Question: 700.5(D) Redundant Transfer Equipment.If emergency loads are supplied by a single feeder, the emergency power system shall include redundant transfer equipment or abypass isolation transfer switch to facilitate maintenance as required in 700.3(C) without jeopardizing continuity of power.According to the above code rule, if a building has a emergency generator that powers (1) emergency ATS (NEC 700) and (1) optional standby ATS (NEC 702),the emergency ATS must be bypass isolation type, correct?
No, that's not necessarily correct. Here's a breakdown of why and what 700.5(D) actually requires: 700.5(D) Focuses Solely on Emergency Systems
The rule in 700.5(D) pertains only to emergency power systems that supply emergency loads. It doesn't directly address optional standby systems or how they are connected.
The "Single Feeder" Trigger
The requirement for redundant transfer equipment or a bypass isolation transfer switch is triggered when emergency loads are fed by a single feeder. This is to ensure that maintenance can be performed on the transfer equipment without interrupting power to the emergency loads.
Your Scenario Analysis
If the emergency ATS in your scenario is fed by its own dedicated feeder from the generator, and only supplies emergency loads, then 700.5(D) might apply. Whether it does apply depends on the interpretation by the AHJ and the specifics of your installation. The presence of an optional standby ATS is irrelevant to the requirements of 700.5(D). If the building is using two separate emergency generators each with their own dedicated feeder to its respective emergency ATS, then 700.5(D) may not apply.
AHJ ruling is the most important. There are many nuances with this code rule. Bypass Isolation vs. Redundant Transfer Equipment
The code offers two options:
Bypass Isolation Transfer Switch
This type of switch allows you to isolate the transfer switch for maintenance while still providing power to the load via a manual or automatic bypass mechanism.
Redundant Transfer Equipment
This typically means having a second, identical transfer switch in parallel with the first. If the primary switch fails or needs maintenance, the load can be transferred to the secondary switch.
In summary, the presence of an optional standby ATS has no bearing on whether 700.5(D) applies. The key factor is whether the emergency loads are supplied by a single feeder and whether the local AHJ (Authority Having Jurisdiction) deems a bypass isolation switch or redundant transfer equipment necessary to maintain continuity of power during maintenance.Important Considerations
Life Safety
Emergency systems are critical for life safety, so over-engineering and redundancy are often beneficial.
AHJ is Key
Consult with your local electrical inspector or AHJ to determine their specific interpretation of 700.5(D) and what they will require for your installation. They have the final say.*
Design Intent: Consider the design intent of the emergency system and the potential impact of a loss of power during maintenance. This will help you determine the most appropriate solution.I strongly recommend consulting with a qualified electrical engineer and the local AHJ to ensure your emergency power system design complies with all applicable codes and regulations. Flag for review