Question: We had a problem with our Makino S56 after we relocated our shop from an industrial park with 120/208 3-phase to a rural location with single phase power. My searches took me to this site, specifically the thread:Grounding delta delta transformers on CNC machinesWe have several CNC machines that are ungrounded. Most have 480/240 delta delta transformers sitting right on the machine. We have been told by Mitsubishi, Fanuc, and other machine tool technicians that is part of a problem we have been having with NC units going bad. I will order or machine...
Okay, I understand. You relocated your Makino S56 CNC machine from a location with 3-phase power to a rural location with single-phase power, and now you're experiencing problems. You also found a thread about grounding Delta-Delta transformers and how it relates to CNC machine reliability. This makes sense, as power quality issues are often exacerbated when converting machines designed for 3-phase operation to single-phase using a phase converter or other solution.Here's a breakdown of the potential issues, why the thread you found is relevant, and how to approach troubleshooting
Why Single-Phase to 3-Phase Conversion Can Cause Problems with CNC Machines:
Phase Balancing
CNC machines designed for 3-phase power expect balanced voltage across all three phases. Single-phase to 3-phase conversion (especially with rotary converters) rarely provides perfectly balanced phases. This imbalance can stress the machine's power supply, motors, and sensitive electronics.
Voltage Fluctuations and Harmonics
Phase converters (static and rotary) can introduce voltage fluctuations and harmonics into the power supply. These "dirty" power issues can disrupt sensitive CNC controls, leading to errors, failures, and reduced machine lifespan.
Grounding and Bonding
Proper grounding is absolutely critical for CNC machines. Improper grounding, or changes to the grounding scheme during the relocation/conversion process, can create ground loops, increase electrical noise, and expose the machine to damaging voltage spikes.
Delta-Delta Transformer Grounding
The thread you found touches on a key issue. Delta-Delta transformers, particularly those used to step-down voltage on the machine, can be ungrounded (or "floating"). While this can be acceptable in certain situations, it can also lead to significant problems, especially if there are insulation faults or voltage imbalances. The ungrounded system can develop large potential differences relative to ground, which can then discharge through sensitive components.
Relevance of the Delta-Delta Transformer Grounding Thread
The thread you linked is highly relevant because it highlights a common issue:
Ungrounded Systems Can Be Problematic
The advice from Mitsubishi, Fanuc, and other technicians mentioned in the thread is generally sound. Ungrounded Delta-Delta transformers can increase the risk of electrical problems in CNC machines.
Component Damage
The thread directly connects the ungrounded transformer to failures in the NC unit (Numerical Control unit), which is a common symptom of power-related issues in CNCs.
Troubleshooting Steps for Your Makino S56
1.
Verify Your Phase Conversion System
Type of Converter
Determine the type of phase converter you're using (rotary, static, VFD, etc.). Each has its pros and cons in terms of power quality. Rotary converters are generally better than static converters. VFD's are the ideal choice if the single to three phase converter is used for a single machine with a single 3 phase motor.
Converter Sizing
Ensure the converter is adequately sized for the Makino S56. Undersized converters will struggle to provide sufficient power and can create voltage drops. Check the machine's power requirements (nameplate amperage) and factor in a safety margin.
Output Voltage and Balance
Measure the voltage between each phase and the voltage from each phase to ground. Ideally, the voltage between phases should be as close to 208V as possible (if that's the machine's voltage requirement), and the voltage to ground should be relatively stable and within acceptable limits. Note any significant voltage imbalances.2.
Inspect the Machine's Grounding System
Check the Ground Connection
Verify that the machine has a solid, low-impedance connection to the main electrical ground. Look for a thick ground wire connecting the machine's frame to the building's grounding electrode system.
Ground Wire Size
Make sure the ground wire is appropriately sized for the machine's amperage.
Ground Loops
Check for potential ground loops (multiple paths to ground). While not always avoidable, excessive ground loops can increase noise.
Transformer Grounding (Critical)
This is where the thread you found is most important. Carefully inspect the Delta-Delta transformer on the machine. Determine if it's grounded or ungrounded. If it's ungrounded, consult with a qualified electrician or CNC machine technician about the possibility of grounding it (e.g., corner grounding or using a grounding transformer).
DO NOT attempt to ground the transformer yourself without expert guidance. Improper grounding can be dangerous and cause further damage.3. Assess Power Quality
Voltage Fluctuations
Monitor the voltage at the machine's main power input for fluctuations. Use a multimeter or, ideally, a power quality analyzer to capture voltage sags, swells, and transients.
Harmonics
Measure the harmonic distortion in the voltage and current. High harmonic distortion can damage sensitive electronics. A power quality analyzer is needed for this.
Transient Voltage Surge Suppression (TVSS)
Ensure that the machine has adequate surge protection. A good TVSS device can help protect against voltage spikes caused by lightning or other electrical disturbances.4.
Review the Machine's Documentation
Power Requirements
Re-examine the Makino S56's documentation to confirm its voltage and amperage requirements.
Grounding Recommendations
Look for any specific grounding instructions or recommendations from Makino.5.
Consult Professionals
Qualified Electrician
Engage a licensed electrician with experience in CNC machine installations and grounding.
CNC Machine Technician
Contact a Makino service technician or a CNC machine repair specialist. They can diagnose the problem and recommend the appropriate solutions.
Power Quality Specialist
If you suspect significant power quality issues, consider hiring a power quality consultant to perform a thorough analysis.
Important Considerations
Safety First
Always disconnect power to the machine before working on any electrical components.
Qualified Personnel
Electrical work on CNC machines should only be performed by qualified professionals.
Documentation
Keep detailed records of your troubleshooting steps, measurements, and any changes you make to the electrical system.
In Summary:
Your problem is likely related to the single-phase to 3-phase conversion and its impact on the machine's power quality and grounding. Thoroughly investigate your phase converter system, the machine's grounding, and the Delta-Delta transformer's grounding configuration. Don't hesitate to consult with qualified professionals to ensure a safe and effective solution. Good luck! Flag for review