Question: In a sub panel on a detached structure, does the neutral get bonded to ground?
No, in a subpanel on a detached structure, the neutral should not be bonded to ground.Here's why: Single Point Bonding
The neutral and ground should only be bonded together at the main service entrance (where the power comes into the property). This creates a single point of reference for the electrical system.
Avoiding Parallel Paths
If you bond neutral to ground in a subpanel, you create a parallel path for neutral current to flow on the grounding conductors. This is undesirable because: It can cause nuisance tripping of GFCI breakers. It can energize metal parts of the system, creating a shock hazard. It violates electrical code.
Detached Structure Requirements
Electrical codes specifically require that detached structures with subpanels have: A separate neutral and ground. An insulated neutral conductor run from the main panel to the subpanel.* A grounding electrode system at the detached structure (e.g., ground rods, ground ring). The grounding electrode system is connected only to the ground bar in the subpanel.
In summary:
In a subpanel of a detached structure the neutral should be isolated from the ground and the ground should have its own independent grounding electrode system such as ground rods. Flag for review