Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Adjustments and derating

User: Alwayslearningelec, Location: NJ

Asked on: Sunday, August 24, 2025 at 3:51 pm EDT
Answered on: Sunday, August 24, 2025 at 3:51 pm EDT

Question: When you derate you can't use the 90 degree for conductors landing on terminals if they are rated for 75 degree?

That's correct. Here's a breakdown of why: Derating

Derating involves reducing the ampacity of a conductor based on factors like ambient temperature, number of current-carrying conductors in a raceway, etc. This is done to prevent the conductor from overheating and potentially causing insulation damage or a fire.


Conductor Ampacity Tables

The ampacity of conductors are found in NEC (National Electrical Code) tables, typically based on temperature ratings (60°C, 75°C, and 90°C).

Termination Temperature Ratings

Electrical equipment (circuit breakers, switches, receptacles, etc.) has termination temperature ratings. These ratings specify the maximum conductor temperature the equipment's terminals can safely handle. Common ratings are 60°C and 75°C. 90°C terminations are less common but are available.


The Rule



Regardless of the conductor's insulation temperature rating (e.g., THHN, which is rated 90°C), you must use the ampacity column corresponding to the lowest temperature rating of the conductor, terminals, or connected equipment.
Why this matters

If you have equipment rated for 75°C terminations, you cannot use the 90°C ampacity column for the conductor landing on that equipment, even if the conductor insulation itself is rated for 90°C and you've derated based on that 90°C ampacity. The heat generated at the terminal could exceed the 75°C rating, damaging the equipment.

Example

Let's say you have a circuit with #12 AWG THHN (90°C rated) conductors. You need to run 10 current carrying conductors in a conduit, so you need to derate.1.

Start with the 90°C Ampacity

For #12 THHN, the 90°C ampacity is 30A.2.

Apply Derating

The derating factor for 10 current-carrying conductors (assuming using Table 310.15(C)(1)) is 50%. So, 30A 0.50 = 15A.
3.


Check Termination Temperature

If the circuit breaker and receptacle are only rated for 75°C, you
cannot use the 15A ampacity calculated above.4.

Use the 75°C Ampacity

The 75°C ampacity for #12 is 25A. Derated by 50%, that becomes 25A
0.50 = 12.5A.
5.


The Final Ampacity

You must use the lower of the two derated ampacities. In this case, you would be limited to a maximum of 12.5 amps on that circuit, even though the wire insulation is rated for 90°C and you derated the 90°C ampacity. You might be better off using a larger conductor to begin with.
6. Futhermore you need to round down to the nearest breaker size. So if the max ampacity on the wire is 12.5A the maximum breaker size is 10A.


In Summary:
Derating affects the ampacity of the conductor. Termination temperature ratings limit the temperature at the point where the conductor connects to equipment. You must always respect the lowest temperature rating in the system (conductor, terminal, or equipment). When derating, after you calculate the derated ampacity, you must always compare that ampacity to the ampacity rating that matches your terminations. Select the lower value as the safe ampacity of your wire. Flag for review

Previous Question Next Question