Topic: Steel conduit with bare grounding conductor

User: Isaiah, Location: Baton Rouge

Asked on: Tuesday, August 26, 2025 at 2:30 pm EDT
Answered on: Tuesday, August 26, 2025 at 2:30 pm EDT

Question: Does a steel conduit containing bare copper grounding conductor require bonding per NEC?Enviado desde mi iPhone utilizando Tapatalk

Yes, a steel conduit containing a bare copper grounding conductor (equipment grounding conductor, EGC) does require bonding according to the National Electrical Code (NEC).Here's why: Parallel Paths for Ground Fault Current

The steel conduit itself becomes a parallel path for ground fault current.


Impedance and Voltage Drop

The impedance of the steel conduit is generally higher than that of the bare copper EGC. If a ground fault occurs, more current might flow through the lower impedance copper conductor. However, some current will flow through the conduit. This can lead to a voltage drop along the conduit, which can create a potential difference between the conduit and other grounded metal parts, posing a shock hazard.

NEC 250.96(A) and 250.92

These sections of the NEC mandate bonding of metal enclosures, raceways, and other metal parts that are likely to become energized. The purpose is to create a low-impedance path for fault current to return to the source, facilitating the operation of overcurrent protective devices (circuit breakers or fuses) and minimizing touch potential hazards.


Ensuring Effective Ground Fault Path

Bonding the conduit ensures that it's electrically connected to the EGC, creating a more effective and lower-impedance ground fault path.

How to Bond



Bonding Jumpers

Use bonding jumpers to connect the conduit to the grounding bus in the panelboard and to any metal enclosures or equipment housings along the raceway path.


Approved Connectors

Use listed grounding/bonding locknuts, bushings, or other fittings specifically designed for bonding conduit to enclosures.

Threaded Connections

For threaded conduit connections, ensure they are wrench-tight to provide good electrical continuity.

Important Considerations



Size of Bonding Jumpers

The bonding jumpers must be sized according to NEC Table 250.102(C)(1) (or 250.102(C)(2) if applicable), based on the size of the ungrounded conductors in the circuit.

Continuity

Ensure the entire conduit system has electrical continuity. Check the tightness of connections and use appropriate bonding methods.


Listed Equipment:
Use only listed and labeled equipment and fittings for grounding and bonding.In summary, even with a bare copper EGC inside the conduit, bonding the steel conduit is essential for safety and code compliance. It ensures a reliable low-impedance ground fault path, minimizes shock hazards, and facilitates the proper operation of overcurrent protection. Flag for review