User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, September 2, 2025 at 9:24 am EDT
Answered on: Wednesday, September 3, 2025 at 1:38 pm EDT

Question: Would you labor conduit within CMU block wall differently that say conduit surface mounted or even recessed? I know you have ot install it in sections/stages as the bricky lays his rows so there is more comeback time. I believe.

Yes, you would definitely approach conduit installation within CMU (Concrete Masonry Unit) block walls differently than surface-mounted or recessed conduit. Here's a breakdown of the key differences and considerations

Key Differences and Considerations for Conduit in CMU Walls:
Installation Timing and Phasing



Coordination is Critical

You absolutely must work very closely with the mason (bricklayer). The conduit installation is directly integrated with the block-laying process.

Section-by-Section

Install conduit in sections
after a course (row) of blocks is laid. This typically involves running conduit horizontally within a course, then transitioning up or down in the next course by using 90-degree bends or offsets, or through cutouts.

Comeback Time

You will have substantial "comeback" time because you have to wait for courses to be laid. Plan your schedule and manpower accordingly. Communication with the mason is critical to minimize delays.

Physical Support and Securing



Direct Attachment

You can't use traditional surface mounting methods. Instead, you'll likely use a combination of:

Straps and Clamps

Secure the conduit directly to the CMU block. Use fasteners designed for concrete/masonry (e.g., concrete screws, expansion anchors, powder-actuated fasteners)


Embedment

Conduit can be embedded in mortar joints but be careful to avoid creating weak points.

Vertical Support

Vertical runs will need to be supported in accordance with code (every 10 ft. typically). Consider using straps or clamps attached to the CMU block itself.


Prevent Movement

Ensure the conduit is securely fastened to prevent movement during the block-laying process. Loose conduit can shift, get crushed, or cause alignment problems with boxes and other components.

Protection from Damage



Physical Protection

CMU construction is rough. Protect conduit from damage during the process.

Marking

Clearly mark the location of conduits to prevent accidental damage during block placement.


Planning and Layout



Detailed Drawings

More detailed drawings are required to show exact conduit routing, bend locations, and box placements
within the block wall.

Avoid Conflicts

Plan carefully to avoid conflicts with other utilities, reinforcement steel, or structural elements within the wall.

Access

Consider future access for maintenance and modifications.


Conduit Type and Material



Rigid Metal Conduit (RMC) or Intermediate Metal Conduit (IMC)

These are generally the preferred choices for CMU walls due to their strength and durability. They can withstand the stresses of construction better than EMT or PVC.


Electrical Metallic Tubing (EMT)

EMT can be used, but extra care is needed to prevent crushing or bending.

PVC

PVC is less common within CMU walls due to its lower physical strength. If used, it should be schedule 80 for physical protection.


Box Installation



Flush Mounting

Electrical boxes are typically flush-mounted within the CMU wall.


Box Positioning

Coordinate the box placement with the mason before the block is laid. You might need to cut out a portion of the block to accommodate the box.

Box Support

Securely support the boxes to the CMU. Methods include:


Mortar

Carefully mortaring around the box to hold it in place. Be careful not to get mortar inside the box.

Straps/Anchors

Using straps or anchors to attach the box directly to the CMU.


Box Extenders

May be needed if the box ends up recessed too far into the wall.

Code Compliance



NEC (National Electrical Code)

All installations must comply with the NEC. Pay particular attention to grounding and bonding requirements.*

Local Codes

Check for any local codes or amendments that may apply to CMU wall installations.

Summary of Key Differences Compared to Other Methods

| Feature | CMU Wall Installation | Surface Mount | Recessed (Stud Wall)

-------------------|----------------------------------------------------------|---------------------------------------------------|------------------------------------------------------


Timing
| Integrated with masonry work | After wall construction | After wall construction, before finishing
Support | Direct attachment to CMU | Straps/clamps to surface | Straps/clamps to studs
Protection | Needs extra protection from construction damage | Typically less exposure to damage | Protection from drywall and finishing
Conduit Type | RMC/IMC often preferred | Varies (EMT, PVC, RMC, etc.) | Varies (EMT, PVC)
Box Mounting | Flush-mounted, requires coordination with mason | Surface-mounted or set within surface-mounted boxes | Flush-mounted within the wall cavity
Planning | Highly detailed planning required | Less detailed planning | Moderate planning
Comeback time | More due to masonry progress | Less | Less |Example Scenario

Imagine you need to run a conduit horizontally within a CMU wall to supply power to an outlet box.1.

Coordination

Before the mason lays the next course of blocks, meet with them to discuss the conduit routing and box placement.2.

Conduit Run

Cut and bend the conduit to the required length and shape.3.

Block Preparation

The mason may need to notch or core a small section of the block to accommodate the conduit.4.

Conduit Placement

Place the conduit horizontally along the mortar joint.5.

Securing

Use concrete screws and straps to secure the conduit to the CMU block. Ensure the conduit is flush with the block surface and won't interfere with the next course.6.

Box Installation

Secure the electrical box in the block cutout.7.

Mortar

The mason will then lay the next course of blocks, carefully mortaring around the conduit and box.8.

Repeat

Repeat this process for each section of the conduit run.

In conclusion:
Installing conduit in CMU walls requires careful planning, coordination with the mason, robust support methods, and a focus on protecting the conduit from damage during construction. Always follow the NEC and local codes. Flag for review