Question: The current code book doesn't reference a breaker for #14 aluminum wire. Does this mean you can't put a breaker?
You are correct in noticing the discrepancy. Here's a breakdown of why you wouldn't typically see a breaker specifically listed for #14 aluminum wire in the code book and what the implications are: Aluminum vs. Copper and the Ampacity Question
The code books (specifically the NEC in the US) primarily focus on ampacity, which is the current-carrying capacity of a wire. Ampacity depends on wire size, insulation type, temperature rating, and other factors. #14 Aluminum has a lower ampacity than #14 Copper.
Breaker Size and Ampacity
Breakers are designed to protect the wire from overheating and causing a fire. You want the breaker to trip before the wire reaches its maximum safe ampacity.
Why No Specific Breaker Listing for #14 Aluminum
While #14 Copper is commonly protected by a 15 amp breaker,
#14 aluminum is rarely, if ever, used for general branch circuit wiring in modern residential or commercial buildings. It's simply not a common or practical application. Therefore, code books generally don't explicitly list breaker sizes for it in the same way they do for copper. What This Means
You generally should not be using #14 aluminum wire for typical branch circuits. It lacks the ampacity to handle the load that #14 copper would handle, making it unsuitable for most common applications. If you must use #14 aluminum in a specific, unusual situation (which is highly unlikely and would require very careful consideration and likely specialized connectors), you would need to ensure the breaker you use is appropriately sized to protect the wire's actual ampacity. Consult the ampacity tables in the code book. These tables specify the allowable ampacity for different wire types (including aluminum) and installation conditions. Always consult the latest edition of the NEC or relevant local electrical codes.
Pay special attention to terminal markings
If connecting aluminum conductors, be sure to use connections (devices and terminals) rated for use with aluminum. Look for markings like "AL-CU" (suitable for both aluminum and copper) or "AL" (suitable only for aluminum). Mixing aluminum and copper without proper connections can lead to corrosion and failure.
In short: While it's possible, in theory, to use a properly sized breaker with #14 aluminum in a very specific application, it's highly unusual and often impractical. Using appropriately sized copper wiring is almost always the better and safer choice for general branch circuit wiring. If you're considering using #14 aluminum wire, carefully evaluate your situation, consult with a qualified electrician, and ensure you fully understand the applicable electrical codes. Never guess or assume when it comes to electrical work. Flag for review