Question: Been noticing inspectors allowing tray cable to be used for interior residentialBeen seeing it on electric clothes dryer installs.It’s black and not orange so it should have been obvious.I thought it was not allowed for that application.Only usable where control and power are applicable. Generators for instance.
You're right to be concerned. Using tray cable (TC) for a typical residential clothes dryer connection is generally not permitted by the NEC (National Electrical Code) and is often a misapplication. Here's a breakdown of why and what might be happening (though it's still likely wrong)
Why TC Cable is Usually Prohibited for Dryer Connections:
NEC Article 336.10 (Uses Permitted) and 336.12 (Uses Not Permitted)
This section outlines where TC cable is allowed and not allowed. While the specifics can vary based on the NEC edition, generally, it's intended for industrial and commercial applications, primarily in cable trays, raceways, or for direct burial (depending on the TC cable's marking). The specific prohibitions typically include use in one- and two-family dwellings except in specific circumstances related to Article 725 (Class 1, 2, and 3 circuits and communications) or other specialized applications. A dryer circuit doesn't fall under these exceptions.
Type NM (Nonmetallic-Sheathed Cable) or Type SE (Service Entrance) Cable is Required
For a standard residential dryer connection, the NEC usually requires either:
NM Cable (Romex)
The most common choice when the wiring is concealed within walls. It's cheaper and easier to work with, but cannot be used in wet or damp locations, or exposed to physical damage.
SE Cable
Used for service entrances, but can be used for dryer circuits if installed and supported correctly. More expensive than NM, and typically needs to be installed in conduit where exposed to physical damage.
Listing and Labeling
TC cable is listed for specific uses. A residential dryer connection, installed directly between a junction box and the dryer, is typically not one of those listed uses.
Flexibility and Strain Relief
Dryers vibrate. While TC can be flexible, it's not designed for the continuous flexing and movement that can occur with a dryer. It lacks the strain relief properties required for appliances that are frequently moved.
Grounding
The grounding conductor in TC is suitable for power and control circuits and not rated for the load a clothes dryer places on it. TC often has a reduced size ground.
Possible (But Unlikely and Problematic) Explanations for Why Inspectors Might be Allowing It (and why they are still wrong)
Misunderstanding/Ignorance of the Code
The most likely explanation. Inspectors are human, and mistakes happen. It's concerning if it's a pattern.
Incorrectly Assuming it's "Okay because it's rated for higher voltage/amperage"
Just because a cable can handle the electrical load doesn't mean it's suitable or listed for that specific application. The NEC is about more than just load calculations; it's about safety and proper installation methods.
Confusing with a Different Type of Cable
It's possible (though unlikely) that they are misidentifying the cable. However, the black jacket should be a clue.
Specific Local Amendments (Rare)
Some jurisdictions have local amendments to the NEC. It's possible there's a very unusual amendment that might permit TC in specific cases, but this is exceedingly rare. You'd need to check your local building codes carefully. Even if there were, it would likely come with many stipulations.
What You Should Do
Verify the Cable Type
Be absolutely sure it's TC cable and not something else that resembles it. Check for markings on the cable jacket. It should clearly say "Type TC."2.
Document the Installations
Take pictures of the cable and the installation.3.
Question the Inspector (Politely and Respectfully)
Ask the inspector why they are allowing TC cable for the dryer connection. Refer to the specific NEC articles (especially 336.10 and 336.12). Be prepared to show them the code. Sometimes a simple question can prompt a re-evaluation.
4.
Escalate to the Building Department (If Necessary)
If the inspector doesn't change their stance and you believe it's a clear violation, contact the chief building official or the head of the inspection department. Be professional and present your evidence clearly.5.
Consult with a Licensed Electrical Contractor
Get a second opinion from a qualified electrician. They can assess the installations, explain the code requirements, and provide documentation to support your concerns.
Important Considerations
Safety
Improper wiring is a fire hazard and an electrical shock hazard.
Liability
If there's a problem in the future, the improper wiring could create liability issues.
Resale Value: A home inspection is likely to flag the improper wiring when you sell the house, which could require costly corrections.In summary, while there are always exceptions and nuances to the NEC, using TC cable for a standard residential dryer connection is generally* a clear violation. You are right to question it. Don't hesitate to follow up with the appropriate authorities to ensure that the installations are safe and code-compliant. Flag for review