User: Alwayslearningelec, Location: NJ
Asked on: Friday, August 22, 2025 at 11:18 am EDT
Answered on: Friday, August 22, 2025 at 11:18 am EDT
Question: When terminating conduits into the top of new switchgear you always need to drill ko's? How about if there is a crown box?
Okay, let's break down conduit terminations into the top of switchgear and the role of knockout (KO) drilling, especially when a crown box is involved.
General Rule: KO's are USUALLY Required
In almost all situations where you're running conduits into the top of switchgear, you'll need to create a knockout (KO) to provide the physical entry point for the conduit. Switchgear manufacturers typically ship the gear without pre-cut KOs in the top. This is for a few key reasons: Flexibility
The manufacturer doesn't know the specific size, number, or exact location of the conduits you'll need. Leaving the top solid allows the installer to customize the entry points to the project's requirements.
Sealing
Solid enclosures keep out debris and the elements prior to installation.
Code Compliance
Properly sized and located knockouts ensure compliant conduit entry points, addressing NEC (National Electrical Code) requirements for secure connections and protection of conductors.
The Role of a Crown Box (also called a Gutters or Auxiliary Gutter)
A crown box (auxiliary gutter) changes things somewhat, but doesn't eliminate the need for KOs entirely. Here's how it works: What is a Crown Box? A crown box or auxiliary gutter is an enclosure mounted on top of the switchgear. It provides a larger, more accessible space for making wire terminations, splices, and pull points. KO Implications with a Crown Box
Conduit-to-Crown Box
You'll still need KOs to bring the conduits into the crown box itself. The top of the crown box will typically not have pre-punched KOs for the same reasons as the switchgear's top. You'll select and create KOs based on your conduit runs.
Crown Box-to-Switchgear
You will also need to make KOs from the bottom of the crown box to allow the conductors to enter the top of the switchgear.
In Summary Direct Conduit-to-Switchgear (Top)
You always need to drill or punch KOs in the top of the switchgear to accommodate conduits unless the manufacturer provides a specific pre-manufactured opening or access plate for conduit entry.
Conduit-to-Crown Box-to-Switchgear
You need to drill or punch KOs into: The top of the crown box for conduit entry. The bottom of the crown box to align with an existing or created KO in the top of the switchgear for conductors to enter.
Important Considerations
Manufacturer's Instructions
Always refer to the switchgear manufacturer's instructions and specifications. They will provide critical information about acceptable KO sizes, locations, and any specific requirements for conduit entry.
NEC Compliance
Ensure all conduit entries and connections comply with the NEC (National Electrical Code) and any applicable local codes. Pay particular attention to: Proper bonding and grounding. Correct conduit fittings and connectors (e.g., bonding bushings, locknuts). Fill capacity of conduits and auxiliary gutters.
Workmanship
Create clean, burr-free KOs to protect conductors from damage. Use appropriate tools (KO punches are best) to avoid damaging the switchgear or crown box.
Wire Bending Radius: Consider wire bending radius of conductors when designing conductor routing.In conclusion, drilling KOs is almost always necessary when terminating conduits into the top of switchgear, whether directly or through a crown box. The exact size, location, and method will depend on the specific installation requirements and manufacturer's specifications. Always consult the relevant documentation and follow best practices for electrical safety and code compliance. Flag for review