Question: Hey guys, just wanted to pick your brain on this. This will be my first outdoor sauna install.So 210.8 (F) requires gfci protection on anything 150v to ground and 50a or less so that would include the sauna i am installing (40a required circuit).The sauna, like all saunas seem to, says not to install gfci protection on it. It doesn't say anything about voiding the warrenty by using a gfci breaker but it says it will most likely trip the gfci.Has anyone done one on a gfci outside and had success? Or should i tell them that it's not a good idea due to the gfci requirements.thanks in advance!
You've hit a common conundrum with saunas and GFCIs. You're absolutely right about the code requirement in 210.8(F) for outdoor 50A or less circuits up to 150V to ground needing GFCI protection. And you're also correct that sauna manufacturers often discourage or even forbid GFCI protection.Here's how to break it down and approach this
Why Saunas and GFCIs Don't Always Play Nice
Inrush Current
Sauna heaters, especially when cold, can have a significant inrush current when they first turn on. This surge can sometimes be interpreted by a GFCI as a ground fault, causing it to trip.
Leakage Current
Even in normal operation, some very small amount of leakage current can be present in the heating element. While not dangerous, a sensitive GFCI might see this as a problem.
Sensitive GFCI
Older and cheaper GFCI's are very sensitive which is why it is common for them to trip frequently.
Addressing the Code Requirement vs. Manufacturer Recommendation
This is a tricky spot. You have to balance code compliance with the sauna manufacturer's guidance and potential warranty implications. Here's a path forward:1. Verify the Voltage to Ground
Double-check the voltage to ground on the sauna circuit. If the sauna's voltage to ground exceeds 150 volts, then the NEC 210.8(F) requirement does not apply.
2.
Contact the Sauna Manufacturer Directly
This is the most important step. Call the manufacturer's technical support line. Explain the situation: You are installing the sauna outdoors. Code requires GFCI protection for the circuit. Their documentation says not to use GFCI. Ask them: Specifically, will using a GFCI void the warranty? Get this in writing (email confirmation is ideal). Do they have a recommended GFCI breaker model or brand that they've found to be reliable with their saunas? Have they tested their sauna with GFCI protection? What were the results? Ask about any specific grounding requirements or best practices that might minimize nuisance tripping.3.
Consult with Your Local Electrical Inspector
Before proceeding, discuss this with your local electrical inspector. They have the final say on code enforcement. Explain: The code requirement. The sauna manufacturer's warning. What the manufacturer told you (ideally, have documentation). Ask for their guidance on how to proceed. They may have experience with this situation and know of a solution. They might accept the manufacturer's documentation as a valid reason to not use GFCI protection (though this is unlikely, it's worth asking).4.
If GFCI is Absolutely Required
Use a High-Quality GFCI Breaker
If you're installing a GFCI, choose a good quality breaker from a reputable manufacturer (Siemens, Square D, Eaton). Avoid the cheapest options. Some GFCI breakers are more tolerant of minor leakage current.
Consider a GFCI Breaker with Adjustable Sensitivity
Some advanced GFCI breakers have adjustable sensitivity settings. This might allow you to reduce the sensitivity to minimize nuisance tripping while still providing protection. However, make sure that the adjustable sensitivity is still compliant with the listing of the GFCI and provides adequate protection.
Upgrade the Wiring
Ensure the wiring is in excellent condition. Damaged insulation or loose connections can contribute to ground faults and nuisance tripping.
Verify Grounding
Double-check that the sauna is properly grounded according to both the manufacturer's instructions and local code. A good ground connection can help prevent nuisance tripping.5.
Documentation is Key
Keep meticulous records of everything: Sauna manufacturer's instructions. Your conversations with the manufacturer (dates, names, and a summary of what was said). Your discussions with the electrical inspector (dates, names, and their instructions). Receipts for all materials (GFCI breaker, wiring, etc.).
Possible Outcomes and Considerations Manufacturer OKs GFCI
If the manufacturer says it's okay to use a specific GFCI breaker without voiding the warranty, that's the best-case scenario. Install that specific breaker and document everything.
Inspector Approves Waiver
If the inspector, after seeing the manufacturer's warning and your documentation, allows you to not use GFCI, get this in writing from the inspector. This is less likely, but possible.
GFCI Required, Nuisance Tripping
You might end up having to use a GFCI that trips occasionally. In this case:
Troubleshooting
Before giving up, try turning off other nearby circuits to see if one of them is contributing to the problem.
Document the Tripping
Keep a log of when the GFCI trips (time of day, weather conditions, etc.). This might help you identify a pattern.
Consider a Time Delay Relay
In some cases, a time delay relay on the heater element can minimize inrush current, but this is a complex solution and needs careful consideration and likely manufacturer approval. It's probably best avoided.
Sauna Incompatible
The worst-case scenario is that the sauna is simply incompatible with GFCI protection, and the manufacturer won't support it. In this case, you might have to reconsider the sauna model.
Important Considerations Safety First
GFCI protection is designed to save lives. Do not bypass or disable it lightly.
Liability: As the electrician, you are responsible for ensuring the installation is safe and code-compliant. Make sure you are comfortable with whatever solution you choose.By following these steps and thoroughly documenting your process, you'll be in the best position to navigate this situation safely and effectively. Good luck! Flag for review