Question: I've been tasked with putting together a rough estimate for a medium voltage overhead line. All my design experience is from the utility source down, so this foray into the medium voltage world is new to me, and I'm hoping someone here can provide me a little guidance on determining what this installation will look like. Below are my parameters:I need to span about 800'-1000' total from the source to my building, where we'll be feeding a pad mount transformer.Overhead line will be 6.9 KV, 3 conductor.This will be installed on a large industrial site, so the span is pretty much clear (no buildings or homes in the vicinity of the line).Is there a rule of thumb that can help me roughly determine pole span, pole heights, type of pole, etc.? What about conductor size/type?

Okay, let's break down estimating your 6.9 kV overhead line. Remember, this is a rough estimate. A proper design requires a qualified engineer considering local codes, regulations, safety factors, and site-specific conditions.1. Pole Span



Typical Span

For 6.9 kV lines, and considering your clear ROW, a typical span range is 300-400 feet. Longer spans can reduce the number of poles, but they also increase conductor sag, tension, and require stronger poles.


Your Distance

For 800-1000 feet, you're looking at likely needing

3 poles
(assuming two spans). Two 400-foot spans would be most economical. If you want a little extra safety margin, go with three 333-foot spans and four poles.2. Pole Height



Minimum Clearance

The most critical factor here is the required vertical clearance from the lowest conductor to the ground. The National Electrical Safety Code (NESC) is the governing document in the USA, and your local utility also likely has requirements. However, as a
very rough starting point: Open land (no roads): 18 feet Roads: 20 feet Railroads: 27.5 feet

Sag

The conductor will sag between poles, especially in warmer temperatures and under heavy loads. You need to add this sag to the minimum clearance to determine the lowest point the pole needs to be. Sag is dependent on span length, conductor type, and tension. For a 400-foot span, you could be looking at 4-6 feet of sag, maybe more.


Hardware

You need to add the height of the insulators and other hardware that will support the conductor. This is typically 2-3 feet.

Rule of Thumb

Minimum Pole Height = Clearance + Sag + Hardware. Example: 20 feet (road clearance) + 6 feet (sag) + 3 feet (hardware) = 29 feet minimum. You'd likely use a

35-foot pole
. It's common to use poles in 5-foot increments (30, 35, 40, etc.). Keep in mind, roughly 10% of the pole will be buried to provide support.3. Pole Type



Wood

Most common and generally the least expensive. Treated wood (typically with preservatives like pentachlorophenol or creosote) is essential to prevent rot and insect damage. Wood poles are rated by class (strength). For this application, a Class 4 or Class 5 pole would likely be sufficient, but this depends on the conductor size, wind loading, and ice loading in your area.


Steel

Stronger and more durable than wood, but also more expensive. Steel poles are often used for longer spans or in areas with high wind or ice loads.

Concrete

Very durable but also very heavy and expensive. Less common for distribution lines.


Recommendation

Wood poles are the most likely choice for your described application.

4. Conductor Size/Type



Load Calculation

You'll need to determine the expected load (kVA or Amps) that the padmount transformer will supply. This is the most important factor in selecting the appropriate conductor size. The conductor must be able to carry the load without overheating and causing excessive voltage drop.


Common Conductor Types



AAC (All Aluminum Conductor)

Lighter and less expensive than ACSR, but not as strong. Less likely for this application.


AAAC (All Aluminum Alloy Conductor)

Has a higher strength-to-weight ratio than AAC, but still not as strong as ACSR.

ACSR (Aluminum Conductor Steel Reinforced)

The most common type for distribution lines. The steel core provides strength, while the aluminum strands provide conductivity.


Rule of Thumb

Without knowing your exact load, I can't give you a precise conductor size. However, as a VERY rough starting point, for a moderate load, something like

1/0 ACSR or 2/0 ACSR
would be a reasonable guess. You will need to calculate your maximum loading to ensure that you do not exceed the ampacity of the conductor. Also, consider future load growth when designing the line. Considerations



Ampacity

The current-carrying capacity of the conductor.

Voltage Drop

The voltage drop along the line should be kept within acceptable limits (typically 5% or less).


Sag and Tension

The conductor's sag and tension are affected by temperature, load, and wind/ice loading.

Cost

Larger conductors are more expensive.

5. Hardware



Insulators

Pin-type or suspension insulators. Pin-type are common for lower voltage lines. Suspension insulators are used on higher voltages or to provide additional insulation.

Crossarms

Wood or steel crossarms to support the insulators.


Guys/Anchors

Often required for end poles and corner poles to provide stability and counteract the tension of the conductors.

Grounding

Proper grounding is essential for safety.

Steps for a Better Estimate


Determine Your Load

The most critical step. How much power will the padmount transformer be supplying?2.

Check Local Codes/Utility Requirements

Your local utility and building codes will have specific requirements for clearances, pole types, grounding, and other aspects of the installation. Contact them
early*.3.

Consult an Electrical Engineer

Seriously. Overhead line design is a specialized area. An engineer can perform the necessary calculations, ensure compliance with codes, and select the appropriate materials.4.

Get Quotes

Once you have a preliminary design, get quotes from pole suppliers, conductor suppliers, and electrical contractors.

Disclaimer:
This information is for general guidance only and should not be used as a substitute for professional engineering advice. Designing and installing an overhead power line is a complex and potentially dangerous task. Always consult with qualified professionals. Flag for review