Question: I installed 175A new breaker and the next day I had to uninstall it and install new 175A breaker and when I asked why, the PM says because the first one is serie breaker. Is this correct?what serie breaker means? Can someone clarify this concep and pros and cons to use serie breaker?

Okay, let's break down this situation and clarify what a "series breaker" might refer to in this context, and why it might be a problem.

Understanding "Series Breaker" (Likely Meaning in This Context)

The term "series breaker" isn't standard electrical terminology in the way that, say, "circuit breaker" or "ground fault circuit interrupter" are. However, in the context of a replacement for a main breaker, the PM most likely meant the first breaker was not rated for the available fault current at that location.

Here's the likely scenario: Available Fault Current (AFC)

Your electrical panel is connected to the utility grid. If a short circuit (fault) occurs, the grid can supply a
very high current for a brief period. This is the available fault current. The closer you are to the utility transformer, the higher the AFC tends to be.

Interrupting Rating (AIC)

Circuit breakers have an interrupting rating (often expressed in kA, or kilo-Amperes). This rating indicates the maximum fault current the breaker can safely interrupt without failing catastrophically (exploding, melting, etc.).

The Problem

If the breaker's AIC rating is
lower than the available fault current at the panel, the breaker is not suitable for that location. If a fault occurs that exceeds the breaker's AIC, the breaker might not interrupt the current properly, leading to severe damage, fire, or even explosion. Using a breaker with an insufficient AIC rating is what your PM likely meant by "series breaker" – as in, it's only suitable for installations with lower available fault current.

Why a Breaker Needs an Adequate AIC Rating
Safety

The primary reason is safety. An inadequate AIC rating can lead to a catastrophic failure during a fault, endangering people and property.

Code Compliance

Electrical codes (like the National Electrical Code - NEC in the US) require that circuit breakers have an AIC rating equal to or greater than the available fault current at the point of installation.


Equipment Protection

Even if the breaker doesn't fail catastrophically, an inadequate AIC can allow excessive fault current to flow through the circuit for too long, damaging wiring, equipment, and appliances.

Pros and Cons of "Series Breakers" (In This Context - Lower AIC Rating)
Cons (Predominate)



Major Safety Hazard

As mentioned above, this is the biggest issue.

Code Violation

Using a breaker with an insufficient AIC rating is a direct violation of electrical codes.


Potential for Catastrophic Failure

Breaker can explode, melt, or otherwise fail under high fault current.

Damage to Equipment

High fault current can damage wiring and appliances.


Liability

If there's an incident, you (and potentially your PM/employer) could be held liable.

Pros (Essentially None in This Context)

Potentially lower initial cost (but the increased risk far outweighs any cost savings).

How to Determine if a Breaker is Suitable
1. Calculate or Measure Available Fault Current

This is best done by a qualified electrician. They can either calculate it based on the utility transformer size and impedance, or they can use specialized equipment to measure it directly at the panel.2.

Check the Breaker's AIC Rating

The interrupting rating (AIC) is clearly marked on the breaker itself. It will be in kA (kilo-Amperes). Example: "AIC 22kA" or "IR 22kA".3.

Compare

Make sure the breaker's AIC rating is equal to or greater than the available fault current at the panel.

In Your Situation

The PM was almost certainly concerned that the first 175A breaker you installed had a lower AIC rating than was required for your electrical panel. That's why he asked to uninstall it and replace it.

Important Recommendations



Don't Use a Breaker Unless You Know Its AIC Rating and the Available Fault Current.
This is crucial. Consult a Qualified Electrician

For determining the available fault current and selecting the correct breaker, always consult a licensed electrician. They are trained to do this safely and correctly.*

Document Everything:
Keep records of the breakers you use, their AIC ratings, and the available fault current calculations (if available).In short, what the PM meant by "serie breaker" was likely a breaker with a too-low AIC rating for your application, and using such a breaker is a dangerous and code-violating practice. Flag for review