Question: Rigid metal conduit penetrates exterior wall to enter the building above ground, per NEC this conduit must be sealed when penetrate, what type of sealant can be used and code compliance?
You're correct. NEC Article 300.7(A) requires sealing raceways (including rigid metal conduit - RMC) where they enter or leave buildings. This is to prevent moisture, gases, or other contaminants from entering the building.Here's a breakdown of suitable sealant types and code compliance
Suitable Sealant Types:
The NEC doesn't specify brand names of sealant, but it implies the sealant should be suitable for the environment and application. Commonly used and appropriate sealants include: Duct Seal
Duct seal is a putty-like substance specifically designed for sealing conduit and other openings. It is non-hardening, remains pliable, and can be easily molded.
Silicone Sealant
Choose a 100% silicone sealant (not acrylic latex with silicone). Ensure it is paintable if desired. Look for those rated for exterior use and extreme temperatures. It's important that the silicone is compatible with the conduit material (e.g., don't use a sealant that will corrode aluminum conduit).
Expanding Foam (Closed-Cell)
Carefully consider expanding foam.
It must be a closed-cell type. Open-cell foam will absorb water and defeat the purpose of the seal. Expanding foam can also be difficult to remove or adjust later if needed. Apply sparingly to avoid over-expansion. This type is less common than the other two. Other Listed Sealants
Sealants that are specifically listed and labeled for use in sealing electrical penetrations. This is the safest bet, as the listing provides assurance of suitability.
Code Compliance & Considerations
NEC 300.7(A) Raceways Exposed to Different Temperatures
This is the primary section covering sealing. It states raceways exposed to different temperatures must be sealed to prevent condensation from entering and accumulating. This is particularly important where the outside temperature is significantly different than the inside.
NEC 314.15 Damp, Wet, or Hazardous (Classified) Locations
If the location outside the building is considered damp or wet (as defined by the NEC), or if it is a hazardous location, the sealant must be listed and suitable for that environment. This will often mean choosing a sealant with specific environmental ratings.
UL Listing
Look for UL-listed sealants. UL listing indicates that the product has been tested and certified to meet specific safety and performance standards.
Manufacturer's Instructions
Always follow the sealant manufacturer's instructions for proper application. This includes surface preparation, application thickness, and curing time. Compatibility
Ensure the sealant is chemically compatible with the conduit material (e.g., galvanized steel, aluminum).
Accessibility
Consider future access. Using a sealant that is easily removable or replaceable can be beneficial for future maintenance or modifications. Duct seal is advantageous here.
Fill the Gap
The sealant must completely fill the annular space between the conduit and the wall penetration. Avoid leaving any gaps or voids.
Example Scenario
Let's say you have a galvanized RMC entering the exterior brick wall of a commercial building. Here's a compliant approach:1.
Preparation
Clean the conduit and wall surfaces around the penetration to remove any dirt, debris, or loose material.2.
Sealant Choice
Select a UL-listed duct seal that is compatible with galvanized steel and suitable for exterior use.3.
Application
Firmly pack the duct seal into the annular space between the conduit and the wall, ensuring a complete and tight seal. Smooth the sealant surface to prevent water accumulation.
Important Notes: Consult local electrical codes. Some jurisdictions may have more stringent requirements or specific sealant approvals. If you are unsure about the proper sealant or application method, consult with a qualified electrician. Proper sealing not only protects the electrical system but also helps to maintain the building's thermal efficiency and prevent moisture damage.* Consider using a sealing locknut when installing the conduit into the enclosure inside.By following these guidelines, you can ensure that your RMC penetrations are properly sealed and compliant with the NEC. Flag for review