Topic: Correcting V.D. with Buck Boost Transformers
User: RPEC_Muns, Location: Rancho Cucamonga, CA
Asked on: Monday, August 25, 2025 at 6:55 pm EDT
Answered on: Monday, August 25, 2025 at 7:01 pm EDT
Question: We are working on a project where the electrical engineer is using a Buck Boost Transformer to correct the voltage due to the distance from the electrical panel. We feel that it will not work but unable to prove or disprove that we will have the correct voltage at the receptacle.The incoming voltage is 120-volt, 1-phase circuit, distance from the panel to the buck boost transformer is 1,300-ft and they are specifing #10AWG wire. They indicate to provide 120V/120V 2KVA buck boost transformer and showing a electrical load of 720VA. From the transformer to the receptacle is another 300-ft with #10AWG.I've read some of the buck boost transformers can boost/correct the voltage by up to 25% but I've was unable to determine/confirm if this will work.
Okay, let's break down this scenario and see if the proposed solution using a buck-boost transformer with #10 AWG wire over those distances will work for a 720VA load on a 120V circuit. This involves calculating voltage drop.
Understanding the Problem: Voltage Drop
The core issue is voltage drop over the long wire runs. As current flows through a wire, it encounters resistance. This resistance causes a voltage drop, meaning the voltage at the end of the wire is lower than the voltage at the source (the electrical panel). The longer the wire and the higher the current, the greater the voltage drop.
Calculations and Considerations
We'll use a standard voltage drop formula to estimate the voltage drop in each segment of the circuit. A simplified formula for single-phase circuits is:
VD = (2 K I L) / CM
Where: VD = Voltage Drop (in volts)
K = DC Resistance (Ohms-circular mils/ft.) depends on wire material. 12.9 Ohms-circular mils/ft. for Copper I = Current (in amps)
L = One-way length of the wire (in feet) CM = Circular Mils (a unit of wire size)1.
Calculate the Current (I)
Load VA = 720VA Voltage (V) = 120V Current (I) = VA / V = 720VA / 120V = 6 Amps2.
Determine Circular Mils (CM) for #10 AWG
#10 AWG has a cross-sectional area of approximately 10,380 circular mils.3.
Voltage Drop Calculation - Panel to Buck-Boost Transformer (1300 ft)
VD1 = (2 12.9 6 1300) / 10380 VD1 = 198,840 / 10380 VD1 = ~19.16 Volts4.
Voltage at the Buck-Boost Transformer Input
Starting Voltage (Panel) = 120V Voltage Drop (VD1) = 19.16V Voltage at Transformer = 120V - 19.16V = 100.84V5.
Voltage Drop Calculation - Buck-Boost Transformer to Receptacle (300 ft)
VD2 = (2 12.9 6 300) / 10380 VD2 = 46,440 / 10380 VD2 = ~4.47 Volts6.
Voltage at the Receptacle (Without Buck-Boost Correction)
Voltage at Transformer (Before Correction) = 100.84V Voltage Drop (VD2) = 4.47V Voltage at Receptacle = 100.84V - 4.47V = 96.37V
Analysis and Conclusions Significant Voltage Drop
The calculations show a significant voltage drop, particularly in the long run from the panel to the buck-boost transformer. Without correction, the voltage at the receptacle would be approximately 96.37V, well below the acceptable range. Buck-Boost Transformer Capability
The 2kVA buck-boost transformer could potentially correct this, IF it's designed to compensate for the voltage drop. Here's the key: Boost Range
You must know the transformer's boost range. A typical buck-boost transformer might have taps or configurations that allow it to boost the voltage by a fixed percentage (e.g., 5%, 10%, 15%, or perhaps even up to 25%). Sizing (kVA)
The 2kVA rating is more than sufficient for the 720VA load after the voltage is corrected. The important thing is that the transformer can handle the current at the lower voltage coming in. At 100.84V input, the current drawn by the 720VA load before voltage boost would be 720VA / 100.84V = ~7.14 Amps. This is under the 2KVA rating of the transformer. However, voltage transformers typically do not provide the ability to boost VA, only to maintain VA. Therefore, the incoming VA is still 720VA, only delivered at 100.84V and will boost to 120V. Will it work? The big IF
Scenario 1: No Correction
Definitely won't work. 96.37V at the receptacle is unacceptable. Scenario 2: Buck-Boost CAN Compensate
If the buck-boost transformer can accept 100.84V and boost it back up to 120V, it might work, but you'd still have the small voltage drop from the transformer to the receptacle. Transformer Output: 120V Voltage Drop (300ft to Receptacle): 4.47V Voltage at Receptacle: 120V - 4.47V = 115.53V NEC Considerations
The National Electrical Code (NEC) generally recommends voltage drop to be no more than 3% for branch circuits (circuits feeding receptacles). 5% is the limit for feeders plus branch circuits. 3% of 120V = 3.6V 5% of 120V = 6V In our case, the voltage drop from the panel to the receptacle is 19.16 + 4.47 = 23.63V, which is 19.69% (23.63 / 120), which is far above the recommended values.Recommendations and Alternatives1.
Verify Buck-Boost Transformer Capability
Crucially, get the specification sheet for the exact buck-boost transformer being proposed. Determine its input voltage range and the available boost settings. Can it actually boost from around 101V to 120V?2.
Increase Wire Size
The best solution is almost certainly to increase the wire size, especially for the long run from the panel to the transformer. Larger wire has lower resistance and therefore lower voltage drop. Consider #6 AWG or even larger. Recalculate the voltage drop with the larger wire. Using #6 AWG (26,240 CM): VD1 (Panel to Transformer): (2 12.9 6 1300) / 26240 = ~7.70V Voltage at Transformer: 120V - 7.70V = 112.30V Then, the transformer only needs to boost by about 7.70V. VD2 (Transformer to Receptacle - Still #10AWG): (2 12.9 6 300) / 10380 = ~4.47V (unchanged) Voltage at Receptacle (Assuming Buck-Boost corrects): 120V - 4.47V = 115.53V. You are still having the same voltage drop issue from transformer to receptacle. Total Voltage Drop: 7.70 + 4.47 = 12.17V, which is ~10.1% (12.17/120). Still exceeds NEC's recommended voltage drop. Using #6 AWG for both runs: VD2 (Transformer to Receptacle): (2 12.9 6 300) / 26240 = ~1.76V Voltage at Receptacle (Assuming Buck-Boost corrects): 120V - 1.76V = 118.24V Total Voltage Drop: 7.70 + 1.76 = 9.46V, which is ~7.9% (9.46/120). Still exceeds NEC's recommended voltage drop.
3.
Move the Transformer
If possible, move the buck-boost transformer closer to the receptacle. This reduces the length of the lower-voltage run after the transformer, minimizing voltage drop.4.
Run a New Circuit
The best, but potentially most expensive, solution would be to run a new, dedicated circuit from the panel with appropriately sized wire.5.
Consider a Higher Voltage
Depending on the load, consider a 240V circuit if feasible (with appropriate transformer to step down at the point of use). 240V circuits allow for lower current and therefore less voltage drop for the same power.
In summary, the proposed solution with #10 AWG over those distances is highly unlikely to work adequately, even with a buck-boost transformer, unless the transformer has exceptional boosting capabilities and the application is tolerant of low voltage. Increasing the wire size is the most practical and reliable approach. You need to calculate the voltage drop with a proposed wire size and see if it meets NEC recommendations.