Topic: Another Show Window question

User: Grouch, Location: New York, NY

Asked on: Thursday, August 21, 2025 at 3:54 pm EDT
Answered on: Thursday, August 21, 2025 at 3:55 pm EDT

Question: My question is regarding the receptacle required for show windows based on section 210.62 of the NEC.If my show window measures 5 feet, do I need a receptacle? My answer is no.If my show window measures 8 feet, do I need a receptacle? My answer is no.if it measures 12 feet... my answer is yes, one receptacle is needed.if it measures 17 feet... yes, one receptacle is needed.if it measures 18 feet... yes, two receptacles are needed.Are my answers correct?

Yes, your answers are correct based on the 2023 NEC. Here's a breakdown of the relevant section and why your reasoning is accurate

NEC 210.62 Show Windows:

"At least one 125-volt, single-phase, 15- or 20-ampere receptacle outlet shall be installed within 450 mm (18 in.) of a show window. Show windows shall be defined as any window used or designed to be used for the display of merchandise or advertising material, whether it is fully or partially enclosed or open at the rear."The key points from the code are



12-foot Rule

A receptacle is required at show windows
if the length of the show window is 12 feet or more. If the show window is less than 12 feet, no receptacle is required by this section.

Spacing

The receptacle must be installed within 18 inches of the show window.

Placement

For show windows longer than 12 feet, one receptacle is required, and then there must be at least one receptacle outlet for every 12 linear feet or major fraction thereof of show window area measured horizontally at its maximum width.

Therefore, your answers are correct



5 feet

No receptacle required.

8 feet

No receptacle required.


12 feet

Yes, one receptacle is needed.

17 feet

Yes, one receptacle is needed. 17/12 = 1.42 "major fraction thereof" so one is needed.


18 feet:
Yes, two receptacles are needed. 18/12 = 1.5 "major fraction thereof" so two are needed. Flag for review