Topic: LFMC entering a threaded motor peckerhead - proper install?

User: emiller233, Location: pittsburgh, pa

Asked on: Thursday, August 21, 2025 at 11:51 am EDT
Answered on: Thursday, August 21, 2025 at 12:15 pm EDT

Question: We have a motor with a threaded conduit hole on the peckerhead. The shop guys tell me the conduit hub won't fully thread onto it (making the gasketed seal). That there's still about 1/4" of thread left before the gasket would make the seal to the peckerhead.And putting the 45-degree LFMC fitting directly onto the peckhead is not permitted, and we shall use a hub, correct?They want to grind the threads out of the conduit opening so the hub makes the gasketed seal.What is the proper way to install this?Also, are there any other APPROVED methods for securing the LFMC? The only one I've found that lists LFMC specifically is an Arlington3" conduit opening to 1-1/4" LFMC (75HP motor)This needs to meet Canadian code as wellparts list for motor connectionhub3" CONDUIT HUBCROUSE-HINDS ST 8reducersRIGID CONDUIT REDUCER, 3" to 1-1/2" NPTCROUSE-HINDS 288RIGID CONDUIT REDUCER, 1-1/2" to 1-1/4" NPTCROUSE-HINDS 275LFMC fitting1-1/4" LFMC FITTING, 45° ANGLE, INSULATED"CROUSE-HINDS LTB12545LFMC clampArlington NM2050motor peckerheadLFMC layoutoverview

Okay, let's break down this motor connection issue and address the proper installation according to code and best practices. Grinding threads is absolutely the wrong approach.

Understanding the Problem Incomplete Thread Engagement

The 3" conduit hub isn't fully threading onto the motor's peckerhead conduit opening. This prevents the gasket from sealing properly, leading to potential water ingress and electrical hazards.


Hub Requirement

Yes, generally, a hub is the correct method to adapt between the threaded opening in the motor peckerhead and the LFMC fitting. Direct connection of an LFMC fitting is usually not allowed due to mechanical stress, vibration, and sealing concerns.

Do NOT Grind the Threads
Grinding the threads voids the listing and certification of the peckerhead and potentially compromises its structural integrity. It is a violation of electrical codes (both Canadian and US) to modify listed equipment in a way that affects its safety or intended use.

The Correct Installation Steps

Here's the proper approach, troubleshooting steps, and code considerations:1. Verify Thread Compatibility (MOST IMPORTANT)



Thread Type

Confirm that the motor peckerhead's threaded opening and the hub's threads are the
same type (NPT - National Pipe Thread). They must be the same to properly engage. NPT threads are tapered.

Thread Size

Double-check that the stated size of the opening and the hub actually match. A mislabeled part is possible.

Thread Condition

Inspect the threads on both the peckerhead and the hub for damage (stripped, cross-threaded, debris). Clean them thoroughly with a wire brush. If damaged, the peckerhead may need replacement or a thread repair solution (but consult a qualified electrician).2.

Use Thread Sealant/Lubricant

Apply a UL-listed thread sealant specifically designed for electrical conduit connections. This helps ensure a watertight and gas-tight seal. Teflon tape (plumber's tape) is not ideal for this application due to its limited ability to fill larger gaps and its potential to unwind under vibration. Use a pipe dope or thread sealant designed for electrical conduit.3.

Tighten Properly

Tighten the hub onto the peckerhead with appropriate tools (pipe wrench). Refer to the manufacturer's torque specifications for the hub if available. Overtightening can damage the threads or the peckerhead.4.

If Threads are Too Short

IF the hub and peckerhead threads are confirmed to be the correct type and size, and after proper cleaning and lubrication, the hub still doesn't engage enough threads to create a good seal, there are two possible solutions:

Longer Threaded Hub

Look for a hub with
longer threads. Some manufacturers offer hubs with extended thread lengths for situations like this. This is the best solution.

Thread Extender/Coupling

As a last resort and only if approved by a qualified engineer and electrical inspector, you might be able to use a threaded coupling or nipple that extends the threaded section on the peckerhead. This must be done with extreme care to maintain grounding continuity and ensure a watertight seal. This option is very rare and usually not recommended.5.

Grounding

Ensure proper grounding continuity throughout the entire conduit system, including the motor peckerhead. Use appropriate grounding bushings or straps where necessary.

LFMC Support and Securing (Canadian Code Considerations)
Arlington NM2050

While this clamp might be suitable for securing the LFMC to a junction box, it is not designed to support the weight of the conduit run, especially with a 75 HP motor's vibration.

Canadian Electrical Code (CEC)

CEC Rule 12-600 series covers the support and securing of cables and raceways.


Proper LFMC Support



Support Spacing

The CEC requires LFMC to be supported at intervals not exceeding the manufacturer's recommendations (typically every 1.2 to 1.5 meters or 4 to 5 feet).


Secure Attachment

Use appropriate conduit clamps, straps, or hangers designed specifically for LFMC to support the conduit run.

Consider Vibration

Account for the motor's vibration when selecting support hardware. Use vibration-dampening clamps or supports where necessary.


Support Near Fittings

Support the LFMC close to the 45-degree fitting (within 300mm or 12 inches) to prevent strain on the fitting and peckerhead connection.

Independent Support

Do not rely solely on the peckerhead for LFMC support. The LFMC should be independently supported from the motor or a nearby structure.

Specific Considerations for your Parts List
CROUSE-HINDS ST 8 (3" Conduit Hub)

Verify that this hub is rated for the intended environment (e.g., wet location). Check the thread length.

CROUSE-HINDS 288 & 275 (Reducers)

Ensure these reducers are also rated for the environment. Use thread sealant on all threaded connections.


CROUSE-HINDS LTB12545 (1-1/4" LFMC Fitting)

An excellent choice. Make sure it's properly tightened to the reducer using thread sealant.

Recommended Actions
1. STOP the grinding!2. Verify Thread Compatibility

This is the #1 priority.3.

Consult the Motor Manufacturer

Contact the motor manufacturer or supplier for clarification on the peckerhead thread specifications and recommended connection methods.4.

Consult a Qualified Electrician

Have a licensed electrician review the installation plan and ensure it complies with all applicable codes and regulations.5.

Get Inspection Approval

Before energizing the motor, have the installation inspected by a qualified electrical inspector.

In summary, the keys to a proper installation are using the correct thread types, applying thread sealant, ensuring adequate thread engagement, and providing proper support for the LFMC run.
Grinding threads is never an acceptable solution. Flag for review