Topic: Service feed overcurrent protection for multi-unit EV charging

User: brian.1, Location: Santa Clara county

Asked on: Monday, September 1, 2025 at 8:28 pm EDT
Answered on: Wednesday, September 3, 2025 at 1:36 pm EDT

Question: My 20 unit condo building is adding EV chargers for all units and I'm looking for help managing the continuous EV charging load on my condo building's transformer and service feed wires.There are 20 units each with a 2 phase 90A at 120/208V main breaker which gives a theoretical total of 1800A at 120/208V. IIUC that would be 1039A in 3 phase.My condo building's service was set up long before EVs and EV charging was a consideration. As was standard at the time, the service was derated so the 3 phase service feed installed was 600A at 120/208V. The 600A is peak load. IIUC A continuous load can only be 80% of that which is 480A.The plan is to limit each EV charging circuit current to 24A at 208V. This would give a total EV charging current of 480A at 208V which is just at the continuous rating for the service transformer and feed wires. This sounds great BUT the condos still need electrical power for other things like A/C, oven, lighting, etc. We could lower the EV charging current but how much? However, people are asking for more current not less. Besides, wouldn't it be rare for all EVs to be charging at the same time?So 2 questions:How to detect 480A continuous, not 480A peak?How to disable or limit EV charging without interfering with a condo's normal power usage?

Okay, this is a common and complex challenge for older buildings adding EV charging. Let's break it down and address your questions

Understanding the Problem:

You've accurately identified the core issue: your building's existing electrical service is likely undersized to handle the potential simultaneous continuous draw of 20 EV chargers, even at a limited 24A per charger. The key word here is "continuous."Answering Your Questions



1. How to Detect 480A Continuous (Not Peak)?


Detecting true continuous current draw requires more than just a snapshot reading. You need to measure the current over time. Here are several approaches: Data Logging Ammeter

This is the most accurate and reliable method. A data logging ammeter can be installed on the main service conductors. It records the current (amperage) at regular intervals (e.g., every 5 minutes, 15 minutes) over a period of several days or even weeks. This provides a detailed profile of the building's actual energy consumption patterns, allowing you to identify periods of sustained high draw. Professionals use these to determine the building's existing load profile.


Power Quality Analyzer

Similar to a data logging ammeter, a power quality analyzer provides even more detailed information about the electrical system, including voltage, current, power factor, harmonics, etc. This can be useful for diagnosing any underlying electrical issues in addition to assessing load. Again, this is a job for a qualified electrician or electrical engineer.

Smart Meter Data (If Available)

Some utilities provide detailed interval data from the building's main meter (if it's a smart meter). If available, this data can be analyzed to determine peak and sustained load periods. Check with your utility company. The problem is this data is often anonymized or in an inconvenient format.


DIY Monitoring (Less Accurate, but Informative)

You could use a clamp meter (amp meter) to take periodic current measurements at various times of day over several days. While less precise than data logging, it can provide a rough idea of load patterns.

Important Considerations for Monitoring



Duration

Monitor for at least a week, ideally two or more, to capture variations in weekday/weekend usage, weather conditions (affecting HVAC loads), and occupancy.


Professional Installation

For the data logging ammeter and power quality analyzer, always use a licensed electrician or electrical engineer. They know how to safely connect the equipment and interpret the data.

Data Analysis

The raw data from the monitoring devices will need to be analyzed to determine the maximum continuous current draw. Look for the highest average current over a sustained period (e.g., 1 hour, 3 hours).


80% Rule

Remember, the continuous load should not exceed 80% of the service rating. So, if you have a 600A service, your measured continuous load (including EV charging) should not exceed 480A.

2. How to Disable or Limit EV Charging Without Interfering with a Condo's Normal Power Usage?


You need a load management system (LMS). This is the only practical way to safely and reliably manage EV charging load in a multi-unit dwelling with limited service capacity. Here are the options: Centralized Load Management



How it Works

A central controller monitors the building's main service current. When the current approaches the predetermined limit (e.g., 480A), the controller automatically reduces or suspends power to the EV chargers. When the building's load decreases, the charging is automatically restored, either at full or reduced power.

Pros

Most efficient use of available power. Automatically adapts to changing building load conditions. Can prioritize charging based on factors like time of day or user needs. Can provide reporting and data on EV charging usage.


Cons

Higher upfront cost due to the central controller and communication infrastructure. Requires professional installation and configuration.

Distributed Load Management



How it Works

Each EV charger has its own smarts and communicates with a central system. The central system sets limits on each charger based on the overall building load. If the building's load increases, the system can reduce the current limit for each charger.

Pros

Potentially lower cost than centralized systems (depending on the technology). More resilient because failure of one charger doesn't affect the whole system.


Cons

Requires compatible smart chargers. May not be as efficient as centralized systems in distributing power.

Charger-Level Load Management (Least Desirable for Your Situation)



How it Works

Each EV charger has a pre-set maximum current limit. This doesn't actively monitor or respond to the building's overall load.

Pros

Lowest upfront cost.


Cons

Least efficient. Does not prevent overloading the building's service. If you set the charger limits too high, you still risk overloading. If you set them too low, it will frustrate EV owners.

Key Features of a Good Load Management System



Dynamic Load Balancing

Adjusts charging power based on real-time building load.


Priority Charging

Allows you to prioritize certain users or charging schedules (e.g., off-peak hours).

Reporting and Monitoring

Provides data on charging usage, system performance, and potential issues.


Communication

Uses a reliable communication protocol (e.g., Ethernet, Wi-Fi, cellular) to communicate between the central controller and the chargers.

Safety Features

Overload protection, short-circuit protection, and ground fault protection.


Open Standards

Choose a system that uses open standards (e.g., OCPP) to avoid vendor lock-in and ensure interoperability with different chargers.

Important Considerations for Load Management



Professional Design

Engage a qualified electrical engineer or EV charging specialist to design the load management system. They will assess your building's electrical system, determine the appropriate system size, and ensure proper installation and configuration.


Charger Compatibility

Not all EV chargers are compatible with all load management systems. Choose chargers that are certified to work with the selected LMS.

User Communication

Clearly communicate the load management system's operation to condo owners. Explain how it works, why it's necessary, and how it will affect their charging schedules.


Future Expansion

Consider future expansion plans when selecting a load management system. Choose a system that can be easily scaled to accommodate additional EV chargers as needed.

Local Regulations and Permits

Check with your local building department about any regulations or permits required for EV charger installations and load management systems.


Cost and ROI

Evaluate the total cost of the load management system, including installation, maintenance, and ongoing operating costs. Compare this to the potential costs of upgrading the building's electrical service. Also, consider the increased property value and tenant satisfaction that EV charging can provide.

Recommendation


Conduct a Thorough Load Study

Use a data logging ammeter or power quality analyzer to determine your building's existing load profile.2.

Consult with Professionals

Engage a qualified electrical engineer and an EV charging specialist to design a load management system that meets your building's specific needs.3.

Choose a Centralized or Distributed LMS

Based on your budget and performance requirements, select a centralized or distributed load management system.4.

Prioritize Safety and Reliability

Ensure that the chosen system meets all applicable safety standards and has a proven track record of reliability.5.

Communicate Transparently:
Keep condo owners informed throughout the process and provide clear instructions on how the load management system works.By taking these steps, you can safely and efficiently provide EV charging for your condo building while protecting your electrical infrastructure. Good luck! Flag for review