User: brycenesbitt, Location: United States
Asked on: Monday, August 25, 2025 at 12:16 pm EDT
Answered on: Monday, August 25, 2025 at 12:16 pm EDT
Question: Question:Under engineering supervision, what latitude if any does the engineer to countheat rather than wires? Anyone dealt with a situation that required it, and how did it go?--The situation:An electrical room with a 2" existing rigid conduit and pull string, empty.It leads roughly 30" through a post tension slab to a garage below.The game is to get as many circuits as possible through that conduit without having to core the slab again.They have to be individual circuits.Wires will be landed on terminal blocks such as Eaton 14002-4, then on to eventual OCPDs.But they're of mixed types.Some are continuous loads, some not.Some are low voltage control cables.Some are at different capacities with different OCPDs.--------------------------------Assuming they were all the same type, do I have it about right?#8 wire at 90C, start at 55A per 310.16Apply 50% factor, so down to 27.5 amp.36 total #8 conductors for the 2" conduit ("Jam probability 9%" per south wire). 37.64% fill OK.Total capacity of 12 circuits * 27.5 amps = 330 amps continuous.But can better be done?#10 wire at 90C, start at 40A per 310.16Apply 45% factor, so down to 18 amp.Now we're good to 66 #10 conductors for the 2" conduit ("Jam probability 13%" per south wire).Total capacity of 22 circuits * 18 amps = 396 amps.Or maybe#12 wire at 90C, start at 30A per 310.16Apply 35% factor, so down to 10.5 amp.Now we're good to 102 #12 conductors for the 2" conduit ("Jam probability 16%" per south wire). 38.52% fill.Total capacity of 34 circuits * 10.5 amps = 357 amps.--------------------------------Can the distance to the terminal block be considered to reduce the actual terminal temperature:75C Terminal block --------------20 feet of wire at 70F ambient --------- 30 inch of conduit ------------ 20 feet of wire at 90F ambient ----- 75C terminal--------------------------------So apparently the #10's are the best for this formula, no?But the question was about 310.14(B). The way I'm reading it the engineer discretion is only to apply a formula on an individualwire, not a total load calculation on a bundle of wires. Is that a correct reading? Could an engineer look at this entire system of wires (continuous loads and non-coincident loads) and do a temperature calculation instead for the inside of the 30 inch constrained conduit ? Or a measurement?
This is a great question with a lot of important considerations. Let's break it down
Understanding "Counting Heat" vs. Counting Wires
The core of your question revolves around NEC 310.14(B) and the engineer's latitude to deviate from standard ampacity tables based on thermal calculations. The NEC is primarily a prescriptive code – it tells you what to do. Engineering calculations are performance based -- you show why a deviation is safe. Counting Wires (Prescriptive Approach)
This is the standard method. You use tables like 310.16 and apply derating factors based on the number of current-carrying conductors in a raceway. This is straightforward but can be conservative. You've started down this path in your calculations.
Counting Heat (Engineering Analysis)
This is where you leverage 310.14(B) and other relevant sections. It allows for a more precise determination of ampacity based on:
Conductor Insulation Temperature Rating
90°C for THHN, XHHW, etc.
Ambient Temperature
The temperature around the conductors.
Heat Dissipation
How well the heat generated by the conductors can escape.
Latitude Under Engineering Supervision
Under qualified engineering supervision, the engineer can perform calculations and/or measurements to justify a higher ampacity than what the standard tables might allow if the engineer can demonstrate the temperature rating of the conductors, terminations and equipment will not be exceeded, and all relevant factors are considered. Crucially, this requires: Professional Judgment
The engineer must possess the knowledge and experience to perform these calculations accurately.
Thorough Analysis
A complete thermal analysis is needed, considering all relevant factors, as outlined in 310.14(B) and related sections.
Documentation
The analysis must be clearly documented and readily available for inspection.
AHJ Acceptance
The Authority Having Jurisdiction (AHJ) ultimately decides whether to accept the engineering analysis. This means you need to discuss your proposed approach with the AHJ beforehand!
Why Would You "Count Heat"?
In your situation, you have a limited raceway size and the desire to maximize circuit capacity. This is the exact scenario where "counting heat" becomes valuable. Standard derating factors can be excessively conservative, especially for short raceway runs.
Your Situation Analysis
Let's look at your calculations and some key considerations:1. Calculations - Prescriptive approach Your individual calculations are correct following 310.16. However, using the prescriptive ampacity adjustment factors is a very conservative route that may not reflect actual operational conditions. The numbers that you've presented show that a #10 wire at 90C is the most efficient way to get power through the conduit prescriptively.2. Mixed Loads
This is a critical point. You can't simply add up the ampacity of all the circuits. You need to consider:
Demand Factors
Are all circuits loaded to their maximum simultaneously? NEC Article 220 addresses demand factors for various load types.
Non-Coincident Loads
Are some loads mutually exclusive (e.g., one load runs only when another is off)?3.
Low-Voltage Control Cables
Are they power limited (Class 2 or Class 3)? If so, they might not need to be considered as current-carrying conductors for derating purposes, check NEC 7254.
Conduit Length
30" through the slab is short! This is a huge advantage for heat dissipation. The prescriptive conduit fill limitations and ampacity adjustment factors are in place to protect wires in long runs of conduit in thermally-insulated building walls. In this installation, the short conduit run and heat sink offered by the concrete slab give you a lot of thermal headroom.5.
Ambient Temperature
The ambient temperature is critical. Assume the highest possible temperature in that garage.6.
Terminal Blocks
Temperature Rating
Use terminal blocks with the highest temperature rating you can find (preferably 90°C).
Termination Temperature
The weakest link is often the termination temperature rating of the connected equipment (breakers, panels, etc.).7.
The 20-foot Wire Runs
Your diagram raises an important point. You might be able to use a lower-temperature-rated wire (e.g., THHN/THWN, rated 75°C at the termination) for the 20-foot sections if the voltage drop is acceptable and the overall system is designed for it. However, using 90°C wire throughout simplifies things and provides more margin.
Can the Distance to the Terminal Block be Considered?
Yes, to some extent. This is where thermal modeling comes in. You need to consider the temperature gradient along the wire. The heat generated in the conduit will dissipate along the 20-foot run. However, you can't simply assume the wire magically reaches 70°F. You need to calculate the temperature profile.
Is an Engineer's Discretion Limited to Individual Wires?
No, the engineer's discretion extends to the entire system. 310.14(B) allows for calculations considering the entire installation. It's not just about the ampacity of a single wire; it's about ensuring the entire system remains within safe temperature limits.
Proposed Approach – "Counting Heat"1. Documentation
Gather all the relevant information about the circuits, loads, conductors, terminal blocks, ambient temperatures, and the raceway.2.
Engineering Analysis (Thermal Modeling)
The most accurate way to determine the ampacity is through a thermal model. Software exists for this purpose. Alternatively, you can create a simplified heat transfer model using hand calculations (conduction through the wires, convection, and radiation).
This is where an experienced engineer is essential. The temperature calculation would be based on each circuit's current and associated heat generation. The model needs to consider the 30-inch conduit run. A finite element analysis is often overkill, and can be achieved through "lumped parameter" modeling.3. AHJ Consultation
Before investing significant time and effort, discuss your approach with the AHJ. Explain that you are proposing an alternative method based on engineering analysis and want to ensure they will consider it.4.
Testing (Optional)
If the AHJ is hesitant or the analysis is complex, consider performing a real-world test. Install a representative sample of the circuits, load them to the calculated ampacity, and monitor temperatures with thermocouples. This provides empirical evidence to support your analysis.5.
Code Compliance
All of the equipment and conductors in the circuit need to be compatible with the engineer's designed circuit ampacity. The engineer needs to ensure that the terminals, wires, and conductors are rated for the amperage and temperature required by the proposed circuit design. For example, the prescriptive calculations resulted in the use of #10 wires at 90C, however, the terminals may only be listed to a maximum of 75C. All elements of the circuit need to be rated to the higher designed capacity.
Example Scenario: Simplified Heat Transfer
Imagine a scenario where you determine, through detailed load analysis and using demand factors, that the actual load on the conduit is significantly lower than the sum of all the circuit breakers. You perform a simplified heat transfer calculation that shows the temperature inside the conduit will not exceed 75°C with the proposed wire sizes and ampacities, considering the short conduit length and the thermal mass of the concrete slab. You document this thoroughly, get the AHJ's blessing, and proceed.
In Summary You can "count heat" under engineering supervision, but it requires a rigorous engineering analysis, thorough documentation, and AHJ acceptance. Your situation is ideal for this approach due to the short conduit length and mixed loads. Don't underestimate the importance of communication with the AHJ early in the process. #10 wires may be the most efficient way to achieve capacity prescriptively, but an engineering analysis and heat modeling can provide different, and often more efficient, results.* Be sure to consider, model, and account for, the temperature rating of all connected equipment.By following these steps, you can likely maximize the capacity of your existing raceway while ensuring a safe and code-compliant installation. Good luck! Flag for review