Topic: POCO broke the service neutral during tree trimming...

User: theavidcitizen, Location: Eastern Washington State

Asked on: Friday, August 22, 2025 at 1:13 am EDT
Answered on: Friday, August 22, 2025 at 1:18 am EDT

Question: I got a call from a customer saying the utility company was on their property trimming tree branches away from her overhead service line, when something happened and they severed the service neutral somehow. The workers told the customer they had reconnected the neutral (how they did that without rerunning the service is still a mystery) and that everything should be fine.Everything was not fine.After getting her power restored, she called me to come and look at her place to see what was damaged. Immediately I noticed the burnt metal smell from the furnace, so I killed that circuit. None of her other electronics or appliances seem affected, and the voltages at the lugs were nominal (120-121V P-P, 121 P-G). I watched the voltages for about 15 mins, no fluctuations or spikes when she turned each appliance on.Anyway, I'm relatively new to residential service, but in the commercial world, this is almost a blank check from the utility. The utility company said to give her a list of what needs replaced and/or repaired and they would cover it. The panel is older, but not obsolete. The house is relatively old (1960's), but all the circuits and devices are in working order.Would you recommend a panel replacement/meter replacement/service mast replacement? I just don't think she should have to wonder about the breakers being damaged.

This is a classic open neutral scenario, and you're right to be concerned. While the voltage appears normal at the panel right now, the damage has likely been done, and the potential for future issues is high. Here's how I'd approach this, balancing safety and thoroughness with the utility company's willingness to pay

Understanding the Problem
Open Neutral Consequences

An open neutral disrupts the balanced return path for current. This causes voltage imbalances on the two legs of the 120/240V service. Some circuits can experience significantly higher voltage than others, leading to appliance damage (especially electronics with sensitive components).


The "Burnt Metal" Smell

This is a HUGE red flag. It almost certainly indicates that the furnace control board (or another component) was subjected to overvoltage and sustained damage. Even if it seems to be working now, its lifespan is significantly reduced.

Why the Voltage Looks Okay Now

The utility's "repair" might be providing a temporary, but potentially unreliable, neutral connection. Or, with a relatively balanced load across the two legs, the voltage difference between them might not be immediately obvious. This is a deceptive situation.

Recommended Actions


Here's a breakdown of what I'd recommend, in order of priority:1. Immediate Safety



Furnace

Do NOT let her use the furnace until it's thoroughly inspected and likely replaced. That burnt metal smell is a serious indicator. Disconnect it at the breaker.

Other Potentially Affected Appliances

While you didn't detect immediate problems, certain appliances are more susceptible to damage from voltage fluctuations:


Microwave

Check that it heats properly and the display works.

Refrigerator/Freezer

Ensure they are maintaining proper temperature.


Washer/Dryer

Confirm all cycles work, and that the dryer's heating element functions.

Dishwasher

Check for proper heating and water pump operation.


Electronics

TVs, computers, audio equipment, etc. Listen to speakers, and observe TV screens for any flickering.2.

Thorough Inspection and Documentation



Panel Inspection

Carefully inspect the panel itself. Look for signs of overheating:
Discolored bus bars. Melted or discolored insulation on wires near breakers. Loose or burnt connections at the neutral bus bar. Evidence of arcing.

Neutral Connections

Pay close attention to the service neutral connection at the meter and at the main panel. This is where the fault likely occurred.

Document Everything

Take detailed pictures and notes of:
The furnace damage. The panel condition. The service mast and meter condition. The utility's "repair" (if visible). Voltage readings at various points in the system (under different load conditions, if possible).3.

Replacement Recommendations (for the Utility Company)



Furnace Replacement

This is non-negotiable, in my opinion. The burnt smell is evidence of damage.


Panel Replacement

I would recommend this. An open neutral can stress the breakers and bus bars, weakening them over time. A new panel provides peace of mind and a fresh start. Justify this to the utility by saying that you cannot guarantee the integrity of the breakers after the voltage surges, and that replacing it is the only way to guarantee the safe operation of the system.

Meter Replacement

While not as critical as the panel, I would strongly suggest it. The meter may have been subjected to excessive voltage or current during the open neutral event. Its accuracy and reliability might be compromised.


Service Mast Replacement

Depends on its age and condition. If it's old or showing signs of rust or corrosion, I would recommend replacing it. It's better to have a new, reliable service entrance.

Service Neutral Wire

Make sure the entire run of neutral wire from the utility feed to the panel is replaced. Don't rely on a "reconnection" by the utility worker.4.

Important Considerations When Talking to the Utility Company



Emphasize Safety

Frame your recommendations in terms of ensuring the customer's safety and preventing future problems.

Be Specific and Detailed

Provide a clear and detailed explanation of why each replacement is necessary. Don't just say "replace panel." Say "Replace the panel because the bus bars may have been damaged by overvoltage, which could lead to breaker failure and a fire hazard in the future."


Get It in Writing

Make sure you have written authorization from the utility company before starting any work.

Liability

Make sure the utility company is fully aware that they are taking responsibility for any latent damage that might arise down the road as a result of this incident. It is reasonable to request a written acknowledgement of this from them.

Additional Advice
Consult with an Electrical Engineer (Optional)

For added assurance, consider consulting with a qualified electrical engineer. They can provide a more in-depth assessment of the damage and offer recommendations.

Check with Your Insurance

See if your insurance has an open neutral clause and if so, consider submitting the bill to them as the utility companies often try to back out of their initial promises.


Check with the Homeowner's Insurance

Have the homeowner notify their insurance company of the event. There may be coverage for damaged appliances and equipment that are not immediately obvious.

Home Surge Protection

Once everything is repaired, recommend a whole-house surge protector to protect against future surges.


Document all Discussions

Keep detailed notes of all conversations with the utility company, including dates, times, names, and what was discussed.

Customer Communication

Keep the customer informed throughout the process. Explain the risks involved and why you're recommending certain actions.


Don't Cut Corners:
This is not the time to try to save money or take shortcuts. The goal is to ensure the safety and reliability of the electrical system.This is a significant event, and you're right to be thorough. By following these recommendations, you can help your customer get their electrical system back to a safe and reliable condition, with the utility company covering the costs. Good luck! Flag for review