Question: Ok so if there was a question( size a THHN for a 49a load terminating to a 75c terminal)You would still stay and size your wire in that column right?
Yes, that's correct. Even though the load is 49 amps, and you're using THHN wire, the termination temperature rating is the controlling factor.Here's a breakdown of why: Termination Temperature Rating (75°C)
This is the weakest link in the circuit. The terminals of breakers, panels, and equipment are rated for a maximum operating temperature. If the wire connected to them runs too hot, it can damage the terminal insulation and lead to overheating, arcing, and potentially a fire.
NEC 110.14(C)
This section of the National Electrical Code (NEC) specifically addresses termination temperature limitations. It requires you to select conductors based on the temperature rating of the lowest-rated termination point (e.g., the breaker, the panel, or the equipment).
THHN Wire
THHN wire typically has a higher temperature rating (90°C) in dry locations. However, you cannot take advantage of that higher rating if your terminations are only rated for 75°C.
Therefore, you must size your THHN wire based on the ampacity in the 75°C column of NEC Table 310.16, even though the wire itself can handle higher temperatures.In your specific example (49A load, 75°C terminals)
Consult NEC Table 310.16
Look at the 75°C column.2.
Find Ampacity
Find the smallest wire size that has an ampacity equal to or greater than 49 amps.In the 2023 version of the NEC, the minimum wire size for a 49 amp load would be a #8 AWG copper conductor.
Important Considerations
Overcurrent Protection
Remember to also size your overcurrent protection (circuit breaker or fuse) appropriately. The overcurrent protection must protect the wire at its ampacity, but should not exceed the ampacity. The next standard size up can be used as per the round up rules in NEC 240.4(B).
Voltage Drop
Always check for voltage drop, especially on long runs. You may need to increase the wire size to minimize voltage drop, even if the ampacity is sufficient.
Aluminum vs. Copper
The ampacity of aluminum wire is different from copper. Make sure you are using the correct table in the NEC.
Specific Equipment Requirements
Some equipment manufacturers may have specific wiring requirements that override the NEC. Always refer to the equipment's documentation.
Qualified Electrician: Electrical work can be dangerous. It is highly recommended to consult with a qualified electrician for any electrical installations. Flag for review