Question: I have a question relative OCPD of motors.As an example 40HP motor rated a 480/3. NEC Table 430.52 for Inverse Time Breaker say 250% of FLA 52 x 250% = 130A thus a 150CB.My Square-D motor calculator says 90 Thermal Magnetic trip rating. Obviously their must be some characteristics of the Square-D type CB that allows for the90ampere rating but I am not sure what that is.

You're right, there's a difference between the calculated values and what a specific motor protection calculator recommends, and understanding the "why" is key. Here's a breakdown

Understanding the NEC and Motor Protection
NEC Article 430

This is the bible for motor circuits. It prioritizes protection against overloads, short circuits, and ground faults.


NEC Table 430.52

Provides maximum allowable overcurrent protective device (OCPD) sizes based on motor type and OCPD type (inverse time breaker, fuse, etc.). The percentages are maximum limits. The goal is to allow for motor starting current (inrush) without nuisance tripping while still providing protection.

FLA (Full Load Amps)

This is the current a motor draws when operating at its rated horsepower and voltage under full load. It's a critical value for calculations.

Why the Discrepancy?
1. NEC as a Maximum

The NEC Table 430.52 values are
maximums, not mandatory ratings. You can always use a smaller breaker or fuse if it adequately protects the motor and doesn't nuisance trip. The NEC prioritizes safety and allowing the motor to start. It says you can go up to 250%, but it doesn't require you to.2.

Motor Service Factor

Motors often have a "service factor" (SF), typically 1.15 or higher. This means the motor can handle a short-term overload without damage. The NEC allows you to consider the service factor when sizing the overload protection (separate from the OCPD).3.

Motor Temperature Rise

Similar to service factor, the motor's insulation class (e.g., Class B, Class F) indicates how much temperature rise it can tolerate. This influences overload protection sizing.4.

Specific Breaker Characteristics

This is the crucial point! Square D (and other manufacturers) design breakers with specific trip curves. These curves dictate how long the breaker will tolerate an overcurrent condition before tripping.


Inverse Time Breakers

By definition, inverse time breakers trip faster as the overcurrent increases. The curve is not perfectly linear.

Square D's Design

Square D breakers, especially those marketed for motor protection (like those in their motor starter combinations or specifically designed for motor circuits), are often designed with a trip curve that allows for higher inrush currents without tripping. They might have a more "sluggish" response to moderate overloads during starting, but still trip quickly under severe fault conditions.5.

Motor Starter vs. Standalone Breaker

Are you using a motor starter with overload relays? If so, the overload relays handle the overload protection, and the breaker is primarily for short-circuit and ground-fault protection. In this case, the breaker can often be sized closer to the motor's FLA.6.

Application-Specific Considerations

Is the motor driving a high-inertia load that requires a long starting time? This might influence the choice of breaker and its trip curve.

How Square D Calculates a 90A Breaker


While I can't know Square D's
exact algorithm without access to their proprietary software, here's the likely process:1. Motor Data

They input the motor's HP, voltage, FLA, service factor, and insulation class.2.

Breaker Family

They select the appropriate family of Square D circuit breakers designed for motor protection. These breakers have specific trip curves.3.

Trip Curve Analysis

The software analyzes the breaker's trip curve against the expected motor starting current profile. The starting current is typically 6-8 times the FLA for a short period.4.

Overload Protection Coordination

The software ensures the breaker's trip curve coordinates with the motor's thermal overload relay (if present) to provide optimal protection.5.

Short-Circuit Protection

The software verifies that the selected breaker provides adequate short-circuit protection.6.

Nuisance Tripping Avoidance

The goal is to choose a breaker that's small enough to protect the motor against overloads and short circuits but large enough to avoid nuisance tripping during starting.

Key Takeaways and Recommendations
Always Consult the Manufacturer

The Square D calculator is your best guide for Square D equipment. Follow their recommendations when using their breakers.

Understand the Trip Curve

If possible, get a copy of the breaker's trip curve. This will show you how the breaker responds to different overcurrent levels over time.


Consider the Entire System

Think about the motor's application, the presence of a motor starter, and any other factors that might influence the breaker selection.

Err on the Side of Safety

If you're unsure, it's generally better to choose a slightly larger breaker than one that's too small and risks nuisance tripping. However,
never exceed the maximum values in NEC Table 430.52.

Verify Coordination

Ensure that the OCPD coordinates with any other protective devices in the motor circuit (e.g., overload relays).

In summary, Square D's 90A recommendation is likely based on the specific trip curve of their motor-rated circuit breakers, which allows for higher inrush current without nuisance tripping, while still providing adequate overload and short-circuit protection.
The NEC value is a maximum allowable, not a requirement, and the calculator is leveraging the specific characteristics of the Square D breaker to get closer to the ideal protection level. Always follow manufacturer recommendations when available. Flag for review