Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 15kVA Single Phase Secondary OCPD size

User: Sparky2791, Location: Northeast, PA

Asked on: Tuesday, August 26, 2025 at 10:31 am EDT
Answered on: Tuesday, August 26, 2025 at 10:31 am EDT

Question: Per the National Electric Code, can a 15kVA stepdown transfomer feed a 100A panel (208V single phase secondary)15000/208 = 90.14423A which is over 90A and the next standard OCPD is 100A. While I would recommend the use of a 20kVA would a 15 be acceptable?Thanks for the replies!

You've done the initial calculation correctly. Let's break down the NEC considerations: Transformer Primary Protection

You didn't mention the primary voltage, but the primary protection is determined by NEC 450.3. This is independent of the secondary breaker sizing discussion.


Transformer Secondary Protection

This is where your question lies. NEC 450.3(B) dictates the secondary overcurrent protection. Here's the breakdown:

450.3(B)(1)

If the secondary contains a single overcurrent device (like your 100A panel's main breaker), then the OCPD
must be rated or set at not more than 125% of the transformer's secondary current.

Your Calculation and NEC Applicability

Your calculation shows a secondary current of approximately 90.14 amps. 125% of 90.14 amps is 112.675 amps. Since you are using a standard size 100A breaker, it is less than the calculated maximum for the secondary.

The Code Answer

Based solely on NEC 450.3(B)(1), a 100A breaker is permitted for the secondary protection of a 15kVA, 208V single-phase transformer,
provided it is the only overcurrent device on the secondary.

Important Considerations (Beyond Basic Code Compliance)



Load Calculations

The fact that the code permits it doesn't mean it's a good design. You

must
perform a thorough load calculation for the panel being fed by the transformer according to NEC Article 220. The calculated load must not exceed 80% of the 100A breaker or 80A. Continuous loading on the transformer. Starting Currents

Consider motor starting currents or other inrush currents of equipment connected to the panel. These can create voltage dips and potentially nuisance tripping.


Voltage Drop

A small transformer being loaded near its maximum capacity is more susceptible to voltage drop under load. Check voltage drop calculations, especially if the load is sensitive to voltage variations.

Coordination

Consider breaker coordination. Ensure the transformer's secondary breaker will trip before the primary overcurrent device in case of a fault.


Continuous Load

Under the National Electrical Code, a continuous load shall not exceed 80% of the rating of the branch circuit or the transformer secondary overcurrent protection device.

In Conclusion

Yes, a 100A breaker is permitted by the NEC as the only overcurrent device on the secondary for secondary protection, but only if the calculated load and other application factors meet the code requirements. Assuming the calculations meet the 80A or less continuous load, and all other applicable NEC articles are observed.Your instincts about using a 20kVA transformer are generally correct. It provides more headroom, reduces voltage drop, and simplifies design, especially with motor loads. A larger transformer is generally good engineering practice.

Disclaimer:
I am an AI Chatbot and not a qualified electrical engineer. This information is for general guidance only. Always consult with a licensed electrical engineer or local electrical inspector for specific design and code compliance questions related to your project. Flag for review

Previous Question Next Question