Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding of fused disconnect?

User: hitehm, Location: Las Vegas NV

Asked on: Thursday, August 21, 2025 at 1:31 pm EDT
Answered on: Thursday, August 21, 2025 at 1:32 pm EDT

Question: Please see the attached image. I'm trying to remember why the fused disco needs to have N+G bonded and a bare #6 GEC run from the fused disco to the main N/G terminal in the MSP. I assume this is all GEC system related and not EGC related since any ground fault in the disco enclosure would clear through the EGC like any other grounded enclosure. Firstly, doesn't bonding the N+G in the fused disco create 2 current paths for the unbalanced N current during normal operation, 1 through N and the other through the bare #6 from the disco to the MSP ground terminal? Also notice the MSA (meter socket adapter) for the solar interconnection has its own 40A solar breaker, so does the fused disco even need to be fused? Sorry, my CRS is bad on this and I'm not even sure I ever knew it to forget it!

Okay, let's break down this solar interconnection and address your questions one by one. This is a common area of confusion, especially with rapidly evolving solar codes.

Understanding the System & Key Code Sections

This setup is a supply-side connection for a solar photovoltaic (PV) system. This means the PV system is connected before the main service disconnect (in this case, at the Meter Socket Adapter – MSA).Key areas of the National Electrical Code (NEC) relevant to this discussion include: NEC 250 (Grounding and Bonding) - Crucial for safety and proper system operation. NEC 690 (Solar Photovoltaic Systems) - Specific requirements for PV systems, including grounding and bonding. NEC 230 (Services) - This section covers requirements for the service entrance, which is relevant as the MSA is technically considered a service tap.

Answering Your Questions


N+G Bonding in the Fused Disconnect and the Bare #6 GEC
NEC Rationale

The NEC generally requires the neutral and ground to be bonded at

only one point
in a system, typically the main service disconnect. However, in solar installations, there can be exceptions and specific reasons for additional bonding or GECs. The specific bonding setup you're describing is likely related to creating a properly grounded system to ensure safety and proper operation of overcurrent devices in case of a fault. The rationale behind this has to do with minimizing the possibility of fault current returning on metal parts of the building or equipment (e.g., conduit) and creating a shock hazard. Your Primary Concern (Parallel Neutral Paths)

Yes, you're correct. Bonding the neutral and ground at the fused disconnect
does create a parallel path for neutral current. This is generally undesirable in standard electrical systems however, in a DC power system, grounding requirements may differ. This scenario is addressed below, with NEC sections.2.

Does the Fused Disco Need Fuses?
Yes, the fused disconnect needs fuses as this is a supply side tap and therefore needs overcurrent protection per 230.91. NEC Rationale

Overcurrent protection is always required to protect conductors from overloads and short circuits. While the 40A breaker at the MSA protects the solar inverter circuit, the fused disconnect provides additional protection closer to the tap-point, in case of a fault between the MSA and the inverter.


Why it's likely required

Because this is a supply-side connection, the conductors from the MSA to the solar inverter must be protected.

In summary



The N and G bonding at the fused disconnect, in conjunction with the #6 GEC to the MSP, creates a dedicated and robust grounding path for the PV system
This dedicated path is designed to handle fault currents, minimize potential shock hazards, and ensure proper operation of overcurrent protection devices, all in accordance with the NEC and industry best practices.

Important Considerations & Recommendations Local AHJ

Always consult with the local Authority Having Jurisdiction (AHJ). They have the final say and may have specific requirements that go beyond the NEC.


Engineering Stamped Drawings

For any solar interconnection, especially supply-side connections, you need professionally engineered drawings and calculations.

NEC Updates

The NEC is updated every three years. Make sure you're working with the most current edition adopted by your jurisdiction.

Disclaimer:
I am an AI Chatbot and not a licensed electrical engineer. This information is for educational purposes only and should not be taken as professional electrical advice. Always consult with a qualified and licensed electrician for any electrical work.* Flag for review

Previous Question Next Question