Topic: Flickering lights when dishwasher running

User: Electric_kool_aid, Location: Washington

Asked on: Wednesday, August 20, 2025 at 5:32 pm EDT
Answered on: Wednesday, August 20, 2025 at 5:35 pm EDT

Question: So I did a full rewire at an older home (40’s). The flipper didn’t want to update the service if not necessary it was a newer maybe early 2000’s Eaton panel. When the customer turns the dishwasher on the kitchen cans flicker. They are on a diva dimmer (led compatible) and the can trims are just standard 3k led trims. Can’t seem to figure out every connection is solid at the panel, not getting any irregular voltage to anything. Obviously dishwasher is on its own dedicated circuit separate from lighting. There is a switch box that both circuits are in and I’m wondering if the dimmer is ultra sensitive to the current pull from the dishwasher motor. Any advice on how to fix this have t really ran into it before. But main service and connections seem solid. Maybe move my arc fault lighting load to a separate pull as the dishwasher ? Replace the dimmer? Replace the AFCI breaker? No other lights in the home are having issues

Okay, let's break this down. You're facing a classic troubleshooting puzzle, and here's a systematic approach to diagnose and resolve the flickering kitchen can lights when the dishwasher is running

1. Ruling out the basics (again, but thoroughly):
Neutral Connections (Critical)

Even though you rewired, double-check

every single neutral connection
in the entire path from the panel, through the switch box, to the lighting fixtures. A loose or corroded neutral is the
prime suspect for this type of issue. Specifically, examine: Panel Neutral Bar

Are the neutral wires for the lighting circuit and the dishwasher circuit securely connected to the neutral bar? Are the screws tight? Check for corrosion.

Switch Box Neutral Connections

This is a key point. Inspect the neutral connections inside the switch box where the lighting and dishwasher circuits pass through. Even if they look tight, loosen them, check for corrosion or arcing signs, and re-tighten them securely. Use a torque screwdriver if you have one. Wire nuts are notorious for backing off over time. Pig-tailing the neutral to each device separately is best practice.


Fixture Neutral Connections

Check the neutral connection at each of the can lights.

Ground Connections

Verify ground connections at the panel, switch box, and fixtures. While less likely to cause flickering
directly, a weak ground can exacerbate other issues.

Voltage Drop

While you said you aren't seeing irregular voltage, under load, a voltage drop could be occurring. Use a multimeter and measure the voltage at the can lights while the dishwasher is running. Note the voltage before the dishwasher starts, immediately when it starts, and while it's running through a wash cycle. Significant voltage drop (more than a few volts) points to a wiring issue or undersized wiring.

2. The Dimmer Suspect



Dimmer Compatibility (Revisited)

You said it's LED compatible, but
specifically check the dimmer's documentation to see if it lists the type of LED trims you're using as compatible. Not all "LED compatible" dimmers work perfectly with all LEDs. The dimmer's minimum load requirements can also be an issue.

Dimmer Replacement (Test)

The easiest way to know for sure is to replace the dimmer with a standard (non-dimming) switch and see if the problem goes away. If it does, you've narrowed it down to the dimmer. Try a different brand or model of LED-compatible dimmer.

Dimmer Location

Where in the circuit is the dimmer? Is it near the beginning of the lighting circuit, or near the end? If it's at the end, and there's already voltage drop in the circuit, the dimmer could be struggling to regulate the voltage.

3. Interference and Circuit Interactions



Arc Fault Breaker Sensitivity

Arc fault breakers can be overly sensitive. The dishwasher motor's starting surge could be creating a small arc or noise on the line that the AFCI is detecting (even though it's not a real arc fault). However, don't just replace the AFCI without more testing. A nuisance trip suggests other issues.

Dedicated Lighting Circuit

Consider moving the kitchen can lights to their own
dedicated circuit, separate from other lighting loads in the kitchen. This isolates them and eliminates potential interference. This is a good move even if it doesn't solve the problem, as it's a better wiring practice overall.

Switch Box Proximity

You mentioned the switch box is shared between the dishwasher and lighting circuits. While code-compliant, this can create a potential path for inductive coupling. Try physically separating the wires as much as possible within the box. Consider a larger box to give more separation.

Check Dishwasher Wiring

Is the dishwasher itself properly wired? Check the wire gauge going to the dishwasher and make sure it's correct. Also, check the connections inside the dishwasher junction box itself.

4. Dishwasher-Specific Considerations



Dishwasher Quality

A cheap or poorly designed dishwasher can generate more electrical noise and harmonics than a high-quality one. While replacing the dishwasher isn't ideal, it's a possibility.

Inverter Dishwashers

Modern dishwashers often use inverter motors for efficiency. Inverters can sometimes introduce electrical noise on the line. This is less common, but worth considering.

5. Systematic Troubleshooting Steps


Thorough Visual Inspection

Start with a careful visual inspection of
all wiring connections.2.

Neutral Check

Methodically check
every neutral connection. This is the most likely culprit.3.

Voltage Drop Test

Measure voltage at the can lights while the dishwasher is running.4.

Dimmer Replacement (Test)

Temporarily replace the dimmer with a standard switch.5.

Circuit Separation

Move the kitchen can lights to a dedicated circuit.6.

AFCI Breaker Test

As a last resort, try replacing the AFCI breaker, but only after ruling out other causes.7.

Dishwasher Inspection

Check wiring to the dishwasher and inside the dishwasher.

Important Safety Notes



Turn Off Power

Always turn off the power at the circuit breaker before working on any electrical wiring.

Qualified Electrician

If you are not comfortable working with electrical wiring, hire a qualified electrician.


Local Codes:
Ensure all work complies with local electrical codes.By following these steps, you should be able to isolate the cause of the flickering lights and implement an effective solution. Good luck! Let me know if you find anything or have further questions. Flag for review

Previous Question Next Question