Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 2/0 aluminum into a 50a breaker

User: ThatSparkySasquatch, Location: Texas

Asked on: Wednesday, August 20, 2025 at 11:48 am EDT
Answered on: Wednesday, August 20, 2025 at 12:27 pm EDT

Question: Good morning ladies and gents.I’m installing a sub panel to run a water well and a few lights on my family place. 50A panel, and the gentleman installing the well told me he wanted #10 copper with a 30a breaker. Thats the easy part.Unfortunately it’s a long way (450 ft) from the main panel at the house, and after running VD equations, and scratching around trying to find the best deal I’ve landed on likely using 2/0 aluminum mobile home feeder. It’s the best budget option I’ve found, and with a run like this it’s pricy no matter how you do it.Unfortunately in my time in, this isn’t a problem I’ve run into, and 90% of what I’ve worked on the engineers dictated everything and I was just an installer.I’ve got a few ideas, but I’d like to bounce this off a few more knowledgable people before I commit to any course of action.I should also add, that I have contacted the utility company about adding a pole and meter. They want $8500 for the added service, and $8500 pays for a lot of underground feeder.Thank yall in advance!

Okay, let's break this down and make sure you're on the right track. You've identified the key challenges: long distance and budget constraints. Using aluminum feeder for a long run is a common and often very effective solution.Here's a structured approach to validate your plan and identify any potential issues

1. Recap & Confirm Your Assumptions
Load Calculation

Let's reiterate the most important part; What's the
actual total amperage of the loads you'll be running on the subpanel simultaneously? You mentioned a well pump (30A breaker) and some lights. What's the total wattage of the lights? Add that up, divide by 120V to get amps, and add that to the well pump's 30A. That is the real load you need to size for. It's possible your total actual load will be less than 50A, which opens up more options for wire sizing. We need to verify this is truly a 50A demand.

Distance

Confirmed at 450ft.

Voltage

Presumably 240V (single phase)? Confirm this, as it affects voltage drop calculations.


Target Voltage Drop

What's your acceptable voltage drop? A general rule of thumb is 3% for feeders and 5% overall (feeder + branch circuits). For critical equipment like well pumps, you might want to aim for the lower end of that range.

Code Compliance

We'll be referring to the NEC (National Electrical Code), but
verify your local codes. Local jurisdictions can have amendments.

Grounding

Essential for safety. We'll get into grounding details later.

2. Analyzing Your Plan: 2/0 Aluminum for a 50A Subpanel at 450ft
Ampacity

2/0 Aluminum is typically rated for 100A at 75°C (NEC Table 310.16, assuming you're using THHN/THHW/USE-2 insulation, which is common). So, ampacity-wise, it
appears to be well over the 50A breaker you're planning. However, NEC 310.15(B)(3) and table 310.15(B)(3)(a) require that you may need to derate the wire's ampacity based on the number of current-carrying conductors in a raceway or cable. If you have four or more, you will need to derate the ampacity to 80%.

Voltage Drop: The Real Issue
This is where the long distance comes into play. You've done some calculations, but let's double-check: Simplified Voltage Drop Formula (Single Phase)

VD = (2
K I D) / CM VD = Voltage Drop (in volts) K = Resistance Constant (17 for Aluminum) I = Current (Amps - Let's use the actual load amps you calculated above) D = One-Way Distance (450 ft) CM = Circular Mils (Area of the conductor). For 2/0 Aluminum, CM = 133,100

Calculate Voltage Drop

Let's assume you're running a full 50A demand. VD = (2 17 50 450) / 133100 = 5.76 volts

Calculate Percentage Voltage Drop

(VD / Voltage) 100 = (5.76 / 240) 100 = 2.4%. This is good and under the 3% threshold for feeders. If your actual load is lower, voltage drop would be even better.

Important Considerations



Terminations

Absolutely critical. You must use connectors and lugs that are rated for aluminum-to-copper connections (AL/CU). Apply an anti-oxidant compound (like Noalox) specifically designed for aluminum connections. This prevents corrosion and ensures a good connection.

Torque

Torque all connections to the manufacturer's specified torque value using a torque wrench. Under-torqued connections are a major cause of failures and fires. Over-torquing can damage the connector.


Burial Depth

Check your local code for the required burial depth for underground wiring. Typically, it's 18-24 inches, but this can vary. Using conduit (even if not required) provides extra physical protection.

Conduit or Direct Burial Cable

Are you planning to run the cable in conduit, or is it direct burial rated? UF (Underground Feeder) cable is suitable for direct burial. Conduit provides better physical protection.


Overcurrent Protection

While 2/0 Aluminum can handle more than 50A, you are protected by the 50A breaker on the supply side. 30A for the well pump sounds fine given that the well driller requested #10 copper.

3. Grounding


This is extremely important for safety. You have two options: Option 1: Separate Ground and Neutral (Recommended) Run four conductors: Two hots, a neutral, and a separate grounding conductor. The grounding conductor should be sized according to NEC Table 250.122. For a 50A circuit, this typically calls for #8 copper or #6 aluminum (check the table). At the subpanel, the neutral and ground must be kept separate. Do not bond them together. The neutral is only bonded to ground at the main service panel. Connect the grounding conductor to a grounding rod at the subpanel location. (Check local code for grounding rod requirements, often two rods spaced a certain distance apart). Option 2: Grounded Conductor (Neutral) as Grounding Electrode Conductor (Only Allowed if no other continuous metallic path exists between buildings) Run three conductors: Two hots and a grounded (neutral) conductor. This is only allowed if there is no other continuous metallic path between the house and the well. This includes metallic water pipes, telephone cables, or cable TV cables. At the subpanel, the neutral is bonded to the subpanel enclosure. Connect the neutral conductor to a grounding rod at the subpanel location.

Which grounding method is better? Option 1, running a separate ground wire, is highly recommended. It provides a dedicated path for fault current, improving safety.4. Mobile Home Feeder Considerations Type

Ensure the cable is rated for underground use (UF or USE). Mobile home feeder is often USE (Underground Service Entrance) or UF.


Markings

Verify the cable is clearly marked with its type, voltage rating, and conductor size.

Connectors

Use connectors specifically rated for the type of cable you're using.

5. Alternatives to Consider
Larger Aluminum Wire

If voltage drop is still a concern, consider 3/0 or 4/0 Aluminum. This will increase the cost but can significantly reduce voltage drop.

Step up/Down transformers

Using step up/down transformers is another option that may need to be discussed, but with a load and distance like you have, it may not be the best option.


Careful Load Management

If your actual load is significantly less than 50A, you could potentially downsize the wire, but only if you're absolutely sure you won't exceed the lower load.

6. Action Plan
1. Refine Load Calculation

Get an accurate total amp draw for all loads that will run simultaneously on the subpanel. Be conservative.2.

Double-Check Voltage Drop

Recalculate the voltage drop using the accurate amp load.3.

Choose Grounding Method

Decide whether to run a separate ground wire (recommended) or use the neutral as the grounding electrode conductor (only if allowed).4.

Verify Local Codes

Confirm that your plan meets all local electrical codes and permitting requirements.5.

Purchase Materials

Buy high-quality AL/CU connectors, anti-oxidant compound, the correct cable, and grounding materials.6.

Installation

Follow all safety precautions. Disconnect power at the main panel before working. Torque all connections to the manufacturer's specifications.7.

Inspection

Have the installation inspected by a qualified electrical inspector.

Important Reminders



Safety First

If you're not comfortable working with electricity, hire a qualified electrician. Electricity is dangerous.


Permits

Obtain the necessary electrical permits before starting the work.*

Professional Advice:
If you have any doubts or questions, consult with a licensed electrician.By carefully considering these factors and following the recommendations, you can ensure a safe and reliable electrical installation for your well pump and lights. Good luck! Flag for review

Previous Question Next Question