Topic: Proposed NM Cable ampacity in WA State

User: tom baker, Location: Bremerton, Washington

Asked on: Monday, August 25, 2025 at 8:11 pm EDT
Answered on: Monday, August 25, 2025 at 8:11 pm EDT

Question: WA labor and industries has a proposal to change NM-B ampacity for 8 and larger to be the 75 deg C rating in WAC 296-46B. Pubic comments will be accepted Oct 7 and the final rule will be issued Dec 19It will be interesting to see comments but there are likely many EV charging stations on 8 NMB at 60 ampsLink https://lni.wa.gov/licensing-permits/_docs/Draft-Rule-Language-Version1.pdfAdvantage is for 6 NM-B on a 60 amp circuit for EVS.

Okay, I understand. Here's a breakdown of the situation and why this proposal from Washington State Labor and Industries (L&I) regarding NM-B cable ampacity is significant

The Core Issue:
Current Practice

Under the National Electrical Code (NEC), which most states (including Washington) adopt as a baseline, NM-B cable (the common "Romex" cable used in residential wiring)
typically uses the 60°C column for ampacity ratings, with some exceptions.

L&I Proposal

Washington L&I is proposing to change WAC 296-46B to specify using the 75°C ampacity rating for NM-B cable sizes 8 AWG and larger. This is a notable shift.

Impact

This effectively increases the allowable current-carrying capacity for those larger NM-B cables.

Why This Matters



EV Charging

As you correctly point out, the rise of electric vehicle (EV) charging is a major driver. Many Level 2 EV chargers require significant amperage (often 40-60 amps). Using the 60°C rating, an 8 AWG NM-B cable might not be sufficient for a 40-50 amp EV charger circuit, and a 6AWG would be required for 60A charger.

Cost Savings

This proposed change could potentially reduce the cost of EV charger installations, since 8 AWG cable is more easily installed and is generally less expensive than larger gauge wire.


Other High-Demand Applications

The change would also benefit other applications that require high amperage, such as: Electric ranges and ovens HVAC systems Welding equipment Electric water heaters

Potential Advantages



6 AWG NM-B for 60A circuits

Using the 75°C rating on 6 AWG NM-B wire will allow the use of 60-amp circuits for EV charging.


Lower Installation Costs

Using smaller gauge wire for higher ampacity applications can reduce material and labor costs.

Easier Installation

Smaller gauge wires are easier to bend, pull, and terminate, making installations faster and more efficient.

Potential Concerns and Points for Public Comment (Things to Consider)



Safety

The primary concern is, of course, safety. While the 75°C ampacity rating is higher, it's based on the cable's ability to withstand higher temperatures. Key questions: Are the terminals/devices being connected to also rated for 75°C? (This is usually required by code, but it needs to be explicitly addressed.) Are there any potential increased risks of overheating, especially in tightly bundled installations, installations in insulated walls, or installations where the ambient temperature is already high? Could this lead to misinterpretations or incorrect installations, with installers assuming all NM-B cable can use the 75°C rating?

Code Compliance

While states can amend the NEC, changes should ideally be based on sound engineering principles and not create conflicts with other parts of the code. How does this align with the NEC's overall approach to ampacity ratings and safety factors?

Device Compatibility

All terminations and devices (breakers, receptacles, etc.) must be rated for the temperature rating of the conductor being used. This is usually 75C but must be verified.


Inspector Training

Inspectors will need to be thoroughly trained on the new rule to ensure consistent and correct enforcement.*

Industry Impact

How will this impact electrical contractors, suppliers, and manufacturers?

What to Do


Read the Draft Rule Carefully

You've already linked to it, but make sure you understand the exact wording and scope of the proposed change.2.

Submit Public Comments

If you have expertise or concerns, submit your comments to Washington L&I before the October 7th deadline. Focus on objective information and potential impacts.3.

Follow the Rulemaking Process

Monitor the L&I website for updates and the final rule on December 19th.4.

Consult with Experts:
If you have significant concerns or questions, consult with a qualified electrical engineer or a code expert.This is a significant change that could have a real impact on electrical installations in Washington State. Your input during the public comment period is valuable. Flag for review