Topic: Primary phase loss on delta Xfmr

User: ptonsparky, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)

Asked on: Wednesday, August 27, 2025 at 8:06 am EDT
Answered on: Wednesday, September 3, 2025 at 1:25 pm EDT

Question: I'm having fun trying to calculate the secondary voltages of a Delta-Wye transformer as the primary line to line voltages change, for whatever reason. Primary is closed Delta 480 voltAssume I lose L2, a fuse opens. What will the voltage be from H1 to H2 and H3 to H2? 240?

Okay, let's break down what happens when you lose a phase (L2) on a 480V Delta primary feeding a Wye secondary transformer. This is a common scenario in industrial settings, and understanding the voltage implications is critical.

Understanding the Situation Original Delta Configuration

In a healthy 480V Delta, each winding (H1-H2, H2-H3, H3-H1) has 480V across it. The line-to-line voltage on the primary is also 480V.


Loss of L2

When the fuse on L2 blows, the Delta is no longer closed. The primary winding connected to L2 (H1-H2 and H2-H3) are now essentially floating, but because they are still connected to the transformer core and there is magnetic coupling to the other winding, they will have voltage induced across them but it will not be the design voltage.

Voltage Analysis


Here's how the voltages will change approximately. Keep in mind that the exact values will depend on factors such as transformer impedance, core design, and load. These are estimates based on idealized behavior. H1-H2

Voltage from H1 to H2 is
significantly reduced. Since H2 is disconnected, the voltage between H1 and H2 will likely drop to something much lower than 480V. The exact value is very difficult to predict. It will depend on core saturation, parasitic capacitance, and other factors. It is unlikely to be 240V. It could be quite low, maybe on the order of 50 - 100 volts, or even less.

H3-H2

Similar to H1-H2, the voltage from H3 to H2 will be significantly reduced for the same reasons. It is unlikely to be 240V.

H1-H3

The voltage across H1-H3
should remain close to 480V. This winding is still energized by L1 and L3. It is still fully operational.

Secondary Side Implications
Severe Voltage Imbalance

The voltages on the secondary side (Wye) will be highly unbalanced. The phases connected to the windings affected by the loss of L2 will experience drastically reduced voltage. The phase connected to the still-energized winding (H1-H3) will be close to normal.

Overheating Risk

Even with no load, the transformer is likely to overheat under this condition. The imbalance in current flow will cause increased core losses. If there is a load connected to the secondary, the overheating will be more severe.


Motor Damage

If the secondary is feeding three-phase motors, running them under this severe voltage imbalance can quickly damage them. Motors will draw excessive current in an attempt to compensate for the low voltage, leading to overheating and winding failure.

Important Considerations & Dangers
Backfeeding

There might be some backfeeding from the load side that can affect the voltages.


Transformer Damage

Running a transformer with a phase missing on the primary can cause significant damage to the transformer itself due to circulating currents and overheating.

Control Circuits

Control circuits powered by the secondary might malfunction due to the low voltage, leading to unpredictable behavior.


Harmonics

The unbalanced condition will introduce significant harmonics into the system.

Grounding

The grounding scheme of the system is crucial. An ungrounded system will behave differently than a grounded system under these conditions.


DO NOT RELY ON THESE ESTIMATES FOR SAFETY-CRITICAL DECISIONS.
Use a voltmeter to measure the actual voltages in the field.

In summary: Losing a phase on the primary of a Delta-Wye transformer creates a very dangerous and unstable situation. The voltages H1-H2 and H3-H2 are not likely to be 240V. They will be severely reduced, leading to a highly unbalanced secondary and the potential for equipment damage. The voltages should be measured to determine the appropriate mitigation actions. Flag for review