Question: I have two buildings side by side (a residence and a detached barn), on two separate utility meters but both fed from the same power company transformer.I have an HVAC system in the primary residence that I wish to feed from the residence meter during day time hours, and the barn meter during evening hours (to address time of use billing). I figure the HVAC system is about 50 amps or less. I am having to keep to NEC 2020 I believe.Can I use a transfer switch to switch the HVAC load from supply A to Supply B legally?Would I need to placard anything indicating the HVAC has two power supplies?
Okay, let's break down the possibility of switching your HVAC load between two utility meters, adhering to NEC 2020, and the associated considerations.
The Short Answer
Yes, in principle, you can use a transfer switch to switch an HVAC load between two different power supplies (in this case, two different utility meters). However, there are significant hurdles and very specific requirements you'll need to meet to do it legally and safely. This is not a straightforward DIY project and
requires a qualified and licensed electrician who understands the applicable codes and utility requirements.The Issues and Requirements
NEC 225.30 Limits on Number of Supplies (Generally Prohibited)
This is the biggest obstacle. NEC 225.30 generally prohibits more than one supply to a single building or structure. The code is written to prevent parallel operation of power sources and to ensure that the electrical system can be safely de-energized for maintenance and emergencies.
Exception No. 1
Special Conditions. Multiple supplies are allowed where the total demand load of the building or structure is calculated to be 2000 kVA or greater. This is highly unlikely for a residential HVAC system.
Exception No. 2
Emergency or Standby Systems. A second supply is allowed for emergency systems, legally required standby systems, or optional standby systems, provided there are provisions preventing parallel operation. This would NOT apply to simply switching to a cheaper utility rate.
Exception No. 3
Legally Required Standby Systems. A second supply is permitted for legally required standby systems. This is also very unlikely for an HVAC system.
Exception No. 4
Parallel Power Production Systems. This applies to systems like solar or wind power, and wouldn't be applicable to your scenario.
Exception No. 6
Additional Supply for Specific Load(s). This is potentially the most relevant exception, but it is narrowly defined. It allows an additional supply for a specific load(s) where the additional supply is controlled in such a way that the total connected load supplied by both supplies does not exceed the maximum demand load of the premises.
This is the most likely avenue to even begin to explore, but it imposes very strict controls.2. NEC 225.39 Disconnecting Means
This specifies the type of circuit breakers/disconnecting means to use. All sources would need to be able to be shut off for the equipment to be considered safe to work on.3.
Transfer Switch Type
If you can somehow get past the multiple supply restrictions, you MUST use a "break-before-make" transfer switch. This ensures that the two power sources are never connected together, preventing backfeed and potential damage to the utility grid or your own equipment. It also prevents unsafe conditions if the two power supplies aren't perfectly in phase or voltage matched.
Manual vs. Automatic
A manual transfer switch is cheaper, but requires you to physically switch the power. An automatic transfer switch (ATS) can switch automatically based on a timer or other conditions, but is more expensive and complex.4.
Grounding and Bonding
Proper grounding and bonding are critical. Since you're dealing with two separate services (meters), you need to ensure that the grounding systems are properly interconnected to avoid circulating currents or potential differences that could create a shock hazard. This is a complex area, and must be done by a qualified electrician.5.
Utility Company Approval
This is essential. You must contact your power company before doing anything. They will likely have specific requirements and may prohibit the setup altogether. They are concerned about grid stability, safety, and preventing energy theft (even unintentional). They may also have tariffs or agreements that prohibit what you're trying to do. If your HVAC system also has a natural gas or propane heater it may affect what the utility will allow.6.
Metering and Load Calculation
The utility will be very interested in how the load is measured and how it is ensured that power is not being drawn from both sources simultaneously except as allowed under Exception 6 to 225.30. The exception allows the "total connected load supplied by both supplies does not exceed the maximum demand load of the premises." This means you need to know the demand load of your house, the demand load of the barn, and the exact power consumption of the HVAC equipment in order to determine that you would be in compliance with this exception.
7.
Placarding and Labeling
If you manage to make this work legally and safely, extensive labeling is required. You would need to clearly label: The HVAC equipment itself, indicating that it has two separate power sources. Each electrical panel that feeds the HVAC system, clearly identifying the circuits and the fact that the HVAC can be powered from another panel. The transfer switch itself, with clear instructions on its operation and warnings about the dangers of improper use.8.
Local Inspections
You will need to obtain all necessary permits and have the installation inspected by your local electrical inspector. They will ensure that the work complies with the NEC and any local codes.
Why This is Difficult and Potentially Not Worth It
Code Compliance
Navigating NEC 225.30 and the other related codes is challenging and requires a thorough understanding of electrical codes.
Utility Approval
Getting the utility company to approve this setup is often the biggest hurdle. They may have valid concerns about the impact on their grid and billing practices.
Cost
The cost of the transfer switch, wiring, permits, inspections, and electrician labor can quickly add up.
Complexity
The system is more complex and introduces potential points of failure.
Risk of Problems
If done improperly, this setup could create safety hazards, damage equipment, or violate utility regulations.
Recommendations
Consult with a Licensed Electrician
This is the most important step. Find an electrician who is experienced in dealing with complex electrical systems and who is willing to work with the utility company to explore the feasibility of your project. They can assess your specific situation, perform load calculations, and advise you on the code requirements.2.
Contact Your Utility Company
Talk to them before you start any work. Explain what you want to do and ask about their requirements and any restrictions they may have.3.
Consider Other Options
Explore other ways to reduce your energy costs, such as:
Energy Efficiency Upgrades
Improve insulation, seal air leaks, and install energy-efficient windows and doors.
Smart Thermostat
Program your thermostat to automatically adjust the temperature based on your schedule.
Demand Response Programs
Some utilities offer programs that reward you for reducing your energy consumption during peak demand periods.
Solar Panels
If your goal is to reduce your overall energy costs, consider installing solar panels.4.
Calculate Cost
If this setup looks like it will work, do the math. Add up the cost of the additional wiring, transfer switch, labor, permitting, inspection, and utility review. Is it worth it to save a few pennies per kilowatt, or would an alternative solution give you a better ROI?
In Summary:
While technically possible, switching an HVAC load between two utility meters is a complex and potentially expensive project. You'll need to overcome significant code hurdles, obtain utility approval, and ensure that the installation is done safely and correctly by a qualified electrician. Explore all other options for reducing your energy costs before pursuing this approach. It is unlikely to be worth the trouble and cost. Flag for review