Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Is correct this math 3 ckts120V(6ccc)?

User: marcosgue, Location: Tampa

Asked on: Thursday, August 28, 2025 at 6:36 am EDT
Answered on: Wednesday, September 3, 2025 at 1:27 pm EDT

Question: Let's do this:-Scenario 1.3/4" emt conduit: 3 circuits #12awg 120V+G (6ccc)More than 3ccc adjustment factor 80%#12awg (30A----90°column)30A*0.8=24AI'm still good with 20A ocpd each circuit-Scenario 2.3/4" emt conduit: 3 circuits #10awg120V +G (6ccc)80% adjustment factor#10awg (40A-----90°column)40A*0.8=32AI'm still good with 20A ocpd each circuitIn this cases:1. For derating adjustment factor is correct to use 90° column ampacity?2. The neutral conductor qualify as ccc?Thanks all in advance

Okay, let's break down both scenarios and address your questions.

Scenario 1: 3/4" EMT, 3 Circuits, #12 AWG, 120V+G (6 CCC) You have correctly calculated the ampacity after derating. #12 AWG THHN is rated at 30A in the 90°C column (Table 310.16). Adjustment factor for 4-6 CCC is 80% (Table 310.15(C)(1)). 30A 0.8 = 24A You are correct in using a 20A OCPD Even though the derated ampacity is 24A, you're still allowed to use a 20A overcurrent protective device (OCPD) since the next standard size OCPD would be 25A, exceeding the derated ampacity.

Scenario 2: 3/4" EMT, 3 Circuits, #10 AWG, 120V+G (6 CCC)
You have correctly calculated the ampacity after derating. #10 AWG THHN is rated at 40A in the 90°C column (Table 310.16). Adjustment factor for 4-6 CCC is 80% (Table 310.15(C)(1)). 40A 0.8 = 32A You are correct in using a 20A OCPD The derated ampacity is 32A, which can be protected by a 20A breaker.

Answers to Your Questions


For derating, is it correct to use the 90°C column ampacity?
Yes, with a very important qualification. You can use the 90°C column for derating purposes. However, the termination temperature rating limits you. NEC 110.14(C) states that conductors with ampacities of 100A or less, you have to use the terminal rated for 75°C. So even though you derate based on the 90°C ampacity, you can't load the conductors beyond the 75°C ampacity. This is critical! For #12 AWG, you would still use the 20A rating. For #10 AWG, you would still use the 30A rating. In the real world, you can only use the 90°C ampacity for derating purposes and not for the final load carrying capacity unless the equipment and terminals are rated for 90°C. Most standard breakers and equipment are not.2. Does the neutral conductor qualify as a CCC? It depends. In a standard 120V circuit, the neutral typically only carries the unbalanced load and is considered a CCC if it carries the maximum current. In this case, if the circuits are primarily incandescent lighting or non-linear loads, the neutral conductor will carry significant harmonic currents and must be counted as a CCC. General Rule

In general, a neutral conductor in a 120V circuit should only be counted as a CCC if it is expected to carry a significant portion of the load current.

In summary:
Your calculations are correct regarding the derating based on the 90°C column. You are still fine to use a 20A OCPD in both scenarios. Remember to always check the termination temperature rating of the equipment and adjust the final ampacity of the conductor accordingly. This often means using the 75°C column ampacity after derating based on the 90°C column.* Assess each situation individually to determine if the neutral should be included as a current-carrying conductor. Flag for review

Previous Question Next Question