Topic: Transformer size

User: don_resqcapt19, Location: Illinois

Asked on: Monday, September 1, 2025 at 11:28 am EDT
Answered on: Wednesday, September 3, 2025 at 1:35 pm EDT

Question: Is this a 25 kVA transformer? I think so, but since three of these are feeding a new 1200 amp service, I am not sure.

I cannot determine if the transformer is 25 kVA without more information. You'll need to look at the nameplate of the transformer. It will explicitly state the kVA rating.Here's why three 25 kVA transformers feeding a 1200A service is highly unlikely and why you're right to question it: Calculating the Power Supply

Three 25 kVA transformers provide a
total capacity of 75 kVA.

Estimating Output Amperage

A 75 kVA transformer, if it is providing 208V 3 phase power, can only provide about 208 amps of power. (kVA 1000) / (voltage sqrt(3)) = current. In this case, (75 1000)/(208 1.732) = 208 amps.Note: The above assumes 3 phase power. Single phase power calculations would be different.

Therefore, 75 kVA is grossly undersized for a 1200A service.
What to look for on the Transformer Nameplate


kVA Rating

This is the most important. Look for a number followed by "kVA".2.

Voltage Ratings

Check the primary (input) and secondary (output) voltages. This is crucial for understanding if the transformers are configured correctly.3.

Phase

Is it single-phase or three-phase?4.

Frequency

Typically 60 Hz in North America.5.

Impedance (Z)

This is important for short-circuit calculations.6.

Connection Diagram

This shows how the transformer windings are connected (e.g., Delta-Wye, Wye-Wye, etc.).7.

Manufacturer and Model Number

Useful for looking up more detailed specifications if needed.

Possible Scenarios (If it's not 25 kVA)



Much Larger Transformers

The most likely scenario is that the transformers are significantly larger than 25 kVA each. You're looking at possibly 3 500kVA transformers or larger.


Incorrect Service Size

While less likely, it's possible the 1200A service size is incorrect or oversized for the actual load.*

Parallel Transformers (Very Complex)

It is possible to parallel transformers together but this requires special equipment and should be done by a professional.

In summary:
Check the transformer nameplates for the kVA ratings. 25 kVA is far too small for a 1200A service. This is a critical safety issue, and any discrepancies should be addressed immediately by a qualified electrician or electrical engineer. Flag for review