XO point to the ground bus on that floor. Ensure the transformer enclosure is bonded to the ground bus using a correctly sized EGC.3.
Bond the First Panelboard
Run a system bonding jumper from the ground bus on each floor to the grounding bar in the first panelboard fed by that floor's transformer. Size per 250.28.
4.
Confirm Grounding Electrode System
Verify that the 3/0 GEC running up the tower is properly connected to an effective grounding electrode system at the service entrance.5.
Document Everything
Keep detailed records of all bonding and grounding connections, conductor sizes, and grounding electrode system details.
Important Considerations
Coordination with the Engineer
Discuss these details with the project engineer (if there is one). They will have specific requirements for grounding and bonding based on the overall system design.
Local Amendments
Be aware of any local amendments to the NEC that may affect grounding and bonding requirements.*
Professional Assistance: If you're not entirely comfortable with these concepts, consider consulting with a qualified electrical engineer or a master electrician experienced in industrial or commercial electrical systems.By following these steps, you'll ensure a safe and code-compliant installation that protects people and equipment from electrical hazards. The most important thing is to create low-impedance fault current paths so that overcurrent protection devices trip quickly and effectively. Good luck! Flag for review