Question: I installed new 175A breaker in a panel, the next day I had to unistall it and install another new 175A breaker and when I ask why, the PM said because the first one is serie breaker? What thats mean?Is this correct?Can someone clarify this concept.
Let's break down what the PM likely meant by "series breaker" and why it's a problem in your scenario
Understanding Series Breakers (or, more likely, improperly rated breakers)
Series Rated Systems
In industrial and commercial settings, sometimes a system is designed with breakers in series (one after the other in the circuit). The upstream breaker (closer to the power source) has a higher Interrupting Capacity (AIC) rating than the downstream breaker. The higher AIC breaker is designed to protect the downstream breaker in case of a major fault. This setup is carefully engineered and requires specific listings from the breaker manufacturers to be used correctly.
"Series Breaker" as a Misnomer
In your situation, it's highly unlikely that you have a properly designed series-rated system in a standard electrical panel (residential or light commercial). The PM's use of the term "series breaker" is probably shorthand for an improperly rated breaker. The most common issue is that the first breaker may not have the proper interrupting rating.
Why the First Breaker Was Likely Replaced
The problem most likely lies with the Interrupting Capacity (AIC) rating of the first 175A breaker. Here's why:1. Interrupting Capacity (AIC) Rating
Every breaker has an AIC rating, expressed in thousands of amps (kA). This is the maximum fault current the breaker can safely interrupt without exploding or failing catastrophically.2.
Available Fault Current
Your electrical system has an available fault current at the panel. This is the amount of current that could flow during a short circuit. This fault current depends on factors like the utility transformer size and the impedance of the wiring.3.
The Mismatch
If the first 175A breaker had an AIC rating lower than the available fault current at the panel, it was a serious safety hazard. If a short circuit occurred that exceeded the breaker's AIC rating, it could fail to interrupt the current, leading to: An explosion Fire Electrocution risk
Was the PM's Reasoning Correct?
Possibly. The PM likely recognized that the initial 175A breaker had an inadequate AIC rating for your electrical system. It's also possible the breaker was from a foreign country and not UL-listed for use in the USA or Canada.
What You Should Do Now1. Find the AIC Rating
Look at the label on the breaker that was removed (the first 175A one). It should have a number followed by "kA" (e.g., "10kA," "22kA"). This is the AIC rating. If you can't find that rating, or the label is unclear, provide the breaker's full model number.2.
Determine Available Fault Current
The most crucial step is to determine the available fault current at your electrical panel. This requires a qualified electrician. They will perform calculations or measurements to determine the maximum fault current that could flow at your panel location.3.
Verify the New Breaker's AIC
Check the AIC rating on the new 175A breaker that was installed. It must be equal to or greater than the available fault current.4.
Proper Documentation
Ensure the panel schedule is updated with the correct breaker information, including AIC rating.
Important Safety Considerations
Don't Guess
Never assume a breaker is safe. The AIC rating is critical.
Qualified Electrician
This is a job for a licensed electrician who understands fault current calculations and breaker selection.
Panel Listing: Your electrical panel itself has a series rating for the types and brands of breakers that are allowed to be installed in it. Installing breakers that aren't listed for use in that panel violates the listing of the panel and may result in unsafe situations.In summary, "series breaker" was likely a misnomer for an improperly rated breaker (specifically, inadequate AIC). The replacement was necessary for safety reasons. Get an electrician to assess the available fault current and confirm the new breaker is correctly rated. Flag for review