Topic: Box fill NEC 2017

User: Brandon002, Location: Tennessee

Asked on: Friday, August 22, 2025 at 9:20 am EDT
Answered on: Friday, August 22, 2025 at 9:20 am EDT

Question: If there was 3 #12 awg ground wire what would be the cubic inch? I’m under the impression you only count it once.Thanks in advance

You are correct that you only count ground wires once when calculating box fill.According to Table 314.16(B)(1) in the NEC, a #12 AWG conductor requires 2.25 cubic inches of free space.Therefore, three #12 AWG ground wires, counted as one, require 2.25 cubic inches of free space. Flag for review