Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sub-panel

User: frofro19, Location: VA.

Asked on: Friday, August 29, 2025 at 9:28 am EDT
Answered on: Wednesday, September 3, 2025 at 1:30 pm EDT

Question: I know this has been asked multiple times but I'm wondering why we can calculate the back-up heat at 65 percent if doing a load calculation for a house but if that same heat is coming from a sub-panel, it has to be calculated at 100 percent? I'm getting ready to install a sub-panel for an addition over a garage and wondering if everything has to be calculated at 100 percent?It will have a dryer, water heater, washer, a 1.5 ton mini-split for the garage and I believe a 2 ton heatpump with 7.5 kw of back-up heat. If this same scenario was a "whole house" it would have some demand factors involved. I know you loose the diversity factor with a sub-panel and I know the total load calculation comes from the entire dwelling but just trying see what I need for the sub-panel feeder. I haven't checked the nameplate on the heatpump and mini-split yet, but will before choosing the feeder for the sub-panel.

You're right, this is a common point of confusion, and it boils down to how the NEC (National Electrical Code) defines the loads and how diversity/demand factors are applied. Let's break it down

Whole House vs. Sub-Panel: Why the Difference?
Whole House Calculation

When calculating the service size for an
entire dwelling unit, the NEC allows for demand factors because it acknowledges that not all loads will be operating at 100% simultaneously. Think about it: you're likely not running your oven, dryer, water heater, and all your lights and receptacles at full capacity at the same time. This is why Article 220 of the NEC includes various demand factors for ranges, dryers, water heaters, etc.

Sub-Panel Calculation

Sub-panels generally feed specific areas or dedicated loads. The NEC treats them more conservatively because:

Lack of Diversity

The loads on a sub-panel are often
more likely to be used simultaneously compared to the entire house. You're concentrating specific load types.

Safety Margin

Erring on the side of caution for sub-panels helps ensure adequate capacity for the connected loads, even if everything is running at (or near) its maximum.

Simpler Calculation

It's a more straightforward, less subjective approach. Applying multiple demand factors at the sub-panel level could lead to calculation errors and undersized feeders.

Applying to Your Garage Addition Sub-Panel



General Rule: 100% Load Calculation for Sub-Panel
- As a general rule, you must calculate the connected load on the sub-panel at 100% (with a few exceptions I'll note below). This means adding up the ampacity of each device as determined by its nameplate or NEC tables.

Specific Loads in Your Scenario


Dryer

Use the nameplate rating. If the nameplate isn't available, use 5000 watts (or 240V) as a minimum (NEC 220.54).
2.


Water Heater

Use the nameplate rating (watts or amps at the rated voltage).3.

Washer

Use the nameplate rating (watts or amps). You might also assume 1500 watts as a worst case scenerio.4.

Mini-Split (1.5 Ton)

You must use the nameplate rating. Look for the Minimum Circuit Ampacity (MCA) and the Maximum Overcurrent Protection (MOCP) values. The MCA is the key value for your load calculation. MOCP defines the MAXIMUM breaker size allowed for equipment protection.5.

Heat Pump (2 Ton) with 7.5 kW Backup Heat



Heat Pump Compressor

Again,
you must use the nameplate. Find the MCA for the heat pump unit.

Backup Heat (7.5 kW)

This is where it gets tricky. Although the NEC does give an exception (see below), I would still calculate the load at 100%.

NEC Exception: Space Heating and Air Conditioning (220.82)
220.82(C) (Exception No. 2) For other than dwelling units and guest rooms or guest suites of hotels and motels, if fixed electric space heating is installed, the connected load shall be calculated at 65% of the total heating load;220.82(B) For dwelling units, you may calculate the heating and air conditioning load at 100% of the larger of the heating and air conditioning load and use the smaller of the two for the total load.

This applies to your scenario because you have heating
and air-conditioning.

You could calculate the heatpump and mini-split at 100% of the larger of the two. If the Mini-Split is the larger load, you do not have to account for the 7.5kW electric back-up heat at all.
Steps for Calculating Sub-Panel Feeder Size


Gather Nameplate Data

Absolutely crucial. Get the MCA and MOCP for both the mini-split and the heat pump.2.

Calculate Total Load (Using the most conservative method) Dryer (Watts/Volts = Amps) Water Heater (Watts/Volts = Amps) Washer (Watts/Volts = Amps) Mini-Split (MCA) Heat Pump (MCA) Backup Heat (7500 watts/volts = Amps) Add these all together (Total)3. Choose Wire Size and Overcurrent Protection

The ampacity of your feeder wires (from a table like NEC 310.16) must be at least the total load calculated above. The breaker size should be at the appropriate size for the wire chosen. Make sure the wire is rated for the termination temperature of the equipment its being connected to.4.

Grounding

Ensure proper grounding of the sub-panel according to NEC Article 250.

Important Considerations



Future Loads

Consider any potential future loads in the garage addition (e.g., a small shop, additional appliances). It's always better to oversize the sub-panel feeder a bit to accommodate future needs.

Voltage Drop

Account for voltage drop, especially with longer feeder runs. A larger wire size may be necessary to minimize voltage drop and ensure proper equipment operation.


Local Codes

Always check and comply with local building codes and electrical codes, which may have stricter requirements than the NEC.*

Consult a Qualified Electrician

This advice is for informational purposes only and should not substitute the expertise of a licensed and qualified electrician. A professional can accurately assess your specific situation, perform the necessary calculations, and ensure a safe and code-compliant installation.

In summary, while the NEC allows demand factors for whole-house load calculations, it generally requires you to calculate sub-panel loads at 100% of their connected rating, with an exception for space heating and air conditioning. Accurately gathering nameplate data, understanding the NEC exceptions, and consulting with an electrician are essential for a safe and reliable sub-panel installation.
Flag for review

Previous Question Next Question