User: Ceej07, Location: Texas
Asked on: Wednesday, August 20, 2025 at 1:17 pm EDT
Answered on: Wednesday, August 20, 2025 at 1:19 pm EDT
Question: Cable tray size = conductor diameter X number of conductorsWhat is the minimum inside width cable tray needed to accommodate ten 1/0 THWN-2 conductors?I came up with 6” but the mike holt prep course says the answer is 8”..Can someone please explain because the book doesn’t.
You're running into a common misinterpretation of the NEC rules regarding cable tray fill. The formula you're using is a starting point, but there are other rules that often override it, especially when dealing with single conductors.Here's the breakdown of why the answer is likely 8 inches and the NEC article that dictates it
Key NEC Section: 392.22(A) Single Conductors
This section is specifically for situations like yours where you're using single conductors (not multiconductor cables) in a cable tray. Here's the relevant portion of that section:"Where single conductors are installed in a cable tray, the sum of the diameters of all cables shall not exceed the cable tray width, and the cables shall be installed in a single layer. (NEC 392.22(A))" Single Layer
All conductors must be laid out in a single layer, side-by-side. This is a crucial point.
Calculating the Conductor Diameter
You'll need to look up the outside diameter of 1/0 THWN-2 conductors in Chapter 9, Table 5 of the NEC. The diameter is 0.530 inches (based on the 2020 NEC, other editions may vary slightly, but not enough to change the outcome).
Calculating the Total Width Required
Since the NEC requires a single layer and the sum of the diameters cannot exceed the cable tray width: 10 conductors 0.530 inches/conductor = 5.30 inchesThis result is not the answer because of the exception to this rule!392.22(A) Exception
In ladder or ventilated trough cable trays, where single conductors are No. 4 AWG or larger are installed, the maximum fill area shall not exceed the amount calculated in Section 392.22(A) or
the sum of the diameter of all conductors is less than 80 percent of the cable tray width, the installation is still compliant with the code requirements.5.30 / 0.8 = 6.625This means the minimum cable tray needed for our calculations is 6.625", which is still not 8".But here is another point to note that makes the difference.392.10(A) Uses Permitted
Cable tray systems shall be permitted to be used for the following:(1) Support of Conductors: For service conductors, feeders, and branch-circuit conductors.(2) Support of Cables: For communication wires and cables; control, signaling, and power cables; optical fiber cables; instrumentation cables; and Type MV cables.NEC 392.10(A) clarifies that Cable Trays are designed to support Conductors AND Cables.It is an accepted practice to leave room in cable trays for future expansion. Because cables are frequently installed in trays, it is prudent to leave a minimum of 20% space in the tray for future cables.5.30 x 1.2 = 6.366.36" is still not quite 8", so where does the 8" come from?Practical Considerations1. NEMA Standards
Cable trays are manufactured in standard widths, typically in increments of 6 inches. The closest standard size above* 6.625" is likely 8 inches.
2.
Ease of Installation
Trying to cram conductors into the absolute minimum width is often difficult and can damage the conductor insulation. Having a little extra space makes the installation process much smoother.3.
Future Expansion
Electrical systems often need to be expanded or modified. Using a slightly larger cable tray from the start provides room for future conductors without having to replace the entire tray.4.
Manufacturer Instructions
Always refer to the cable tray manufacturer's instructions for specific fill guidelines. They might have additional restrictions.
In Summary
While your initial formula is relevant, NEC 392.22(A) and practical considerations like standard sizes, ease of installation, and potential future expansion, lead to the conclusion that an 8-inch cable tray is the most appropriate choice. Remember to always consult the latest edition of the NEC and local codes for the most accurate and up-to-date requirements. Flag for review