Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Fire pump fed from customer owned transformer multi building campus style complexes

User: hhsting, Location: Glen bunie, md, us

Asked on: Tuesday, September 2, 2025 at 9:11 am EDT
Answered on: Wednesday, September 3, 2025 at 1:38 pm EDT

Question: I have fire pump, jockey pump fed from customer owned 13.8kV to 480/277V three phase delta to wye transformer. The setting is multibuilding campus-style complex and in accordance with NEC 2017 Article 695.3(C)(2). The customer owned 13.8kVA to 480/277V also feed another switchboard downstream as well as the fire pump and jockey pump. See attached below.NEC 2017 Article 695.5(C) allows this. However I am confused with NEC 2017 Article 695.5(C)(2) where it says the following “..overcurrent protection is provided for the transformer in accordance with 450.3 and for the feeder in accordance with 215.3 and such that the overcurrent protection device(s) is selected or set to carry indefinitely the sum of locked rotor current of the fire pump motor(s), the pressure maintenance pump motor(s), the full load current of the associated fire pump accessory equipment and 100 percent of the remaining loads supplied by the transformer. The requirement to carry the locked rotor currents indefinitely shall not apply to conductors or devices other than overcurrent devices in the fire pump motor circuit(s).”It is very confusing what exactly is feeder in this case such as transformer secondary conductorFor feeder protection does the NEC 2017 require transformer secondary overcurrent protection for secondary side conductor feeding the fire pump sized per locked rotor current or not?

Let's break down the requirements of NEC 2017 Article 695.5(C)(2) in your specific scenario and clarify the "feeder" definition

Understanding the Scenario
You have a customer-owned 13.8kV-480/277V transformer supplying multiple loads: Fire pump Jockey pump Other downstream switchboard loads You are using the exception in 695.5(C) to connect the fire pump ahead of the main service disconnect.

Defining "Feeder" in This Context

In this specific application, the following definitions should be considered:
Transformer Secondary Conductors

The conductors running from the secondary terminals of the 13.8kV/480V transformer to the secondary switchboard that serves the fire pump, jockey pump, and other loads are the

feeder
you are referring to. Feeder Overcurrent Protection

This refers to the overcurrent protective devices (OCPDs) at the
secondary side of the transformer. Typically, this is a circuit breaker or fuses in the secondary switchboard.

Interpreting 695.5(C)(2)
695.5(C)(2) dictates how this feeder overcurrent protection must be selected and set. Let's dissect the requirements:1. 450.3 Compliance

The transformer itself must have overcurrent protection according to NEC 450.3 (Overcurrent Protection). This addresses
transformer protection based on its kVA rating.2.

215.3 Compliance

The
feeder (the conductors from the transformer secondary to the secondary switchboard) must have overcurrent protection according to NEC 215.3. This section of the NEC usually references sizing based on the feeder capacity.
3.


Indefinite Carry Requirement

This is the critical and often confusing part:
The feeder OCPD(s) must be selected or set to carry indefinitely the sum of: Locked rotor current (LRC) of the fire pump motor(s) Locked rotor current of the jockey pump motor(s) Full load current (FLA) of associated fire pump accessory equipment (e.g., alarm bells, control panels, heaters) 100% of the remaining loads supplied by the transformer (the loads other than the fire pump, jockey pump, and accessories).

Crucially

The "indefinite carry" requirement ONLY applies to the OCPDs (overcurrent protective devices). It
does not apply to the conductors themselves. The conductors are still sized based on their ampacity, not the indefinite LRC carry.

Does the NEC require transformer secondary overcurrent protection for secondary side conductor feeding the fire pump sized per locked rotor current or not?


Here's the important clarification:
No, the secondary side conductors feeding the fire pump and jockey pump do NOT need to be sized based on carrying the LRC indefinitely. They are sized based on their ampacity per NEC 695.6 (Power Source Circuit Capacity), which will likely be higher than the motor FLA but will not be the LRC. 695.6(A) states, "The power source circuit shall have a minimum ampacity of at least 125 percent of the sum of the fire pump motor(s) full-load current(s) and 100 percent of the associated fire pump accessory equipment." Yes, the secondary feeder overcurrent device (OCPD) MUST be selected or set to carry the LRC indefinitely (along with the other loads as described above).Practical Implications and Sizing Considerations Transformer Sizing is Critical

The transformer kVA needs to be large enough to handle the fire pump LRC without excessive voltage drop, while also supplying the other loads. This often dictates using a larger transformer than would be required for the normal load.

Coordination

Careful coordination is essential. The goal is to ensure the fire pump gets power reliably
when needed, while still protecting the transformer and conductors from faults. Coordination studies are highly recommended.

Feeder OCPD Settings

You will likely need to use a large OCPD to meet the indefinite carry requirement. Consider using adjustable trip circuit breakers to allow for precise settings.

In summary, 695.5(C)(2) requires the FEEDER overcurrent protective device (not the conductors) to be capable of carrying the fire pump and jockey pump LRC indefinitely in addition to any other loads on the transformer. The conductors from the transformer to the fire pump controller are sized per article 695.
6.
Recommendation:

Consult with a qualified electrical engineer experienced in fire pump installations and NEC compliance to perform the necessary calculations, coordination studies, and ensure a safe and code-compliant installation. Flag for review

Previous Question Next Question