Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generator sizing

User: Josuea1990, Location: Florida, USA

Asked on: Wednesday, August 27, 2025 at 8:17 pm EDT
Answered on: Wednesday, September 3, 2025 at 1:26 pm EDT

Question: Can 220.83 (a) be used to calculate the optional standby system (generator) size for a whole house automatic transfer as per 702.4 (b)(2)(a) on a dwelling unit?

No, 220.83(A) cannot be used to directly calculate the minimum optional standby system (generator) size for a whole-house automatic transfer switch as per 702.4(B)(2)(a) on a dwelling unit.Here's why: 220.83 is for Existing Dwelling Units

220.83, specifically, is designed for
existing dwelling units when determining feeder and service loads. It allows for a streamlined calculation method based on historical consumption.

702.4(B)(2)(a) requires calculation per Article 220

702.4(B)(2)(a) instructs you to calculate the load served by the optional standby system according to Article 220. While Article 220 includes 220.83, that section specifically has requirements for when it can be used.

Optional Standby Systems are for Calculated Loads

Optional standby systems are typically sized based on the
calculated load they are intended to supply during an outage. You want to ensure the generator can handle the loads you expect it to carry, not just what the house has drawn in the past.

Minimum Requirements vs. Intended Use

While you could theoretically use 220.83 to get a value and possibly argue it's a minimum, it doesn't address the intended use of the generator. If you plan to run more appliances or equipment on the generator than your historic consumption reflects, using 220.83 would result in an undersized generator.

How to correctly determine generator size for whole-house transfer


Calculate the Load per Article 220

Follow the general load calculation procedures in Article 220 (e.g., Part III - General, Part IV - Branch Circuit Load Calculations, Part V - Feeder and Service Load Calculations) considering the loads you intend to be supplied by the generator when it is running on optional standby power.2.

Include Demand Factors

Apply appropriate demand factors as allowed by Article 220 for the loads you are calculating.3.

Consider Motor Starting

Motors, such as those in HVAC systems, refrigerators, and well pumps, require a significant surge of power when starting. You must account for this motor starting kVA/horsepower, especially for the largest motor. Often a 220.18 exception is used.
4.


Size the Generator

Based on your calculated load (continuous and motor starting), select a generator with sufficient capacity (kVA or kW) and a proper starting capacity rating. Consult with the generator manufacturer to ensure it can handle the specific loads you've calculated.5.

Informational Note 1 of 702.4(B)(2)

This note suggests considering future expansion when sizing the optional standby system. Don't just size for the bare minimum; plan for potential future needs.

In Summary

While 220.83 provides a simplified method for existing dwelling unit feeder/service calculations, it is generally inappropriate to use it as the primary method to size an optional standby generator for a whole-house transfer switch as required by 702.4(B)(2)(a). The focus should be on calculating the anticipated load based on the connected equipment and demand factors as per the applicable sections of Article 220.

Disclaimer:
Consult with a qualified and licensed electrician or electrical engineer for specific electrical system design and installation guidance. Flag for review

Previous Question Next Question