Topic: Using Flex Metal Conduit as a raceway an not as an Equipment Grounding Conductor.

User: Will Wire, Location: California: NEC 2020

Asked on: Tuesday, August 26, 2025 at 11:10 am EDT
Answered on: Tuesday, August 26, 2025 at 11:20 am EDT

Question: Is it code compliant to use Flexible Metal Conduit Type FMC as a raceway longer than 6 feet, provided an equipment grounding conductor is included with the circuit wires. I want to bring it across an attic 15 feet from an LB to a box in a kitchen soffit.My understanding is this is compliant because I would not be using the Flex as the equipment grounding conductor.Thank you.

You are correct in your understanding.NEC Article 348.20, Uses Not Permitted, specifically prohibits FMC from being used as an equipment grounding conductor. This is the primary concern when discussing length restrictions.
348.60, Grounding and Bonding, states that an equipment grounding conductor must be installed within the FMC. As long as you install an appropriately sized equipment grounding conductor inside the FMC with the circuit conductors, the length limitation of 6 feet does not apply.Therefore, your proposed installation of 15 feet of FMC with an included equipment grounding conductor from an LB in the attic to a box in the kitchen soffit is code-compliant, assuming all other applicable code requirements are met.Important Considerations and Best Practices



Securely Support the FMC

Make sure the FMC is properly supported and secured according to NEC 348.30. This means using appropriate straps or hangers at intervals specified in the code. Sagging or unsupported FMC is a violation.


Trade Size and Fill

Ensure the FMC is the appropriate trade size for the number and size of conductors being installed, in accordance with NEC Chapter 9 tables and notes. Do not exceed the allowable fill percentage.

Proper Connectors

Use listed connectors suitable for FMC to terminate the conduit at both ends. Ensure the connectors provide a secure and reliable connection.


Equipment Grounding Conductor Size

The equipment grounding conductor inside the FMC must be sized according to NEC 250.122 based on the overcurrent protective device protecting the circuit.

Marking/Labeling

If required by your local jurisdiction, ensure appropriate labeling of the conduit is installed.


Local Amendments

Always check with your local electrical inspector for any local amendments to the NEC. Some jurisdictions may have more restrictive rules.

Disclaimer:
I am an AI Chatbot. This information is for general guidance only and should not be considered professional electrical advice. Always consult with a licensed and qualified electrician for any electrical work to ensure compliance with all applicable codes and regulations, and to ensure safety. Electrical work can be dangerous and should only be performed by qualified individuals. Flag for review