Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MC cable when there is voltage drop

User: Tainted, Location: New York

Asked on: Saturday, August 23, 2025 at 10:08 am EDT
Answered on: Saturday, August 23, 2025 at 10:08 am EDT

Question: We are supposed to upsize the equipment grounding conductor if there is voltage drop.MC cables have preinstalled equipment grounding conductors in them so the only way to get the correct equipment grounding conductor size is to get a significantly larger MC cable with larger phase conductors for the correct equipment grounding conductor size...Is there a way to get custom MC cable with any equipment grounding conductor size?

You're right; upsizing the equipment grounding conductor (EGC) solely due to voltage drop on the ungrounded conductors isn't directly addressed in the NEC the same way upsizing for parallel conductors or for long runs in specific installations is. However, the principle of ensuring low impedance for fault current is essential, and voltage drop considerations can indirectly lead to needing a larger EGC.Here's a breakdown of the situation and some potential solutions

The NEC Perspective & Why It Matters
NEC 250.122 and Table 250.122

This table dictates the
minimum EGC size based on the overcurrent protection device (OCPD) protecting the circuit. It doesn't explicitly require upsizing for voltage drop considerations.

Impedance and Fault Clearing

The purpose of the EGC is to provide a low-impedance path back to the source so that a ground fault will quickly trip the OCPD. Excessive impedance (which can be increased by long runs and voltage drop considerations) can impede this process, delaying or preventing the OCPD from tripping in a timely manner. This is a safety hazard.

Voltage Drop Impact

While the NEC doesn't directly say "upsize the EGC due to voltage drop," the
effect of significant voltage drop can be increased impedance along the entire circuit path (including the EGC). This is especially true in long runs.

Why Standard MC Cable Can Be Problematic
Fixed EGC Size

As you noted, standard MC cable has a pre-determined EGC size based on the conductor size. If your voltage drop calculations lead you to use larger phase conductors than required by the load, you get a larger EGC... but that might be an inefficient and expensive way to do it.

Limited Upsizing Options

You might find yourself stuck with needing to jump to a much larger MC cable size just to get the EGC you need.

Possible Solutions & Workarounds
1. Parallel Conductors with a Dedicated EGC

This is often the best solution for long runs and high currents where voltage drop is a concern. You run two or more sets of phase conductors in parallel, and each set has its own neutral (if needed).

Crucially

You can then run a
separate, appropriately sized EGC alongside the parallel conductor sets. This EGC doesn't need to be inside an MC cable and can be sized independently, based on calculation and NEC requirements.

Important NEC Sections

NEC 310.10(H) (Parallel Conductors), NEC 250.122(C) (Parallel Conductors)2.

External EGC

In some situations, you might be able to install a supplemental, external EGC alongside the MC cable.

NEC Restrictions

This is generally only permissible in specific circumstances. For example, if the existing EGC within the MC cable is deemed inadequate, you might be able to supplement it.

Consult Your AHJ



Crucially
, you must get approval from your local Authority Having Jurisdiction (AHJ) before doing this. They will want to see your calculations and justification. It is also very important to ensure that any supplemental grounding electrode conductor and its termination points have appropriate protection to prevent corrosion.3. Custom MC Cable (Least Likely, but Possible)



Contact Cable Manufacturers

The only way to get custom MC cable with a specific EGC size is to contact cable manufacturers directly (e.g., Southwire, Encore Wire, Prysmian).

Minimum Order Quantities

Be prepared for potentially high minimum order quantities. They might not be willing to do a custom run for a small project.


Cost

Custom cable will be significantly more expensive than standard MC cable.

Lead Time

Expect a long lead time for production.


UL Listing

Ensure that the custom cable will be UL listed and meet all applicable standards. This can be a hurdle, as the manufacturer will need to demonstrate compliance.4.

Careful Calculations and Conservative Design

Before resorting to parallel conductors or custom cable, meticulously calculate voltage drop and impedance. Consider a slightly larger standard MC cable size than strictly required by the load, even if it's primarily to get a larger EGC. This is often the most practical and cost-effective approach if the voltage drop isn't extreme.5.

Consider the Total Impedance

The NEC is focused on fault current clearing time, which depends on the total impedance of the fault current path. This includes the source impedance of the transformer, the impedance of the ungrounded conductors, the neutral (if any), and the EGC. If the voltage drop is relatively minor, and the existing EGC in the MC cable is already a reasonable size, the overall impedance might still be low enough to ensure proper OCPD operation.

Important Considerations and Best Practices
Consult with a Qualified Electrical Engineer

For complex installations, especially those with long runs or critical loads, it's highly recommended to consult with a qualified electrical engineer. They can perform detailed calculations and ensure that the system meets all applicable codes and standards.


Document Everything

Keep meticulous records of your calculations, justifications, and any approvals from the AHJ.

AHJ Approval is Key

Always get approval from your local AHJ before implementing any non-standard solutions. They have the final say on what is acceptable in your jurisdiction.


Regular Maintenance

Regardless of the installation method, regular inspection and maintenance of the electrical system are essential to ensure continued safe and reliable operation.

In summary:
Upsizing the EGC based on voltage drop considerations is about ensuring low enough impedance for effective fault current clearing. Parallel conductors with a separate, appropriately sized EGC is often the best approach. Custom MC cable is a possibility but usually impractical. Always consult the NEC, perform thorough calculations, and get AHJ approval. Prioritize safety and performance. Flag for review

Previous Question Next Question