Question: OK, so I know this is a very very basic question but these inspectors have me in a rage. I have a 200 amp multifamily service. I have three 250 KCMIL aluminum XHHW conductors feeding a meter socket. Can someone please tell me what size schedule 40 PVC conduit/riser you can use that’s code compliant ? (The riser is about 14’ with a weatherhead) very basic I know!!!After a couple responses I will explain more- I just want unbiased opinions !
Okay, here's the straight answer, keeping it simple and focusing on code compliance:You need 2-inch Schedule 40 PVC conduit for three 250 kcmil aluminum XHHW conductors.
Explanation
Conductor Fill
This is the key. You need to calculate the total cross-sectional area of your conductors and compare it to the allowed fill percentage in the conduit. NEC Chapter 9, Table 1 specifies maximum conduit fill percentages. For three or more conductors, the fill percentage is 40%.
Appendix C
Chapter 9 has a series of tables, 1 through 12. Appendix C has a series of tables C1 to C12(a). Use Appendix C Table C9, Conduits – Percent Area of Conduit and Tubing for Conductors to determine your answer.
Why 2-inch? 250 kcmil aluminum XHHW, see Chapter 9, Table 5. Each has an outside diameter of .668 inches, and a cross section area of 0.35 square inches. Three conductors have a combined cross section area of 1.05 square inches. Referring to Appendix C, Table C9, a 2-inch schedule 40 PVC conduit has an "available space" of 1.371 inches. This is greater than 1.05 square inches. 1 1/2 inch schedule 40 PVC conduit has an "available space" of 0.864 inches. This is NOT large enough. Important Considerations
Weatherhead
Ensure the weatherhead is appropriately sized for the conduit.
Bends
Minimize bends in the conduit run. The NEC limits the total bend amount in a conduit run.
Support
Support the conduit properly as per NEC requirements (every 3 feet for PVC).
Expansion Fittings
Depending on your climate and the length of the conduit run, you might need an expansion fitting to accommodate thermal expansion/contraction of the PVC. This is especially important for long runs.*
Local Codes
ALWAYS check with your local jurisdiction for any amendments to the NEC.
Bottom line: 2-inch Schedule 40 PVC is the correct size based on NEC fill calculations for three 250 kcmil aluminum XHHW conductors.Now, tell me more about why the inspectors are giving you trouble! I am curious. Flag for review